Fixing Static Electricity Issues: Tips from an Electrician

AI Thread Summary
Static electricity is causing repeated damage to garage door openers located in a pole barn, particularly after electrical storms. The barn is grounded, but the effectiveness of this grounding is in question, as well as the potential for static charge accumulation. Suggestions include installing a lightning rod to dissipate static electricity and ensure proper grounding of the barn's wiring. Concerns about attracting lightning with a lightning rod are addressed, emphasizing that it can help prevent static discharge. Overall, improving grounding and considering external static dissipation methods are critical to protecting the electronics from damage.
  • #51
gtacs said:
As far as the whole house protectors you mentioned, I did read a fair amount on those.
Your telco's switching computer is typically exposed to 100 surges with each storm. How often is your town without phone service for four days while they replace their $multi-million computer? 'Whole house' protector was how protection was done even 100 years ago when operators had headsets attached to their ears during every thunderstorm. Technology is that well proven. And that little known when so many only know what advertising promotes.

Critical to protection is hundreds of thousands of joules absorbed harmlessly outside the building. Any homeowner can upgrade his earthing to both meet and exceed post 1990 code requirements. Increased earthing at massive cost makes minor improvements. Since earthing - not a protector - does protection, then high reliability facilities spend $thousands more on earthing to have that little better improvement. The point – a protector is only as effective as its Earth ground.

That antenna example demonstrated so many electrical concepts unknown even to electricians. That are critical to surge protection. Repeatedly posted was a one example: low impedance (ie 'less than 10 feet'). Even sharp wire bends increase impedance; subvert protection. Sharp bends are not a problem for 60 Hz electricity. But are a major problem for effective protection.

A ground wire inside metallic conduit is also not sufficiently conductive for surge protection.

More responsible companies provide these well proven solutions. Including ABB, Siemens, Leviton, Intermatic, General Electric, Polyphaser, and Square D. One 'whole house' protector for the entire house sells in Lowes and Home Depot for less than $50. Superior protection typically costs tens or 100 times less money. Effective protection is found in a profit center.

Lightning is typically 20,000 amps. So a minimal 'whole house' protector is rated at about 50,000 amps. Effective protection means direct lightning strikes are connected harmlessly to Earth outside the building. Even a protector is not damaged.

Effective protection means nobody even knows a surge existed. Even the protector does not fail.

All appliances contain superior protection. Your concern is a rare transient (typically once every seven years) that might overwhelm existing protection. Informed homeowners do what is done in every telco switching center, broadcasting station and even in munitions dumps.

Upgrade earthing. Connect every single wire in every incoming cable short (ie 'less than 10 feet') to single point Earth ground. That means protection from all types of surges (inclduing normal mode). Connection made either by a wire or by one 'whole house' protector. Then hundreds of thousands of joules dissipate harmlessly outside the building. Then nobody even knows a surge existed.
 
Engineering news on Phys.org
  • #52
Thanks westom for that expound... now it's clear what you meant by

"" Connect every single wire in every incoming cable short (ie 'less than 10 feet') to single point Earth ground. "

not literally of course
but through an overvoltage(surge) protector.
I assume you are suggesting such a protector at entrance to barn?

Now it makes sense.

Are gas discharge tubes still the fastest ? I haven't messed with them in twenty years.
Perhaps you'd post links to spec sheets for a couple of your favorite protectors.



old jim
 
  • #53
jim hardy said:
Thanks westom for that expound... now it's clear what you meant by
"" Connect every single wire in every incoming cable short (ie 'less than 10 feet') to single point Earth ground. "

not literally of course but ...
Some wires have better protection when no protector exists. When the wire literally connects to Earth (ie satellite dish, cable TV, AC neutral wire). Other wires only have a protector (ie telephone) because, if earthed by wire, then service would not be possible. The NIST (US government research agency that studies this stuff) says same:
> What these protective devices do is neither suppress nor arrest a surge,
> but simply divert it to ground, where it can do no harm.

Divert as in bond, shunt, connect, conduct, or switch. Dr Kenneth Schneider writes:
>Conceptually, lightning protection devices are switches to ground. Once a
> threatening surge is detected, a lightning protection device grounds the
> incoming signal connection point of the equipment being protected. Thus,
> redirecting the threatening surge on a path-of-least resistance (impedance)
> to ground where it is absorbed.

