Grounding / Earthing. What does these lines mean?

Click For Summary
SUMMARY

This discussion focuses on the proper grounding of a 5 ampere weighing equipment located 80 feet from a soil point. The manufacturer specifies the need for a reliable third wire ground, ideally connected to a ground rod, with a target resistance of 0 ohms. Users are advised to use a digital clamp meter to measure resistance and ensure both the green ground wire and the equipment's metal frame are grounded effectively. It is recommended to consult a qualified electrician for installation and compliance with safety standards.

PREREQUISITES
  • Understanding of grounding principles and electrical safety.
  • Familiarity with digital clamp meters and resistance measurement.
  • Knowledge of electrical wiring, particularly for 110 VAC systems.
  • Awareness of local electrical codes and regulations.
NEXT STEPS
  • Research proper grounding techniques for electrical equipment.
  • Learn how to use a digital clamp meter for resistance measurement.
  • Investigate the specifications for grounding rods, including length and diameter.
  • Consult local electrical codes regarding grounding requirements for residential equipment.
USEFUL FOR

Electrical engineers, technicians, and anyone responsible for the installation and maintenance of sensitive weighing equipment requiring proper grounding to ensure safety and functionality.

Azee
Messages
3
Reaction score
0
Hello Everyone,
I have a 5 ampere weighing equipment & need it to ground properly. It is about 80 feet away from soil point. (Direct wire to the equipment will be used & long term connection is required).

Manufacturer says that:

"There must be a good third wire ground, preferably to a true ground or ground rod. Then check the resistance to that ground to all the contact surfaces of the equipment. There should be 0 ohms resistance since the static generated by the motion of the product needs a place to go".

1: What metal rod/wire or some thing else will be enough to use to vertically or horizentaly drive in soil. Length + diameter & other specifications. What size device will work in this case.
I need to be much closer to 0 ohms resistance. This is the actual target.
I can have digital clamp meter which have 200, 20k, 20M & 2000M ohms options.

2: Green (Ground) wire of the equipment is still to be ground as there is no ground connection to the wall socket.
Shall I need two rods?
First to connect with green wire & the second to connect with equipment's metal frame?
Or the same rod will be used to connect Green wire & Metal Frame?

3: For my reference please inform after grounding Green Wire & Metal frame how I can check resistance just like one can check voltage readings with a meter in hand by using probes. Please inform step by step.
Means to say how i can say or proof that resistance to the ground to all the contact surfaces of my equipment is 0 or any other reading that displays.

Thanks in advance.
 
Engineering news on Phys.org
Hi Azee. http://img96.imageshack.us/img96/5725/red5e5etimes5e5e45e5e25.gif

I understand your question, but I'll leave it for others to answer as it's outside my area. But it might help if you were to indicate whether your factory, etc., has metal water pipes that are laid under the ground.
2: Green (Ground) wire of the equipment is still to be ground as there is no ground connection to the wall socket.
Just clarify this. You are saying that no wall sockets in that building have three pins? They are all two pins? What is your electricity voltage?
 
Last edited by a moderator:
I want you to reply my question. Please don't leave it for other.
The Weighing equipment is on the 1st floor of my house. I have water pipes but that grounding is insuficient. I need to directly ground the equipment with a rod or so.
Equipment power supply cable has three wires or leads
1: Black "Hot"
2: White "Neutral"
3: Green "for Grounding" or "Earthing".

There is a three pin female wall socket near equipment often used for plugin Air conditioner power supplies. This Three Pin Female Wall Socket ONLY supplies Phase "Hot" & "Neutral" connection & there is NO "Earth" or "Ground" connection in it.
I also use Three Pin Male Plug to plugin above socket but without Green Wire.
I want to connect this green wire coming from the equipment supply cable DIRECTLY to a ROD driven in ground or so.
I also want to take a separate cable that connects equipment's frame to Rod or so.
Please help.
Equipment is 110 VAC & is being operated with 220VAC to 110VAC inverter. Equipmnet need 110-120VAC to run & i have adjusted Servo Motor Inverter Potentometer around 116VAC.
Awaiting reply.
 
Azee said:
Hello Everyone,
I have a 5 ampere weighing equipment & need it to ground properly. It is about 80 feet away from soil point. (Direct wire to the equipment will be used & long term connection is required).

