Parallel Equipment Grounding Conductors, Short Circuit

Click For Summary

Discussion Overview

The discussion centers on the interpretation of the National Electrical Code regarding the use of multiple smaller equipment grounding conductors in place of a single larger one, specifically in the context of fault current and safety. Participants explore the implications of this standard, including its appropriateness and the technical factors involved, such as inductive reactance and the behavior of fault current in parallel conductors.

Discussion Character

  • Debate/contested
  • Technical explanation
  • Conceptual clarification

Main Points Raised

  • Some participants argue that the common interpretation of the National Electrical Code does not allow for multiple smaller equipment grounding conductors to replace one larger conductor, except in specific cases.
  • There is a concern regarding fault current and the size of conductors needed to prevent overheating or failure, with some suggesting that the safety of the equipment grounding conductor is paramount.
  • One participant notes that while ungrounded conductors can be paralleled, the same flexibility is not extended to equipment grounding conductors, raising questions about the rationale behind this distinction.
  • Another participant emphasizes that both equipment grounding conductors and ungrounded conductors must withstand available fault current, suggesting that if larger grounds are required, ungrounded conductors should also be sized accordingly.
  • There is a discussion about the potential consequences of a failure in grounding conductors, which could lead to dangerous voltage levels on equipment that is supposed to be grounded.
  • Some participants reference external resources and discussions that provide additional context and criteria for exceptions to the grounding conductor rules.

Areas of Agreement / Disagreement

Participants express differing views on the appropriateness of the current code requirements for equipment grounding conductors, with no consensus reached on whether the existing standards are justified or overly restrictive. The discussion remains unresolved regarding the technical justifications for the size and configuration of grounding conductors.

Contextual Notes

Participants highlight the complexity of fault current behavior in parallel conductors and the implications of grounding conductor sizing, indicating that assumptions about current division and safety are not fully settled. The discussion also touches on historical contestation of the code requirements without definitive scientific proof to support changes.

Leyden
Messages
39
Reaction score
4
TL;DR
Seeking information on parallel equipment grounding conductors fault characteristics.
I am seeking direction, information, resources and thoughts on the following subject. The common interpretation of the National Electrical Code does not allow you to use multiple smaller equipment grounding conductors in place of one larger one (except in a few cases such as a cable assembly, this thread is specifically dealing with single conductors in conduit). So, could anyone point me to any information, studies, etc. that would lead me to believe either this standard is appropriate or an overburden?

The issue I see at hand is fault current and the level at which a particular size of wire fuses/melts/fails. I think the major factor in the question is inductive reactance, some things that I think will play a large role in this are the proximity of the the equipment grounding conductor to the ungrounded conductors under fault and the proximity to grounded equipment foreign to the designed circuit (local metal objects), also carrying varying levels of fault current.

Some background information; You are allowed to use multiple smaller wires for ungrounded current carrying conductors. I believe the thought behind the holdout on equipment grounding conductors is because it is the safety conductor, so it is more safe for an ungrounded conductor to fail than an equipment grounding conductor.

Under the common interpretation of the standard, an equipment grounding conductor larger than the ungrounded circuit conductors could be required under certain circumstances, another less commonly accepted interpretation is that the ground does not have to be larger than the circuit conductors(in more common installations the ground is smaller than the circuit conductors).

It is already a related requirement for conductors to be able to withstand the available fault current but the basis of the question is the fault current dividing among the parallel equipment grounding conductors. The equipment grounding conductor size is based on the size of the overcurrent protection device, if you have parallel feeders say twelve sets of 600kcmill copper circuit conductors you may need a 800kcmill copper equipment grounding conductor in each of the twelve conduits.

Also, this is an old code requirement and has been contested through the years, the only legitimate argument I have seen to keep it is not an argument based on science that it should be required, but that to get rid of it requires clear scientific proof that it should not be required, that fault current will divide adequately and one parallel conductor will not bear too much of the brunt and fuse.Thank you
 
Last edited by a moderator:
Engineering news on Phys.org
anorlunda said:
There's a pretty good discussion here https://iaeimagazine.org/magazine/2...ductors-for-parallel-conductor-installations/

including the criteria for exceptions to the rule.
Yes. A good discussion. I thought I'd add this image as a reference.

242937


image compliments of https://www.ecmweb.com/qa/stumped-code-installing-circuit-conductors-parallel-separate-raceways
 
  • Like
Likes   Reactions: jim hardy
If I were forced to defend the status quo:
A connection failure in 1 (or more) power conductors in a multi-conductor feed may result in conductor overheating or system performance issues. That's bad, but probably won't kill anyone. A similar connection failure in safety grounds may prevent a breaker trip and/or allow a substantial voltage (to ground) to exist on things that are theoretically 'grounded.' Most important, the ground issue is nearly impossible to detect, unless you go looking for it - that usually happens as part of the accident investigation / lawsuit.
 
  • Like
Likes   Reactions: dlgoff and Asymptotic
I agree, i believe i mentioned that in the original post. but there is already another requirement which both the equipment grounding conductor and the ungrounded conductors must both be able to survive the available fault current, so really if each of the grounds need to be that big then the ungrounded circuit conductors should be as well.

Technically I see a good argument that the ungrounded should be the bigger ones. For example, say an ungrounded circuit conductor of a parallel feeder installation somehow severs and the upstream side connects to grounded metal equipment , the entire available fault current is borne on the individual wire, while the current on the equipment grounds will divide(probably somewhat evenly, but I'm not sure enough about this part, this is the part the entire thread is about). just to try to illustrate the extreme, NEC allows you to parallel 1/0, so say the scenario has 10 parallel conduits of 1/0 ungrounded circuit conductors and 500Kcmil equipment grounding conductors in each conduit. a single 1/0 of a long run may posses enough impedance for a system like that to keep the protective device from opening, all while possibly introducing deadly voltage gradients in the area.
 

Similar threads

Replies
6
Views
2K
  • · Replies 9 ·
Replies
9
Views
4K
  • · Replies 38 ·
2
Replies
38
Views
8K