All protector devices are more than fast enough. For example, an MOV must also state how many inches down its lead that speed test is conducted. Because even 2 inch leads will change the response time. Gas Discharge Tubes (GDTs) do not have life expectancy that other newer solutions (MOV, semiconductor) provide. GDTs are used when capacitance is important. For example, telcos replaced GDTs with other MOV like devices sometimes called 'the carbons'. And then obsoleted those with semiconductors.

Favorite protector depends on what is to be protected. For AC mains (the OP's problem), a best solutions come from more responsible companies including General Electric, Square D, Siemens, ABB, Intermatic, Leviton, and Polyphaser. All use MOVs - the best protector per dollar for that application. Are rated at about 50,000 amps. A Cutler-Hammer version sells in Lowes and Home Depot for less than $50.
 
  • #54
westom said:
Critical to protection is hundreds of thousands of joules absorbed harmlessly outside the building. Any homeowner can upgrade his earthing to both meet and exceed post 1990 code requirements. Increased earthing at massive cost makes minor improvements. Since earthing - not a protector - does protection, then high reliability facilities spend $thousands more on earthing to have that little better improvement. The point – a protector is only as effective as its Earth ground.

Point of use protectors do not work primarily by earthing a surge.

Excellent information on surges and surge protection is available from the IEEE:
<http://www.lightningsafety.com/nlsi_lhm/IEEE_Guide.pdf>
A simpler guide aimed at the unwashed masses is from the US-NIST:
<http://www.nist.gov/public_affairs/practiceguides/surgesfnl.pdf>

westom said:
Lightning is typically 20,000 amps. So a minimal 'whole house' protector is rated at about 50,000 amps. Effective protection means direct lightning strikes are connected harmlessly to Earth outside the building. Even a protector is not damaged.

An investigation done by the author of the NIST surge guide found that the maximum current that has any reasonable probability of occurring on each hot service wire is 10,000A. (There is a reference to that in the IEEE surge guide.) That current is based on a 100,000A lightning hit to a utility pole adjacent to a house in typical urban distribution. It is very unlikely there will be a worse event.

The IEEE surge guide suggests a 20,000 - 70,000A per wire rating for houses for a service panel protector, or 40,000 - 120,000A in high lightning areas. Ratings far above the likely event current give a long life for the protector.

Service panel protectors are a good idea.
But from the NIST surge guide:
"Q - Will a surge protector installed at the service entrance be sufficient for the whole house?
A - There are two answers to than question: Yes for one-link appliances [electronic equipment], No for two-link appliances [equipment connected to power AND phone or cable or...]. Since most homes today have some kind of two-link appliances, the prudent answer to the question would be NO - but that does not mean that a surge protector installed at the service entrance is useless."

That is because the NIST surge guide suggests that most equipment damage is from high voltage between power and phone/cable/.. wires. Service panel protectors are likely to protect anything connected only to power wiring.

The NIST surge guide says:
"Intruder alarm systems using wires between sensors and their central control unit can be disturbed - and damaged in severe cases - by lightning striking close to the house. The wires necessary for this type of installation extend to all points of the house and act as an antenna system that collects energy from the field generated by the lightning strike, and protection should be included in the design of the system, rather than added later by the owner."

Damage with wiring acting as an antenna would require a nearby strike.

I expect the surge protector from Sears will eliminate the damage. Point of use protectors work by limiting the voltage on all wires to the ground at the protector. The voltage between the wires going to the protected equipment is safe for the protected equipment. They do not work primarily by earthing a surge. For protection, all wires to a set of equipment must go through the protector. In this case, it sounds like the manufacturer did not provide internal protection for control wiring. (There is an example of how point of use protectors work in the IEEE surge guide starting page 30.)

westom said:
All appliances contain superior protection.

Some equipment contains no surge protection. Little, if any, is "superior".

-------------------------------
Ground rods are not particularly good earthing electrodes. A very good resistance to Earth might be 10 ohms. If you have a 1,000A surge current earthed through a rod the system ground potential would rise 10,000V above 'absolute' Earth potential. About of 70% of the voltage drop through the Earth away from the rod is in the first 3 feet. The voltage to system ground a little way from the rod would be 7,000V or higher. Jim had a nice example of that. The potential of the Earth at the pole, house, garage and pole barn may be very different during a surge.

With the pole barn connected including a supply ground, pole barn system ground and earthing electrode and supply ground connect together. The neutral is not connected and neutral (and hots) can have a far different potential than the pole barn system ground during an 'event'.

