Deflection of fixed beam with point load at center

Click For Summary
SUMMARY

The maximum deflection of a 20.5ft C3x5 steel channel with a point load of 921.86lbs at the center can be calculated using the formula PL^3/192EI, resulting in approximately 1.5 inches of deflection. The moment of inertia is 1.86 in^4, and the modulus of elasticity (E) is 30,000,000 psi. If the beam is simply supported, the deflection increases fourfold, and the stresses double, raising concerns about the beam's suitability for the load without proper lateral support to prevent flange buckling.

PREREQUISITES
  • Understanding of beam deflection formulas
  • Knowledge of moment of inertia and its significance in structural engineering
  • Familiarity with modulus of elasticity in materials
  • Concepts of lateral support and local flange buckling in steel beams
NEXT STEPS
  • Research the effects of lateral support on beam performance
  • Learn about the implications of shear center loading on steel beams
  • Explore methods to calculate allowable stress in structural steel
  • Investigate alternative beam profiles for improved load-bearing capacity
USEFUL FOR

Civil engineers, structural designers, and anyone involved in the analysis and design of steel beam structures will benefit from this discussion.

blake92
Messages
50
Reaction score
0
i have a 20.5ft c3x5 steel channel with a point load at the exact center and i wanted to determine its maximum deflection.

the point load is 921.86lbs, and moment of inertia is 1.86in^4.

modulus of E= 30,000,000psi
 
Engineering news on Phys.org
I'm sorry you are not finding help at the moment. Is there any additional information you can share with us?
 
blake92 said:
i have a 20.5ft c3x5 steel channel with a point load at the exact center and i wanted to determine its maximum deflection.

the point load is 921.86lbs, and moment of inertia is 1.86in^4.

modulus of E= 30,000,000psi
if the beam is truly fixed against rotation at both ends, max deflection occurs at midpoint and is equal to PL^3/192EI , or near an inch and a half for your load and beam length and size. But, you have to be careful using long channels because stresses may be excessive if the beam is not laterally supported against local flange buckling, and loading not at the shear center causes additional torsional and warping stresses. If the beam is simply supported, stresses double and deflection increases fourfold. Seems like a very flimsy channel to use for this loading. Allowable stress is a great concern.
 
Had my central air system checked when it sortta wasn't working. I guess I hadn't replaced the filter. Guy suggested I might want to get a UV filter accessory. He said it would "kill bugs and particulates". I know UV can kill the former, not sure how he thinks it's gonna murder the latter. Now I'm finding out there's more than one type of UV filter: one for the air flow and one for the coil. He was suggesting we might get one for the air flow, but now we'll have to change the bulb...

Similar threads

Replies
33
Views
5K
Replies
3
Views
3K
  • · Replies 5 ·
Replies
5
Views
6K
Replies
6
Views
4K
  • · Replies 8 ·
Replies
8
Views
3K
  • · Replies 2 ·
Replies
2
Views
3K
  • · Replies 1 ·
Replies
1
Views
1K
  • · Replies 8 ·
Replies
8
Views
2K
Replies
5
Views
2K
  • · Replies 10 ·
Replies
10
Views
2K