Comparing Charging Currents for Underground vs. Overhead Cables

  • Thread starter Thread starter raeesi
  • Start date Start date
  • Tags Tags
    Cable
Click For Summary

Discussion Overview

The discussion centers around the differences in charging currents between underground cables and overhead lines, particularly in the context of high voltage AC power distribution. Participants explore the implications of these differences on voltage regulation, capacitance, and the advantages and disadvantages of each type of cable.

Discussion Character

  • Exploratory
  • Technical explanation
  • Debate/contested

Main Points Raised

  • Some participants suggest that underground cables take continuous relatively high charging currents due to higher line-to-line capacitance per unit length, attributed to the smaller distance between conductors and a higher dielectric constant compared to air.
  • Others note that underground cables have better voltage regulation than overhead lines, which they attribute to lower inductance resulting from the compact and well-insulated construction of underground cables.
  • Participants discuss the advantages of underground cables, including reduced susceptibility to damage from storms and lightning, while also acknowledging disadvantages such as higher costs, continuous high charging currents leading to I²R and dielectric losses, and limited power transfer capability due to lower thermal limits.
  • There is speculation about the potential economic benefits of DC power lines in reducing charging currents, with some participants expressing uncertainty about the current push for DC transmission and its implications for underground cable economics.
  • Historical context is provided regarding the economic advantages of DC transmission over AC, particularly in relation to line losses and the challenges of synchronizing AC frequency and phase.

Areas of Agreement / Disagreement

Participants express multiple competing views regarding the implications of charging currents in underground versus overhead cables, and the discussion remains unresolved on several points, particularly concerning the future of DC transmission and its economic viability.

Contextual Notes

Participants reference general observations and speculative reasoning without providing specific numerical data or established formulas, indicating a reliance on assumptions and general knowledge rather than definitive measurements.

raeesi
Messages
4
Reaction score
0
HI

why underground cables take continuous relatively high charging currents, while overhead line take less charging current

Underground cables have a better voltage regulation than overhead lines due to the lower inductance (how) formula please
 
Last edited:
Engineering news on Phys.org
raeesi said:
HI

why underground cables take continuous relatively high charging currents, while overhead line take less charging current

Underground cables have a better voltage regulation than overhead lines due to the lower inductance (how) formula please

Welcome to the PF. It would help us if you could post some links to the information you are asking about. Your questions are general enough that we would have to first guess what you are asking about, and then try to come up with answers.

Are you referring to HV AC Mains power distribution? If so, which level? What voltages? What distances?

What is the context of your question? Is this for homework or coursework? Or are you looking to design your own home-brewed power distribution grid?
 
berkeman said:
Welcome to the PF. It would help us if you could post some links to the information you are asking about. Your questions are general enough that we would have to first guess what you are asking about, and then try to come up with answers.

Are you referring to HV AC Mains power distribution? If so, which level? What voltages? What distances?

What is the context of your question? Is this for homework or coursework? Or are you looking to design your own home-brewed power distribution grid?


I am talking about 2Km for 33KV and it is HV AC
 
raeesi said:
I am talking about 2Km for 33KV and it is HV AC

Okay, and where are you getting your inductance and current numbers from?
 
berkeman said:
Okay, and where are you getting your inductance and current numbers from?


there are no numbers I am talking in general and I mentioned 33Kv and 2Km by guess

Advantages of underground cables over overhead lines are:

1-They are less liable to damage by storms or lightning.
2-Underground cables have a better voltage regulation than overhead lines due to the lower inductance they have as a result of the compact, well insulated construction.
Disadvantages of underground cables over overhead lines are:

1-the cost of underground cables is much higher than that of equivalent overhead line. High voltage cables are 8 to 15 times more expensive than equivalent overhead lines.
2-underground cables take continuous relatively high charging currents. This can cause high I2R losses as well as high dielectric losses.
3-underground cables have a limited power transfer capability caused by lower thermal limits in cable insulation.
4-cables are more liable to permanent damage following a flash-over, this is because while air, which is the insulating medium for overhead lines, is restorable, cable insulation cannot be restored if damaged by a flashover.
 
