Delta wye connection using 3 small transformers

Click For Summary

Discussion Overview

The discussion revolves around the wiring of three small transformers to create a delta-wye connection. Participants explore the implications of different configurations for the primary and secondary sides, particularly concerning the connections labeled X1 and X2, and their impact on phase relationships and output characteristics.

Discussion Character

  • Technical explanation
  • Debate/contested

Main Points Raised

  • One participant expresses confusion regarding the wiring diagrams for delta-wye connections, specifically about whether to use X1 or X2 for neutral connections.
  • Another participant notes that connecting all X2 together or all X1 together will yield a three-phase output, but there may be a 180-degree phase difference depending on the connection used.
  • Concerns are raised about the implications of using different connections for applications such as rectifiers versus phase control circuits.
  • A participant recommends using NEMA standardized connections, emphasizing that the higher voltage side should be labeled to reflect a 30-degree phase lead over the lower voltage side.
  • Detailed wiring instructions are provided for both the wye and delta sides, including suggestions for grounding the neutral connection based on the application.
  • One participant mentions the importance of polarity dots in schematics to aid in understanding the phase relationships in the transformer configurations.

Areas of Agreement / Disagreement

Participants do not reach a consensus on the optimal configuration for the neutral connections, as differing opinions on the implications of using X1 versus X2 remain. The discussion includes multiple competing views on the effects of these configurations on phase relationships and application suitability.

Contextual Notes

Some assumptions about the application context and specific circuit requirements are not fully explored, leaving room for uncertainty regarding the best practices for wiring configurations.

sauce6358
Messages
3
Reaction score
0
I am confused from a couple of diagrams I have about how to correctly wire 3 small transformers to form a delta wye connection. The transformers are labeled as
Primary H1 H2, H1 H2, H1 H2
Secondary X2 X1, X2 X1, X2 X1

My question is in all the diagrams I have the Delta connections are identical, but the wye connections in one of the diagrams shows all of X1's tied together to form the neutral and another diagram shows all of X2's tied together to form the neutral. So does it matter whether I use X1's as the hot connections and X2's as the neutral connections or viceversa?
THANKS!
 
Engineering news on Phys.org
Connecting all X2 together will give 3 phase output.
Connecting all X1 together will give 3 phase output.
There will be a difference of 180 degrees between the 3 phases depending on which connection is used. ?There may be a difference in phase rotation, will have to think about that?
The output voltage will be the same for both connections.
If you are using the output for a rectifier the connection will not make any difference.
If you are using the output for phase control, it may make a difference depending on the circuit you are using.
 
Is the higher voltage side connected in wye? I would recommend using NEMA standardized connections. The industry practice is that the higher voltage side be labeled so as the line to line voltages on the high voltage side lead those of the low voltage side by 30 degrees electrical phase.

If the high side is in wye, low side in delta, here are the connections:

Y-side: Let us use "H2" as the neutrals. All 3 "H2" terminals are joined. Phase A hot connects to H1 of xfmr A, phase B hot connects to H1 of xfmr B, phase C hot connects to H1 of xfmr C. If this Y-side is a secondary, then it might be desirable to connect the neutral (H2-H2-H2) to Earth ground. It depends on the application. If the Y-side is the primary, then an Earth ground may already be present. Definitely check if you need to have the neutral grounded.

Delta-side: Connect X2 of xfmr A to X1 of xfmr B. Connect X2 of xfmr B to X1 of xfmr C. Connect X2 of xfmr C to X1 of xfmr A. Then label as follows.

The junction of xfmr A X1 & xfmr C X2 becomes phase A. The junction of xfmr B X1 & xfmr A X2 becomes phase B. The junction of xfmr C X1 & xfmr B X2 becomes phase C.

With these connections & phase labeling, the line to line voltages on the lower voltage delta side will lag those on the higher voltage wye side by 30 degrees, in accordance w/ power industry standard practice in North America. I.e. the A-B line-to-line voltage on the wye side leads the A-B l-l voltage on the delta side by 30 degrees.

If you're using the delta as the high side, let me know & I'll help you, as the designations would be different. Have I helped? Later, I'll attach a sketch.

Claude
 
cabraham said:
Is the higher voltage side connected in wye? I would recommend using NEMA standardized connections. The industry practice is that the higher voltage side be labeled so as the line to line voltages on the high voltage side lead those of the low voltage side by 30 degrees electrical phase.

If the high side is in wye, low side in delta, here are the connections:

Y-side: Let us use "H2" as the neutrals. All 3 "H2" terminals are joined. Phase A hot connects to H1 of xfmr A, phase B hot connects to H1 of xfmr B, phase C hot connects to H1 of xfmr C. If this Y-side is a secondary, then it might be desirable to connect the neutral (H2-H2-H2) to Earth ground. It depends on the application. If the Y-side is the primary, then an Earth ground may already be present. Definitely check if you need to have the neutral grounded.

Delta-side: Connect X2 of xfmr A to X1 of xfmr B. Connect X2 of xfmr B to X1 of xfmr C. Connect X2 of xfmr C to X1 of xfmr A. Then label as follows.

The junction of xfmr A X1 & xfmr C X2 becomes phase A. The junction of xfmr B X1 & xfmr A X2 becomes phase B. The junction of xfmr C X1 & xfmr B X2 becomes phase C.

With these connections & phase labeling, the line to line voltages on the lower voltage delta side will lag those on the higher voltage wye side by 30 degrees, in accordance w/ power industry standard practice in North America. I.e. the A-B line-to-line voltage on the wye side leads the A-B l-l voltage on the delta side by 30 degrees.

If you're using the delta as the high side, let me know & I'll help you, as the designations would be different. Have I helped? Later, I'll attach a sketch.

Claude

Yes, Delta Primary Side and Wye Secondary Side. High/Low. Thanks!
 
The attached pdf details how to obtain the industry standard high voltage side 30 degree phase lead using a wye-delta as well as a delta-wye xfmr configuration. I added polarity dots to the schematics as a visual aid. This should be what you are looking for. Hopefully it is legible.

Claude
 

Attachments

cabraham said:
The attached pdf details how to obtain the industry standard high voltage side 30 degree phase lead using a wye-delta as well as a delta-wye xfmr configuration. I added polarity dots to the schematics as a visual aid. This should be what you are looking for. Hopefully it is legible.

Claude

Thanks So Much! Sauce
 

Similar threads

  • · Replies 1 ·
Replies
1
Views
2K
  • · Replies 20 ·
Replies
20
Views
3K
  • · Replies 1 ·
Replies
1
Views
2K
  • · Replies 6 ·
Replies
6
Views
3K
  • · Replies 22 ·
Replies
22
Views
8K
Replies
9
Views
2K
  • · Replies 7 ·
Replies
7
Views
3K
Replies
0
Views
2K
Replies
4
Views
4K
Replies
3
Views
2K