Another way remote buildings could be connected in the past is no source ground wire and the building is connected like a service with system ground and earthing electrode connected to the neutral. I prefer this for surge protection. If you use a entrance panel protector, this uses a 3 wire protector, like at the service. For the connection above, a 4 wire protector is required, with separate ground and neutral wires. I would prefer to have my own entrance protector, not one supplied by the utility.

According to the IEEE surge guide, over 90% of protectors (service entrance and point of use) use MOVs for the voltage limiting element for power wiring. MOVs are plenty fast enough for surges. Gas discharge tubes take a short time to establish an arc and may not catch the start of the surge.
 
Last edited by a moderator:
  • #55
westom said:
Some wires have better protection when no protector exists. When the wire literally connects to Earth (ie satellite dish, cable TV, AC neutral wire).

The building entrance protection required for coax (cable, dish) is a ground block that ties the coax shield to the building system ground. That does not limit the voltage on the center conductor, and the IEEE surge guide says that the center conductor to shield voltage is limited only by breakdown voltage of F connectors, typically 2000-4000V. And "there is obviously the possibility of damage to TV tuners and cable modems from the very high voltages that can be developed, especially from nearby lightning."

westom said:
The NIST (US government research agency that studies this stuff) says same:
> What these protective devices do is neither suppress nor arrest a surge,
> but simply divert it to ground, where it can do no harm.

Point of use protectors don't primarily protect by earthing a surge. The NIST (and IEEE) surge guides clearly say they are effective.

westom said:
For example, an MOV must also state how many inches down its lead that speed test is conducted. Because even 2 inch leads will change the response time.

The response time is not affected. The clamp voltage is raised as the lead length gets longer. (This is covered in the IEEE surge guide.)
 
  • #56
Those are two great links, Bud.

From IEEE: ""In general, there is little understanding of
how the different parts of the protection system need to work together."
Isn't that the truth! They tied up some loose ends for me..

Thanks!

As an IEEE guy you might enjoy "Modern Jupiter", a biography of Charles Steinmetz.

Steinmetz was GE's counterpart to Westinghouse's Tesla.
He built a lab to study lightning that was right out of a Mad Scientist movie.

An avowed socialist, he was written out of the textbooks in cold war years.
I only heard of him from an old-timer educated before WW2 , so i read that book.
https://www.amazon.com/dp/B0029Z1F2Q/?tag=pfamazon01-20
He is mentioned frequently (in present tense) in my 1901 electric motors book .
Maybe he's back in the textbooks by now - i don't know.
He sure deserves to be - he was as much a pioneer as Tesla, even if less colorful.



old jim
 
Last edited by a moderator:
  • #57
Very informative links Bud, and thanks for the rewrite westom.

I am curious, what happens to the surge once it enters an AC to DC powersupply? Is the powersupply normally the failed component?
 
  • #58
jim hardy said:
From IEEE: ""In general, there is little understanding of
how the different parts of the protection system need to work together."
Isn't that the truth! They tied up some loose ends for me..
Those links provide important facts that Bud routinely forgets to mention. For example, the NIST says quite bluntly what a protector does when not properly earthed:
> A very important point to keep in mind is that your surge protector will work by
> diverting the surges to ground. The best surge protection in the world can be
> useless if grounding is not done properly.

That point was made repeatedly. Either a protector connects energy harmlessly to earth. Or it does ineffective protection.

That IEEE citation shows what happens when a protector is too close to electronics and too far from Earth ground. Page 42 Figure 8 shows the power strip protector earthing a surge 8000 volts destructively through TV2. Where is protection? Once energy is inside, then nothing stops a destructive hunt for earth. It will Earth via the connected TV or any other nearby appliances. A surge simply selects a best appliance to damage. In figure 8, TV2 was damaged when the protector earthed a surge 8000 volts destructively.

Bud said, "Point of use protectors do not work primarily by earthing a surge." So what do they do? If it does not Earth energy, then it must either stop, block or absorb that energy. How do 2 centimeter parts in a protector stop what three miles of sky could not? It doesn't. How does a protector (rated for hundreds of joules) absorb hundreds of thousands of joules? It doesn't. As long as claims are made subjectively, then a plug-in protector can do miracles. Once we add facts and numbers from the NIST, IEEE, and a long list of professionals, then a power strip is near zero protection.