Manufacturer says that:

"There must be a good third wire ground, preferably to a true ground or ground rod. Then check the resistance to that ground to all the contact surfaces of the equipment. There should be 0 ohms resistance since the static generated by the motion of the product needs a place to go".

1: What metal rod/wire or some thing else will be enough to use to vertically or horizentaly drive in soil. Length + diameter & other specifications. What size device will work in this case.
I need to be much closer to 0 ohms resistance. This is the actual target.
I can have digital clamp meter which have 200, 20k, 20M & 2000M ohms options.

2: Green (Ground) wire of the equipment is still to be ground as there is no ground connection to the wall socket.
Shall I need two rods?
First to connect with green wire & the second to connect with equipment's metal frame?
Or the same rod will be used to connect Green wire & Metal Frame?

3: For my reference please inform after grounding Green Wire & Metal frame how I can check resistance just like one can check voltage readings with a meter in hand by using probes. Please inform step by step.
Means to say how i can say or proof that resistance to the ground to all the contact surfaces of my equipment is 0 or any other reading that displays.

Thanks in advance.

Azee said:
I want you to reply my question. Please don't leave it for other.
The Weighing equipment is on the 1st floor of my house. I have water pipes but that grounding is insuficient. I need to directly ground the equipment with a rod or so.
Equipment power supply cable has three wires or leads
1: Black "Hot"
2: White "Neutral"
3: Green "for Grounding" or "Earthing".

There is a three pin female wall socket near equipment often used for plugin Air conditioner power supplies. This Three Pin Female Wall Socket ONLY supplies Phase "Hot" & "Neutral" connection & there is NO "Earth" or "Ground" connection in it.
I also use Three Pin Male Plug to plugin above socket but without Green Wire.
I want to connect this green wire coming from the equipment supply cable DIRECTLY to a ROD driven in ground or so.
I also want to take a separate cable that connects equipment's frame to Rod or so.
Please help.
Equipment is 110 VAC & is being operated with 220VAC to 110VAC inverter. Equipmnet need 110-120VAC to run & i have adjusted Servo Motor Inverter Potentometer around 116VAC.
Awaiting reply.

You need to consult a qualified electrician in your area. We cannot help you self-install electrical equipment when you already have wiring problems in your house. You need an electrician to help you run ground wires in your house.

This thread is locked.
 


I can provide a response to your question about grounding/earthing. Grounding or earthing refers to the process of connecting an electrical device or equipment to the ground in order to avoid the buildup of static electricity and to protect against electrical shocks. This is especially important for sensitive equipment, such as your 5 ampere weighing equipment.

In order to properly ground your equipment, you will need to use a metal rod or wire that is driven into the soil. The length and diameter of the rod or wire will depend on the type of soil and its moisture content, as well as the specific requirements of your equipment manufacturer. It is important to follow the manufacturer's guidelines to ensure proper grounding and prevent any potential damage to your equipment.

You can use a digital clamp meter to measure the resistance to the ground of your equipment. The 0 ohms resistance mentioned by the manufacturer is the ideal target, but any reading below 5 ohms is considered acceptable. To check the resistance, you will need to connect the meter to the grounding wire and metal frame of your equipment. If the reading is above the acceptable range, you may need to adjust your grounding method or use additional rods to improve the connection.

It is important to ground both the green (ground) wire and the metal frame of your equipment. You can use the same rod to connect both, as long as the connection is secure and the resistance is within the acceptable range.

To check the resistance after grounding, you can use the same process as mentioned above with the digital clamp meter. Simply connect the meter to the grounding wire and metal frame and take a reading. It is important to periodically check the resistance to ensure that your equipment remains properly grounded.

I hope this helps to clarify the concept of grounding/earthing and provides some guidance for properly grounding your equipment. If you have any further questions or concerns, it is always best to consult with a professional electrician or follow the specific guidelines provided by your equipment manufacturer.
 

Similar threads

  • · Replies 1 ·
Replies
1
Views
2K
  • · Replies 8 ·
Replies
8
Views
1K
  • · Replies 13 ·
Replies
13
Views
6K
  • · Replies 6 ·
Replies
6
Views
2K
  • · Replies 26 ·
Replies
26
Views
3K
  • · Replies 32 ·
2
Replies
32
Views
4K
Replies
16
Views
4K
Replies
6
Views
4K
  • · Replies 4 ·
Replies
4
Views
5K
  • · Replies 13 ·
Replies
13
Views
11K