Converting frequency to current for an ac generator

Click For Summary
SUMMARY

The discussion centers on calculating current output from a single-phase alternating current (AC) generator operating at 50 Hz and producing 120 volts. It is established that without a load, the current is zero amps. To determine the current under load, users should apply Ohm's Law (E=IR) and check the generator's specifications, such as VA rating, which can indicate maximum current output. Practical testing with resistive loads, such as 120-volt lamps, is suggested as a last resort if manufacturer data is unavailable.

PREREQUISITES
  • Understanding of Ohm's Law (E=IR)
  • Familiarity with AC generator specifications
  • Basic knowledge of electrical load concepts
  • Safety practices for working with electrical equipment
NEXT STEPS
  • Research the specifications of single-phase AC generators
  • Learn about calculating current using Ohm's Law
  • Explore methods for safely testing electrical loads
  • Investigate common electrical components like VA ratings and their implications
USEFUL FOR

Environmental engineering students, electrical engineering students, hobbyists working with AC generators, and anyone interested in understanding electrical load calculations.

bacchus
Messages
1
Reaction score
0
before anyone has a good laugh at me, I am studying environemental engineering and have to do a course that has some electronics it.

i have a single phase alternating current (50 Hz) generator that produces 120 volts. I need to calculate the current from this information.

can anyone help me?

Thanks
 
Engineering news on Phys.org
With nothing but that open circuit, there's no load, therefore no current.

That would be zero amps.
 
If you had a known load, and knew the resistance of said load you could figure the amp draw by using Ohm's law, E=IR.
 
Have a look on the side of the generator. There should be a metal plate that gives more information than that.
If there is a number like 500 VA this will tell you the generator can deliver 4.16 amps (500 VA / 120 V = 4.16 A).

At the very least, there may be a makers name and model number which you may be able to check on Internet or with some phone calls.

Failing all that, you can get some 120 volt lamps and start wiring them (safely!) across the generator and then measuring the output voltage. If you are already getting 120 volts out of it, field coil excitation has been supplied internally.
Measure the total current when the 120 volts drops by, say, 10 % with constant speed drive.

But testing it yourself should be a last resort. Try to find the maker's data.
 
Most likely this can only be answered by an "old timer". I am making measurements on an uA709 op amp (metal can). I would like to calculate the frequency rolloff curves (I can measure them). I assume the compensation is via the miller effect. To do the calculations I would need to know the gain of the transistors and the effective resistance seen at the compensation terminals, not including the values I put there. Anyone know those values?

Similar threads

Replies
30
Views
1K
  • · Replies 26 ·
Replies
26
Views
3K
  • · Replies 15 ·
Replies
15
Views
3K
  • · Replies 6 ·
Replies
6
Views
3K
  • · Replies 12 ·
Replies
12
Views
6K
Replies
10
Views
3K
  • · Replies 21 ·
Replies
21
Views
5K
Replies
9
Views
2K
Replies
7
Views
2K
  • · Replies 3 ·
Replies
3
Views
2K