Calculate shear strength A36 plate

AI Thread Summary
The discussion focuses on calculating the shear strength of an A36 steel plate used in a tank designed to hold diesel fuel. The tank's sides will be made of 1/4 inch A36 steel plate, while the rest will be 10 gauge steel, with a total weight of approximately 1,250 lbs when full. The original calculations for shear strength were questioned, highlighting the need to de-rate the allowable stress for shear to 14,400 psi instead of using the tensile strength directly. Recommendations were made to use multiple lifting lugs for stability and to ensure proper sizing for shackles to avoid increased stress. Overall, it is advised to consult an engineer for safety and structural integrity before proceeding with the design.
Hugh99
Messages
2
Reaction score
0
I'm trying to build a tank to hold diesel fuel, it will be on skids to lift with a fork lift but I also want to extend the the sides to provide a way to raise the tank from two attachment points on each side. The sides will be 1/4 A36 steel plate and the rest of the tank will be 10 gauge (0.140625). The tank should weigh around 350 lbs and hold 119 gallons of diesel. Using maximums that's 119x7.5 lbs = 892.5 lbs, including the weight of the tank that is roughly 1250 lbs.

Assuming the holes at the tope of the side plate are 2 in diameter and the shear formula F = P x T X PSI
I was going to calculate P as 2 in x pi and then divide by the portion of the whole that would be in contact with the rigging, so assuming 1/4 of the perimeter is in contact with perimeter, = 1.57
F = 1.57 x .25 x 36,000
F = 14,130 lbs per hole, so I should be able to support over 28,000 pounds for the two holes.

Does my math look correct?
If I left the sides as 10 gauge, it looks like it could still support 7900 lbs per hole for total of 15,800 lbs so I may not need 1/4 plate on the sides.

Thanks
 

Attachments

  • IMG_3746.JPG
    IMG_3746.JPG
    23.2 KB · Views: 2,113
Engineering news on Phys.org
Hugh99 said:
I'm trying to build a tank to hold diesel fuel, it will be on skids to lift with a fork lift but I also want to extend the the sides to provide a way to raise the tank from two attachment points on each side. The sides will be 1/4 A36 steel plate and the rest of the tank will be 10 gauge (0.140625). The tank should weigh around 350 lbs and hold 119 gallons of diesel. Using maximums that's 119x7.5 lbs = 892.5 lbs, including the weight of the tank that is roughly 1250 lbs.

Assuming the holes at the tope of the side plate are 2 in diameter and the shear formula F = P x T X PSI
I was going to calculate P as 2 in x pi and then divide by the portion of the whole that would be in contact with the rigging, so assuming 1/4 of the perimeter is in contact with perimeter, = 1.57
F = 1.57 x .25 x 36,000
F = 14,130 lbs per hole, so I should be able to support over 28,000 pounds for the two holes.

This is your first mistake. A36 steel has a minimum tensile strength of 36,000 psi. In shear, the allowable stress is much lower, typically 0.4 * 36,000 = 14,400 psi, which allows vagaries of shear stress distribution, provides for a minimal factor of safety on the load, etc. Even in bending, which provides partial tensile loads, the allowable stress should be kept below 0.6 * 36,000 = 21,600 psi. Many designers use higher safety factors depending on the service, sometimes 2:1 or 3:1 even.
Does my math look correct?
If I left the sides as 10 gauge, it looks like it could still support 7900 lbs per hole for total of 15,800 lbs so I may not need 1/4 plate on the sides.

Thanks
It's not a question of getting the arithmetic correct as knowing what you are doing with the numbers.

It would be better to have 2 lifting lugs per end to provide stability for the tank while it is being lifted. One lug per end could allow the tank to flip in the slings if not carefully handled.

You also need to check that plain plate can hold all that diesel fuel when it is suspended only at the ends. Such thin gage metal may appear attractive now, but what happens down the road once a little metal is lost due to corrosion?

It's better to have someone knowledgeable, like an engineer, take a look at what you want to build while it's still on paper.
 