Effective protection always means energy diverted (shunted, bonded, connected) harmlessly outside to earth. Otherwise a protector must somehow block or absorb that energy. No protector does that even though professional sales promoters routinely make that claim.

NIST said, "The best surge protection in the world can be useless if grounding is not done properly." Therefore protectors that will somehow block that current or somehow absorb that energy do not even claim to do protection. A professional sales promoter for power strip protectors claims plug-in protectors will magically stop or absorb surges. How? His NIST citation says otherwise. His IEEE citation shows how a protector, too close to appliances and too far from earth, grounded an 8000 volt surge destructively through a nearby appliance.

The NIST did not just called a plug-in protector ineffective. NIST called it 'useless'. Protection is always about where energy dissipates. Protection always means discussing where energy dissipates. Always.

Lightning surge is typically 20,000 amps. An IEEE paper from 1979 entitled "Coordination of Surge Protectors in Low-Voltage AC Power Circuits" shows a 100,000 amps surge to AC mains down the street. Figure 8 in that paper shows 30 kA going in other directions. 40 kA is earthed via a utility transformer ground. And 30 kA into the nearby house. In each case, surge current will find Earth ground. So that 30 kA remains that low, the utility's Earth ground must be intact. An informed homeowner inspects his primary surge protection system. A picture demonstrates what to inspect so that up to 40,000 amps obtains Earth out at the street. Does not seek Earth destructively via appliances and other homes. All homeowners (including the OP) are encouraged to inspect what is shown in this picture:
http://www.tvtower.com/fpl.html

Most will never see a 100,000 amp surge. Most lightning strikes are closer to 20,000 amps. So that all surges do not even damage a protector, a minimal 'whole house' protector starts at 50,000 amps. These are provided by more responsible companies.

Most of what his post is irrelevant to the OP's problem and a solution. But a coax protector claim demonstrates why cable TV does not need any protector. Richard Harrison, a broadcasting engineer who made lightning irrelevant all his professional life, said in "Lightning Arrester" in the newsgroup rec.radio.amateur.antenna:
> Coax, inside, rejects common-mode propagation of lightning energy.

That would only be understood by few who actually learn these engineering concepts. But more important is a fact relevant to the OP's problem. Common-mode explains damage to the OP's door closer. Common-mode is also why cable TV must always have its shield connected to single point Earth ground. And rarely needs a coax cable protector. What must always exist to have protection? Single point Earth ground. If selling protectors without earthing, then that engineering reality must be denied. If trying to avert more garage door failures, then AC wires entering that garage without earthing must be corrected.

IEEE even gives numbers in a Standard called The Green Book entitled 'Static and Lightning Protection Grounding':
> Lightning cannot be prevented; it can only be intercepted or diverted to a
> path which will, if well designed and constructed, not result in damage.
> Even this means is not positive, providing only 99.5-99.9% protection.

"Well designed and constructed" were defined previously. Short (ie 'less than 10 feet'), no sharp wire bends, ground wire separated from other non-grounding wires, no metallic conduit, etc. Missing earthing explains the OP's garage door damage.

Yes, the IEEE says plug-in protectors can add protection. But only if a 'whole house' solution is implemented. IEEE then says how much protection. A properly earthed protector does 99+% of the protection. That leaves a power strip to add maybe add another 0.2%. Yes, he is correct that a plug-in protector costing $40 or $100 might increase protection ... by another 0.2%. He also forgets to mention the power strip is "useless" without a properly earthed 'whole house' protector.

IEEE citation also says what only one properly earthed 'whole house' protector will do:
> Still, a 99.5% protection level will reduce the incidence of direct strokes from
> one stroke per 30 years ... to one stroke per 6000 years ...

The OP has garage door damage because 1) a surge entered due to no earthing, and 2) the surge found Earth destructively through that garage door. Protection is always about where energy dissipates. Any protector that will somehow magically make energy disappear is best called a profit center.
 
Last edited by a moderator:
  • #59
gtacs said:
I am curious, what happens to the surge once it enters an AC to DC powersupply? Is the powersupply normally the failed component?
The power supply is why electronics have protection superior to anything connected to its power cord.

Appreciate how power supplies worked even before the IBM PC existed. That 120 VAC is filtered. Then converted to high voltage (well over 300 volts) DC. Then filtered again. Then converted to high voltage radio waves. All part of making electronics immune from most anomalies on AC mains. And why transients also do not get through a supply.

