I'm sorry. I can't see it for you. It doesn't matter if the part where the current 'splits' and part goes one way, part goes another way is at the molex connector or not.UrbanFarmEngineer said:Help me understand. I can't see that. Would the path of current flow be the same in both?
-
I'm not making sense of this.UrbanFarmEngineer said:When I entirely disconnect the AC the net current on the dedicated furnace line is the sum of what the average AC line reading and the average furnace line reading.
-
Back to the original complaint:
With the clampmeter around the hot and neutral of the dedicated circuit feeding the furnace you claim a residual reading. Meaning the current in the hot and neutral are not identical and don't 100% cancel as they should. You claim that when turning off the main breaker to the furnace, the meter drops to zero. You have to isolate things. Did you disconnect all of the low voltage wiring that goes to the outdoor unit and check for current imbalance on the dedicated furnace circuit like I asked a month ago? If so, did you still have an imbalance?