Can Lead Acid Batteries Be Used in Parallel for Optimal Performance?

Click For Summary
SUMMARY

This discussion centers on the use of two 24V lead acid batteries connected in parallel for conducting drain tests. Participants emphasize the risks associated with parallel connections, particularly the potential for dangerous short circuits due to voltage mismatches. It is concluded that while theoretically one battery can be removed for testing, practical results may vary, and it is safer to discharge both batteries separately and average the results. Additionally, understanding Peukert's Law is crucial, as battery capacity is not a linear function of load.

PREREQUISITES
  • Understanding of Peukert's Law and its implications on battery capacity
  • Knowledge of electrical concepts such as voltage, current, and resistance
  • Familiarity with lead acid battery specifications and characteristics
  • Experience in conducting electrical experiments safely
NEXT STEPS
  • Research Peukert's Law and its impact on battery performance
  • Learn about safe practices for connecting batteries in parallel
  • Investigate battery matching techniques for parallel configurations
  • Explore the effects of thermal resistance on battery performance during charging and discharging
USEFUL FOR

Electrical engineers, battery technicians, and hobbyists conducting experiments with lead acid batteries or interested in optimizing battery performance in parallel configurations.

cshieldsx
Messages
6
Reaction score
0
Hello,

I have 2 24V lead acid batteries in parallel to make a power supply for my circuit. I want to do some drain tests, and plot a curve for % energy remaining vs. time. The load on the battery isn't that large, and I don't want to have to supervise my experiment for 12 hours solid.

Im presuming the curve will be the same if I take one of the batteries out (to shorten the drain time)? If I multiply my values by a factor of 2, will that be a fair representation of the system with both batteries.

I will be working out the energy remaining using V=E/Q and Q=It, the Wh/kg value I have for my batteries, and the conversion rate of 1Wh = 3.6kJ

I hope this makes sense, thanks in advance
 
Engineering news on Phys.org
cshieldsx said:
Hello,

I have 2 24V lead acid batteries in parallel to make a power supply for my circuit. I want to do some drain tests, and plot a curve for % energy remaining vs. time. The load on the battery isn't that large, and I don't want to have to supervise my experiment for 12 hours solid.

Im presuming the curve will be the same if I take one of the batteries out (to shorten the drain time)? If I multiply my values by a factor of 2, will that be a fair representation of the system with both batteries.

I will be working out the energy remaining using V=E/Q and Q=It, the Wh/kg value I have for my batteries, and the conversion rate of 1Wh = 3.6kJ

I hope this makes sense, thanks in advance

Are these batteries designed to be used in parallel? Parallel connection of batteries is not usually done, at least not connected straight together. For sure, if you drain on battery in a 1-up experiment, and then hook them back in parallel, there will be problems.
 
Connecting batteries in parallel can be very dangerous if you don't know what your doing. The reason for this is large currents going through the batteries due to differences in potential. Batteries have a relatively low internal resistance, so if you have one at 11.5v and one at 13v and connect them in parallel you are essentially creating a current unlimited short circuit that could cause one of the batteries to explode or catch fire. For batteries in parallel they must always be charged and discharged together. If you discharge one, but not the other, don't put then back in parallel again.

Back to your question, ideally no it wouldn't make a difference. But in reality, yes it will. Not all batteries are manufactured to the exact same specification, even if they are the same model of the same assembly line. The easiest and safest thing to do would be to discharge them both separately and average the results.
 
You need to study Peukerts Law before embarking on your experiment. Battery capacity is NOT a linear function of load.
http://en.wikipedia.org/wiki/Peukert's_law

Are these batteries designed to be used in parallel?
There is no such thing.

The easiest and safest thing to do would be to discharge them both separately and average the results
Equally nonsensical as the prior quote.

I want to do some drain tests, and plot a curve for % energy remaining vs. time.

Nothing wrong with conducting an experiment, but you can find many such results by looking online at manufacturer specifications
 
Naty1 said:
There is no such thing.

I suppose not, but I meant more along the lines of same type, same size/capacity, same state (age and chemistry changes due to history of use) same initial charge, etc. All to minimize differences in the voltages when connected together, and during cycling.

Might be safer to just Schottky diode-or them...
 
Naty1 said:
There is no such thing.
Well, not actually. I have seen UPSs with parallel battery banks. It is dangerous if the batteries aren't at the same voltage however. And I would not recommend doing the experiment.
"www.nyc-arecs.org/Connecting_Batteries_and_Chargers_in_Series_and_Parallel.pdf"[/URL]
 
Last edited by a moderator:
dlgoff said:
Well, not actually.

I think Naty was referring to my comment about batteries "designed" to be put in parallel, not that parallel battery banks don't exist. I think we agree that they do, but you have to be very smart and careful and know the history of the batteries before hooking up that last wire...
 
You need to study Peukerts Law before embarking on your experiment. Battery capacity is NOT a linear function of load.

He's not trying to determine the capacity based on load, he said he wants to generate a discharge curve based on a constant load.

dlgoff said:
Well, not actually.

Correct. Batteries, or rather battery packs can be designed to be use in parallel configurations by designing cells that "match" each other. "Matched" battery packs or arrays are built using cells that are manufactured to have small differences in specifications such as internal resistance and open circuit voltage so they have very little stray current between the cells. Although, this can't be done with all chemistries. For example, LiPo cells in my RC heli become unmatched after about 20 cycles.
 
Topher925 said:
Batteries, or rather battery packs can be designed to be use in parallel configurations by designing cells that "match" each other. "Matched" battery packs or arrays are built using cells that are manufactured to have small differences in specifications such as internal resistance and open circuit voltage so they have very little stray current between the cells. Although, this can't be done with all chemistries. For example, LiPo cells in my RC heli become unmatched after about 20 cycles.

Very good to know Topher. What tells you that the batteries are becoming mismatched?

As Berkeman implies, all things being equal, one should expect each battery should preform as the other, though process variations are a factor that changes things, and there are other unexpected variations such as thermal resistance to ambient during charging and discharging. Apparently Lithium Poly are very touchy?
 
Last edited:
  • #10
Naty1 said:
There is no such thing.
[...as batteries designed to be used in parallel.]

I don't know if you're talking about lead acid batteries in particular or batteries in general.

Do you think you might be able to come up with a reference, or a quote that says something about this?
 

Similar threads

  • · Replies 26 ·
Replies
26
Views
4K
  • · Replies 4 ·
Replies
4
Views
10K
  • · Replies 7 ·
Replies
7
Views
2K
  • · Replies 0 ·
Replies
0
Views
2K
  • · Replies 4 ·
Replies
4
Views
2K
Replies
2
Views
2K
Replies
4
Views
2K
  • · Replies 8 ·
Replies
8
Views
2K
Replies
7
Views
21K
  • · Replies 2 ·
Replies
2
Views
3K