Design standards in 1970 required 120 volt supplies to withstand 600 volts without damage. Today, standards require more like 1000 volt transients without damage.

A protector too close to a computer may sometimes bypass that supply protection. I just fixed a multifunction printer damaged just for that reason. It was on a power strip protector. Building owner is now installing 'whole house' protectors in all buildings to avert what has been repeat damage to electronics connected to power strip protectors.
 
  • #60
jim hardy said:
As an IEEE guy you might enjoy "Modern Jupiter", a biography of Charles Steinmetz.

Steinmetz was GE's counterpart to Westinghouse's Tesla.
He built a lab to study lightning that was right out of a Mad Scientist movie.

An avowed socialist, he was written out of the textbooks in cold war years.
I only heard of him from an old-timer educated before WW2 , so i read that book.
https://www.amazon.com/dp/B0029Z1F2Q/?tag=pfamazon01-20
He is mentioned frequently (in present tense) in my 1901 electric motors book .
Maybe he's back in the textbooks by now - i don't know.
He sure deserves to be - he was as much a pioneer as Tesla, even if less colorful.



old jim

It is hard to be as "colorful" as Tesla (though it sounds like Steinmetz 'stood out'). I'll try to find a copy of the book.

Going through the 'U' in ee (not IEEE) I don't remember Tesla even being mentioned. One explanation I have read is that Tesla's patents (sold to Westinghouse) completely covered induction motors. Other companies regularly infringed on his patents, and it was not in the interest of other companies to recognize Tesla's contributions. One of the early standard texts was written by Steinmetz (GE) and minimized Tesla's contributions. Perhaps turnabout was 'fair play'?
 
Last edited by a moderator:
  • #61
westom said:
Those links provide important facts that Bud routinely forgets to mention. For example, the NIST says quite bluntly what a protector does when not properly earthed:

Westom "routinely forgets to mention" what the NIST guide really say about plug-in protectors:
They are "the easiest solution".
And "one effective solution is to have the consumer install" a multiport plug-in protector.

westom said:
That point was made repeatedly. Either a protector connects energy harmlessly to earth. Or it does ineffective protection.

Nonsense.

Plug-in protectors do not work primarily by earthing a surge. Read the IEEE surge guide starting page 30.

Both the IEEE and NIST surge guides say plug-in protectors are effective. The IEEE surge guide has 2 examples of protection - both use plug-in protectors.

Westom seems to have a religious belief (immune from challenge) that surge protection must directly use earthing. Thus plug-in protectors, which are not well earthed, can not possibly work. He just ignores anything that contradicts his belief (like the IEEE surge guide).

Being evangelical, westom googles for "surge" to find places to spread his beliefs. Some of what he says is very good. Some not-so-good. About everything he writes about plug-in protectors is nonsense.

westom said:
That IEEE citation shows what happens when a protector is too close to electronics and too far from Earth ground. Page 42 Figure 8 shows the power strip protector earthing a surge 8000 volts destructively through TV2. Where is protection? Once energy is inside, then nothing stops a destructive hunt for earth. It will Earth via the connected TV or any other nearby appliances. A surge simply selects a best appliance to damage. In figure 8, TV2 was damaged when the protector earthed a surge 8000 volts destructively.

If poor westom could only read and think he could discover what the IEEE guide says in this example:

- A plug-in protector protects the TV connected to it.
- "To protect TV2, a second multiport protector located at TV2 is required."
- In the example a surge comes in on a cable service with the ground wire from cable entry ground block to the ground at the power service that is far too long. In that case the IEEE guide says "the only effective way of protecting the equipment is to use a multiport [plug-in] protector."
- westom's favored power service protector would provide absolutely NO protection.

It is simply a lie that the plug-in protector in the IEEE example damages the second TV.

Westom tries to turn an example of how plug-in protectors work on its head.

westom said:
Bud said, "Point of use protectors do not work primarily by earthing a surge." So what do they do? If it does not Earth energy, then it must either stop, block or absorb that energy. How do 2 centimeter parts in a protector stop what three miles of sky could not? It doesn't.

Of course it doesn't. Protectors don't stop or block. And neither service panel or plug-in protectors protect by absorbing. (Both absorb some energy in the process of protecting.)

I don't say point of use protectors do not work primarily by earthing a surge - the IEEE surge guide does. Just like the IEEE surge guide explains they work by limiting the voltage on each wire (power and signal) to the ground at the protector. And the guide says earthing happens elsewhere ( starting page 30).

westom said:
How does a protector (rated for hundreds of joules) absorb hundreds of thousands of joules? It doesn't.