raeesi said:
HI

why underground cables take continuous relatively high charging currents, while overhead line take less charging current..
Without knowing more about underground power cables I'd speculate that the greater charging current is simply due to a higher line to line capacitance per unit length. The distance between conductors is relatively small in the underground case and the dielectric constant, whatever it may be, is greater than air: [itex]C = \epsilon_{r} \frac{A}{d}[/itex]
 
mheslep said:
Without knowing more about underground power cables I'd speculate that the greater charging current is simply due to a higher line to line capacitance per unit length. The distance between conductors is relatively small in the underground case and the dielectric constant, whatever it may be, is greater than air: [itex]C = \epsilon_{r} \frac{A}{d}[/itex]
I agree that this is the reason. After he first posted I was looking around and found this PDF on the subject of how cable ratings are dependent on charging current.
The capacitive or charging current has a limiting effect on cable rating
capacity (MW).
http://www.contactenergy.co.nz/web/pdf/our_projects/waikatowindfarm/june2008/R01_HMR_Connection_to_220kV_Main_Grid_Undergrounding_Study_Attachment1_Appendix7and8.pdf"
 
Last edited by a moderator:
thanks my friend I got some idea about charging current
 
dlgoff said:
I agree that this is the reason. After he first posted I was looking around and found this PDF on the subject of how cable ratings are dependent on charging current.

http://www.contactenergy.co.nz/web/pdf/our_projects/waikatowindfarm/june2008/R01_HMR_Connection_to_220kV_Main_Grid_Undergrounding_Study_Attachment1_Appendix7and8.pdf"

I wonder if the new push for DC power lines will see much of a economic improvement in the underground domain since the charging current goes to zero after the line is energized.
 
Last edited by a moderator:
  • #10
mheslep said:
I wonder if the new push for DC power lines will see much of a economic improvement in the underground domain since the charging current goes to zero after the line is energized.

I didn't know there was a big push for DC power lines.

Probably not since there is more infra-structure required to get the AC to DC.

CS
 
  • #11
stewartcs said:
I didn't know there was a big push for DC power lines.

Probably not since there is more infra-structure required to get the AC to DC.

CS
For a given voltage, it has always been more economical to transmit electrical power as DC rather than AC because of the greater line losses when using AC, going back to battles between Edison and Tesla. DC transmission also eliminates the challenging problem of synchronizing line frequency and phase between remote locations.

The main problem for DC has been in stepping the voltage up and down. At the time of Tesla's victory the AC transformer provided the only practical, no-moving-parts way of doing so. Technology gradually came to the rescue, and the first commercial HVDC line was installed in '54. Today high power semiconductor thyristors and FETs make DC voltage changes practical and increasingly economic, though it still doesn't compete with AC at the end points. Thus at the moment HVDC is only used on very long lines where the power savings pays for the end equipment; underground and undersea cables are even more attractive for DC for the reasons discussed up thread. Recently alternative energy sources such as wind and concentrated solar, where the source is variable and often far removed from the load, have stepped up the buzz on HVDC.
See e.g.
http://www.abb.co.uk/cawp/gad02181/5950ab82df908d0cc1256e89002f3e6f.aspx?
 
Last edited by a moderator:
  • #12
mheslep said:
For a given voltage, it has always been more economical to transmit electrical power as DC rather than AC because of the greater line losses when using AC, going back to battles between Edison and Tesla. DC transmission also eliminates the challenging problem of synchronizing line frequency and phase between remote locations.

The main problem for DC has been in stepping the voltage up and down. At the time of Tesla's victory the AC transformer provided the only practical, no-moving-parts way of doing so. Technology gradually came to the rescue, and the first commercial HVDC line was installed in '54. Today high power semiconductor thyristors and FETs make DC voltage changes practical and increasingly economic, though it still doesn't compete with AC at the end points. Thus at the moment HVDC is only used on very long lines where the power savings pays for the end equipment; underground and undersea cables are even more attractive for DC for the reasons discussed up thread. Recently alternative energy sources such as wind and concentrated solar, where the source is variable and often far removed from the load, have stepped up the buzz on HVDC.
See e.g.
http://www.abb.co.uk/cawp/gad02181/5950ab82df908d0cc1256e89002f3e6f.aspx?

I found a little more info on the pros and cons of AC vs. DC:

http://en.wikipedia.org/wiki/High-voltage_direct_current#Advantages_of_HVDC_over_AC_transmission

It was quite interesting to read.

CS
 
Last edited by a moderator:

Similar threads

Replies
2
Views
2K
  • · Replies 1 ·
Replies
1
Views
2K
  • · Replies 4 ·
Replies
4
Views
6K
Replies
10
Views
6K
  • · Replies 21 ·
Replies
21
Views
6K
Replies
1
Views
2K
  • · Replies 8 ·
Replies
8
Views
6K
Replies
31
Views
5K
Replies
5
Views
3K
  • · Replies 26 ·
Replies
26
Views
3K