Can you calulate a transformer secondary resistance by using load regulation %

Click For Summary
SUMMARY

This discussion focuses on calculating the secondary resistance of a 300 VA step-down transformer with a voltage rating of 45-0-45 Volts and a load regulation of 10%. The calculation method involves determining the voltage difference between no-load and full-load conditions, resulting in a secondary series resistance of 1.36 ohms. It is emphasized that the primary resistance must also be considered, as it is reflected by the square of the turns ratio. Ultimately, the effective secondary resistance should be taken as half of the calculated value due to the equal contribution of both secondary and reflected primary resistances to the regulation.

PREREQUISITES
  • Understanding of transformer principles, including load regulation.
  • Knowledge of Ohm's Law for calculating resistance.
  • Familiarity with circuit simulation tools like Circuit Maker Student Edition.
  • Basic concepts of primary and secondary winding resistance in transformers.
NEXT STEPS
  • Research "transformer load regulation calculations" for deeper insights.
  • Learn about "copper losses in transformers" to understand efficiency factors.
  • Explore "circuit simulation techniques" using Circuit Maker Student Edition.
  • Investigate "turns ratio impact on transformer performance" for advanced analysis.
USEFUL FOR

Electrical engineers, students studying power electronics, and anyone involved in transformer design and analysis will benefit from this discussion.

mp3streetpart
Messages
3
Reaction score
0
If I had a step down transformer of 300 VA in size at 45-0-45 Volts@3.3 Amps with a regulation of 10% could I do the following to calculate the internal resistance of the secondary winding for my power supply circuit?

Voltage * Regulation 10% to work out the voltage difference between noload and full load.

45 Volts* .1 = 4.5 volts

Secondary series resistance per winding
4.5 Volts/3.3 amps = 1.36 ohms

I know there is inductance as well but at the moment I am ignoring it.
I need to put values into circuit maker student edition to reflect the real world.
 
Engineering news on Phys.org
You need to take the primary resistance into account. It is reflected by the square of the turns ratio to the secondary, and is a quite significant contributor to regulation.

If a transformer is well designed, typically the reflected value of the primary resistance on the secondary side will be the same as the secondary intrinsic resistance (equal copper losses in both windings being the goal). Often this is close to the truth, but not always. However, in the absence of any possibility of measuring both windings' DC resistance, the best you can do is to take them to be equal.

Since both the secondary resistance AND the reflected primary resistance will contribute equally to the regulation (if the copper losses both windings are equal), you should take the secondary resistance to be half of your calculated value.
 
Ok I forgot about the primary resistance thanks for that.
 

Similar threads

Replies
2
Views
2K
  • · Replies 8 ·
Replies
8
Views
3K
Replies
6
Views
4K
Replies
2
Views
4K
  • · Replies 10 ·
Replies
10
Views
5K
  • · Replies 2 ·
Replies
2
Views
3K
  • · Replies 9 ·
Replies
9
Views
3K
  • · Replies 9 ·
Replies
9
Views
4K
Replies
5
Views
2K
  • · Replies 8 ·
Replies
8
Views
3K