JohnPinnacle
Messages
3
Reaction score
0
Hello,

Here are the knowns:
Inlet open area = 17 inches^2
Outlet open area = 30 inches^2
Internal Fans = 270 cfm (3 fans @ 90 cfm each)

What is the CFM through the system and what's the equations used to figure this out?

Thanks a ton!
John
 
Physics news on Phys.org
The fan spec is 90cfm per fan. That doesn't mean that 270cfm (3 fans) is what will exhaust out the rear of the unit. If I have a huge fan inside a box and a very little inlet or outlet, the fan will be choked and pressure will build due to the open air restriction.
 
You'll need to look at fan curves and estimate pressure drop through your system then.

Do you have a sketch you can upload?
 