Good way to test variable-speed generator output?

Click For Summary

Discussion Overview

The discussion centers around testing a variable-speed generator connected to a small wind turbine, focusing on measuring power output and current in a three-phase Y configuration. Participants explore methods for testing, including load considerations and the nature of the generator.

Discussion Character

  • Technical explanation
  • Debate/contested
  • Experimental/applied

Main Points Raised

  • One participant suggests using a purely resistive load with a bank of resistors to measure power output for each phase.
  • Another participant proposes that the generator might be a brushless alternator and emphasizes the need for a variable speed motor to test it properly.
  • Some participants express uncertainty about the generator's classification, debating whether it is a dynamo or a permanent magnet generator.
  • There are discussions about the importance of load resistance in determining output power and its effect on the generator's operation.
  • One participant mentions the possibility of using existing appliances for resistance testing instead of purchasing new resistors.
  • A separate inquiry about a hospital's emergency generator raises questions about load capacity and starting currents for motors, indicating a broader context of generator testing.

Areas of Agreement / Disagreement

Participants do not reach a consensus on the classification of the generator or the best method for testing it. Multiple competing views and uncertainties remain regarding the load requirements and testing procedures.

Contextual Notes

Some participants highlight the need for a voltage versus RPM plot before selecting resistors, indicating that assumptions about the generator's output characteristics may vary. The discussion also touches on the implications of using variable frequency drives (VFDs) for motor starting currents.

Who May Find This Useful

This discussion may be useful for individuals interested in testing variable-speed generators, those working with wind turbine systems, or professionals dealing with generator load calculations in industrial settings.

HydroGuy
Messages
29
Reaction score
0
I need to test a variable-speed generator attached to a small wind turbine (lets say). I want to see how much power its producing, as well as the current. It outputs in three-phase Y configuration at frequencies varying from 3 to 9 Hz. The generator is rated at 1.2 kW at 550RPM, with an open circuit rectified DC voltage of 380 V.

I have zero experience working with high-power motors and generators and how to test them. I think the best bet would be to use a purely resistive load, correct? I'd have to use some robust resistors - my thinking was to setup a "bank" of resistors in parallel to meet the power requirement and then connect one bank to each phase. I could then measure voltage, and knowing the resistance of the bank determine power for each phase, right?

Would the load resistance matter in determining output power? Does the load effect how hard the generator is to turn, etc?
 
Engineering news on Phys.org
I think you are actually talking about a dynamo, meaning a brushless alternator with a permanent magnet rotor. The best way to test this is to use the rectified dc diode output (2 per phase) into a single resistive load. You can use a voltmeter to diagnose individual phases. To completely test this you will need a variable speed motor capable of ~1.5 HP at 550 RPM (torque = 26 Nm). Using a fixed-1740 RPM induction motor is not suitable. Electric drills could provide the correct RPM, but lack the torque (HP). The load resistance value depends on the no-load dc output voltage (which is linearly proportional to RPM), and the magnetic coupling efficiency between the magnets and the pickup coils.
Bob S
 
Last edited:
Hmm, I don't think it's a dynamo... it outputs three phase power. Here is the website:

www.Ginlong.com

I know that I need a voltmeter, but we would need some type of load to deliver the power to, right? I could find open circuit voltage just by spinning it, but I want to see the power delivered through an actual load... I think.

Thanks for the help.
 
Last edited by a moderator:
HydroGuy said:
Hmm, I don't think it's a dynamo... it outputs three phase power. Here is the website:

www.Ginlong.com..

They call it an alternator, but it does not have a slipring to contol the output voltage. Perhaps a PM generator is a better name.

.
I know that I need a voltmeter, but we would need some type of load to deliver the power to, right? I could find open circuit voltage just by spinning it, but I want to see the power delivered through an actual load... I think.
.
I agree. If it is a commercial PM generator, its output impedance should be fairly low, but still you need a plot of voltage vs. RPM before you can buy or make kilowatt resistors.

[added] The GL-PMG-1000 PM generator will put out 1600 W and 350 volts at 550 RPM. Nice generator. The resistance should be R = V2/1600 = 76 ohms #@ 1600 watts. You could parallel about 13 1000-ohm 100-watt resistors for full load measurements.

Bob S
 
Last edited:
Ginlong provides power and voltage curves for the model, but I'm looking to test/confirm it and do some additional testing in the future.

http://www.ginlong.com/images/200906/1000-PMG-Power-Curve-1.jpg

http://www.ginlong.com/images/200906/1000-Open-Circuit-Voltage-1.jpg

Couldn't I just make a bank of say 100 resistors in parallel so I don't have to have resistors rated at 20 W each, etc?
 
Last edited by a moderator:
Too bad they don't make these for low frequency applications.
http://www.transcat.com/images/Photos/cw_yokoga.jpg
http://www.transcat.com/Catalog/productdetail.aspx?itemnum=CW121-D-1&utm_source=google&utm_medium=base"
They sure are cute.
 
Last edited by a moderator:
HydroGuy said:
Ginlong provides power and voltage curves for the model, but I'm looking to test/confirm it and do some additional testing in the future.

http://www.ginlong.com/images/200906/1000-PMG-Power-Curve-1.jpg

http://www.ginlong.com/images/200906/1000-Open-Circuit-Voltage-1.jpg

Couldn't I just make a bank of say 100 resistors in parallel so I don't have to have resistors rated at 20 W each, etc?

You could cannibalize toasters, hairdryers or other used appliances for some nichrome resistance wire instead of buying a bunch of power resistors. You can stretch out segments for testing various loads.
 
Last edited by a moderator:
Hi,
I have a question. We have a 480V, 3 phase,1500.KW emergency generator in my hospital.What is the maximum load can we connect it? most of our loads are motors and pumps. I heard we can connect only 1/3 of the capacity of the generator because the motors are taking starting 3 times current. That means onlky 500KW.Is that true?
Other thing is that most of our motor starting with VFD. Is there any difference of starting current if motor starting with VFDs.

How do we calculate the load when it is running. When our last test we got the amps readings 826,820 and 796 respectively in each phase. I know the power is 1.73x volt x current x power factor.what will be the amps and volts for calculating?The line voltage was showing 282 in each phase.

The way my co wokers are calculating is 1.73 times total amps(2442) times 282Volts/1000 to get the KVA.Is that aright calculation?
I hope some one can help me.
thanks
 
Performing an Open circuit test and a Short circuit test can help you.
You will be needing a voltmeter and an ammeter.
:approve:
 

Similar threads

  • · Replies 38 ·
2
Replies
38
Views
5K
  • · Replies 7 ·
Replies
7
Views
3K
Replies
9
Views
2K
  • · Replies 4 ·
Replies
4
Views
2K
  • · Replies 38 ·
2
Replies
38
Views
8K
  • · Replies 8 ·
Replies
8
Views
3K
  • · Replies 37 ·
2
Replies
37
Views
7K
Replies
19
Views
3K
  • · Replies 11 ·
Replies
11
Views
2K
  • · Replies 5 ·
Replies
5
Views
3K