Thanks for the information, I did not know you had to de-rate the PSI for shear stress, so that changes the calculations. There will be a steel tube substructure under the bottom plate for the forks to fit under and support the weight on the bottom, so I think that will be strong enough. Having multiple lifting lugs on each side make sense and as you said should stabilize the load, this should also decrease the shear stress of each lug.
 
Hugh99 said:
Thanks for the information, I did not know you had to de-rate the PSI for shear stress, so that changes the calculations. There will be a steel tube substructure under the bottom plate for the forks to fit under and support the weight on the bottom, so I think that will be strong enough. Having multiple lifting lugs on each side make sense and as you said should stabilize the load, this should also decrease the shear stress of each lug.
The lugs have to be carefully designed as well. If you make a lug with a 2" diameter hole and then use a 1" shackle to lift with, the stresses go up in the lug material.

Size the holes in the lifting lugs to fit one size shackle, which is rated to take the load of lifting a tank full of diesel. Each shackle size has a particular clearance between the bolt and the hoop. Don't ignore this clearance.

You must also check the pull out stress around the hole on the lug as well. Because of the potential beating the lugs are going to get, I would not recommend that they be constructed from thin gauge material. It's better, I think, to use a heavier plate for the lugs and weld them to the tank.
 
Hugh99 said:
I'm trying to build a tank to hold diesel fuel, it will be on skids to lift with a fork lift but I also want to extend the the sides to provide a way to raise the tank from two attachment points on each side. The sides will be 1/4 A36 steel plate and the rest of the tank will be 10 gauge (0.140625). The tank should weigh around 350 lbs and hold 119 gallons of diesel. Using maximums that's 119x7.5 lbs = 892.5 lbs, including the weight of the tank that is roughly 1250 lbs.

Assuming the holes at the tope of the side plate are 2 in diameter and the shear formula F = P x T X PSI
I was going to calculate P as 2 in x pi and then divide by the portion of the whole that would be in contact with the rigging, so assuming 1/4 of the perimeter is in contact with perimeter, = 1.57
F = 1.57 x .25 x 36,000
F = 14,130 lbs per hole, so I should be able to support over 28,000 pounds for the two holes.

Does my math look correct?
If I left the sides as 10 gauge, it looks like it could still support 7900 lbs per hole for total of 15,800 lbs so I may not need 1/4 plate on the sides.

Thanks
I am a mechanical engineer and have taught rigging to a fairly large group. I strongly suggest that you lift from the top so that your lifting lugs are primarily in axial stress as close to normal (90 degrees) as possible.
 
Because of the sizes and weights involved, and the inexperience of the OP, this thread should have been closed a while ago.
 
Hi all, I have a question. So from the derivation of the Isentropic process relationship PV^gamma = constant, there is a step dW = PdV, which can only be said for quasi-equilibrium (or reversible) processes. As such I believe PV^gamma = constant (and the family of equations) should not be applicable to just adiabatic processes? Ie, it should be applicable only for adiabatic + reversible = isentropic processes? However, I've seen couple of online notes/books, and...
Thread 'How can I find the cleanout for my building drain?'
I am a long distance truck driver, but I recently completed a plumbing program with Stratford Career Institute. In the chapter of my textbook Repairing DWV Systems, the author says that if there is a clog in the building drain, one can clear out the clog by using a snake augur or maybe some other type of tool into the cleanout for the building drain. The author said that the cleanout for the building drain is usually near the stack. I live in a duplex townhouse. Just out of curiosity, I...
I have an engine that uses a dry sump oiling system. The oil collection pan has three AN fittings to use for scavenging. Two of the fittings are approximately on the same level, the third is about 1/2 to 3/4 inch higher than the other two. The system ran for years with no problem using a three stage pump (one pressure and two scavenge stages). The two scavenge stages were connected at times to any two of the three AN fittings on the tank. Recently I tried an upgrade to a four stage pump...
Back
Top