Delta Transformers on Wye Distribution System

Click For Summary
SUMMARY

Connecting a Wye generation scheme directly to a transformer with a Delta primary is feasible and practiced, particularly in large generators (Sn > 50 MVA) that utilize direct grounding methods. The generator neutral is often resistance grounded to limit fault currents, preventing electrical explosions during ground faults. Surge arrestors' MCOV ratings at the high side of a transformer are critical for ensuring system stability, although specific details on their application were not discussed. The grounding resistor's design is essential for protecting equipment, as demonstrated by a case where a generator successfully tripped on a ground fault without sustaining damage.

PREREQUISITES
  • Understanding of Wye and Delta transformer configurations
  • Knowledge of grounding methods for generators, including resistance grounding
  • Familiarity with surge arrestors and their MCOV ratings
  • Basic principles of electrical fault protection and monitoring systems
NEXT STEPS
  • Research the implications of Wye and Delta transformer connections in power generation
  • Learn about resistance grounding techniques and their advantages in generator systems
  • Study surge arrestor specifications and their role in transformer protection
  • Explore fault detection and monitoring systems for high-capacity generators
USEFUL FOR

Electrical engineers, power system designers, and professionals involved in generator and transformer installations will benefit from this discussion, particularly those focused on grounding practices and fault protection strategies.

Josh111
Messages
37
Reaction score
0
Hopefully this has not already been asked. It would be hard to do a forum search with the right words to find it if it has been already.

I am wondering if it is ever possible or common place to generate power in a Wye generation scheme and then connect it directly to a transformer with a Delta primary.

If this is done, what would be the major setbacks.

Also, how would one MCOV ratings of elbow arrestors at the high side of a transformer?
 
Engineering news on Phys.org
Josh111 said:
I am wondering if it is ever possible or common place to generate power in a Wye generation scheme and then connect it directly to a transformer with a Delta primary.
Possible of course.
 
That's how our central station main generator is connected to the main stepup transformer. Generator neutral was resistance grounded .

I don't know anything about the surge arrestors.
 
jim hardy said:
That's how our central station main generator is connected to the main stepup transformer. Generator neutral was resistance grounded .

I don't know anything about the surge arrestors.
I found this Addressing Ground Faults on MV Generators from our old friend, http://ecmweb.com/. They address advantages/disadvantages of Low & high impedance grounding and single & multiple point grounding. Then they show an optimal Hybrid grounding solution.

907ecmPQfig7.jpg
I Love their site. :approve:
 
  • Like
Likes jim hardy
Big sync generators (Sn>50 MVA) I know of, are directly grounded (at least that's the practice in my country). However, I know case where a relatively small generator (Sn< 10 MVA) is grounded via quite a large Petersen coil.
 
zoki85 said:
Big sync generators (Sn>50 MVA) I know of, are directly grounded (at least that's the practice in my country). However, I know case where a relatively small generator (Sn< 10 MVA) is grounded via quite a large Petersen coil.

I find that surprising. The reason for the resistor is to limit current to just a few amps should a ground fault develop, so there's not an electrical explosion.
Our machine was 894MVA at 22kv. Ten amps at 22kv is of course 220KW so the grounding resistor was big as a pickup truck. A relay monitors the voltage across it and trips the unit in case of a ground fault.
That design pays off - at another plant somebody left a wrench inside the generator. When it fell shorting one terminal to frame the unit tripped on "ground fault" with no damage, just had to go in and retrieve the wrench.
 
jim hardy said:
I find that surprising. The reason for the resistor is to limit current to just a few amps should a ground fault develop, so there's not an electrical explosion.
Our machine was 894MVA at 22kv. Ten amps at 22kv is of course 220KW so the grounding resistor was big as a pickup truck. A relay monitors the voltage across it and trips the unit in case of a ground fault.
That design pays off - at another plant somebody left a wrench inside the generator. When it fell shorting one terminal to frame the unit tripped on "ground fault" with no damage, just had to go in and retrieve the wrench.
Jim, you are right! I rechecked my data and big generators in my country are also impedance-grounded on regular basis. I don't know why but seems I confused generators data with HV power transformers...o:)
 

Similar threads

  • · Replies 1 ·
Replies
1
Views
2K
  • · Replies 8 ·
Replies
8
Views
3K
Replies
9
Views
2K
  • · Replies 11 ·
Replies
11
Views
6K
  • · Replies 1 ·
Replies
1
Views
5K
  • · Replies 5 ·
Replies
5
Views
6K
  • · Replies 16 ·
Replies
16
Views
4K
Replies
14
Views
3K
  • · Replies 18 ·
Replies
18
Views
4K
  • · Replies 8 ·
Replies
8
Views
11K