Of course it doesn't.

François Martzloff was the surge guru at the NIST and wrote the NIST guide plus many technical papers. One of them looked at the energy absorbed at a plug-in protector with no service panel protection. The branch circuits were 10m and longer, and the power service wire surge was up to 10,000A, which I said in another post is the accepted maximum probable surge. The maximum energy dissipated was a surprisingly low 35 joules. In 13 of 15 cases it was 1 joule or less.

I recently bought a plug-in protector that had ratings of 30,000A and 590J per MOV for each of the 3 MOVs - H-N, H-G, N-G. (It is not possible to get 30,000A at the protector, the rating just goes with a high energy rating.) It is very unlikely this protector will ever fail, which is one reason it has a connected equipment warranty.

Since this is a physics forum the technical details are that there are 2 reasons why the energy was so low. One is that at about 6,000V there is arc-over from service panel busbars to the enclosure. After the arc is established the voltage is hundreds of volts. Since the service enclosure is connected to the earthing electrodes this dumps most of the energy to earth. And at the service the neutral and ground are connected, also limiting the voltage on the house wiring.

The second reason is that the branch circuit impedance greatly limits the current (and thus energy) that can reach the protector. A surge is a very short event. A surge from lightning is over in less than 100 microseconds. That means the surge current has relatively high frequency elements, and the inductance of the wire is more important than the resistance.

Even more surprising than the 35J max energy was that the highest energies were for the smaller incoming surges (and shortest branch circuits). For some of the smaller surges the voltage limitation in the plug-in protector kept the voltage at the service panel below 6,000V, so arc-over did not occur.

So "absorb hundreds of thousands of joules"? Complete nonsense.

westom said:
As long as claims are made subjectively, then a plug-in protector can do miracles. Once we add facts and numbers from the NIST, IEEE, and a long list of professionals, then a power strip is near zero protection.

More complete nonsense. The NIST and IEEE both say plug-in protectors are effective.

Where is any professional that says plug-in protectors do NOT work. Cite.

The only one who says plug-in protectors are NOT effective is westom.

westom said:
A professional sales promoter for power strip protectors claims plug-in protectors will magically stop or absorb surges.

In case anyone didn't catch it, he is referring to me. My only connection with surge protection is I am using a couple protectors. If westom had valid technical arguments...

And it is only magic for westom. I have provided Martzloff's description of energy at a plug-in protector often. Apparently anything that does not conform to westom's belief in earthing is filtered out.

westom said:
But a coax protector claim demonstrates why cable TV does not need any protector.

The IEEE surge guide says otherwise.

westom said:
IEEE even gives numbers in a Standard called The Green Book entitled 'Static and Lightning Protection Grounding':

The IEEE Emerald book ("IEEE Recommended Practice for Powering and Grounding Sensitive Electronic Equipment") recognizes plug-in protectors as an effective protection device.

westom said:
Yes, the IEEE says plug-in protectors can add protection. But only if a 'whole house' solution is implemented.

Complete nonsense, and in many cases backward.

Repeating what the NIST surge guide says:
"Q - Will a surge protector installed at the service entrance be sufficient for the whole house?
A - There are two answers to than question: Yes for one-link appliances [electronic equipment], No for two-link appliances [equipment connected to power AND phone or cable or...]. Since most homes today have some kind of two-link appliances, the prudent answer to the question would be NO - but that does not mean that a surge protector installed at the service entrance is useless."

And my comment:
"That is because the NIST surge guide suggests that most equipment damage is from high voltage between power and phone/cable/.. wires. Service panel protectors are likely to protect anything connected only to power wiring."

Most likely damage would probably be around the signal wiring at the equipment.
A rather limited investigation of damaged equipment that included Martzloff and an insurance company found in some cases just fuses blown or diodes burned out on the DC side of computer switch mode power supplies from a line surge.

westom said:
The OP has garage door damage because 1) a surge entered due to no earthing, and 2) the surge found Earth destructively through that garage door.

Westom has the definitive answer from his Ouija board.

Sears seems to be familiar with the problem and seems to think it is unprotected control wiring. A surge on the power wiring is possible. As I said, the neutral and ground are not connected at the pole barn and the ground potential at the pole barn during an 'event' may be quite different from elsewhere.
 