Guidance on wire gauge size for automotive wire in a bundle

Click For Summary

Discussion Overview

The discussion revolves around determining the appropriate wire gauge size for a wiring harness in class 8 heavy-duty trucks, specifically focusing on the acceptable voltage drop and maximum current in bundled wires. The context includes considerations for 12V DC systems, peak amperages, and the thermal management of wire bundles.

Discussion Character

  • Technical explanation
  • Exploratory
  • Debate/contested

Main Points Raised

  • One participant seeks guidance on acceptable voltage drop and maximum current for bundled wires, noting the challenge of high peak amperages at startup that quickly drop to lower levels.
  • Another participant suggests calculating I^2R losses as heat addition within a PVC pipe to model heat retention and dissipation, proposing an iterative programming approach to ensure temperatures remain below 125°C.
  • Additional participants share links to resources with tables and formulas for wire sizing, although one notes a lack of specific information for bundled wires.
  • A later reply indicates that the participant feels confident about their wire sizing after referencing a NEC bundled wire table, suggesting they are well within safe limits.

Areas of Agreement / Disagreement

Participants express varying levels of confidence in their approaches, with some suggesting methods for calculating thermal effects while others share resources. There is no clear consensus on a single method or solution for sizing bundled wires.

Contextual Notes

Participants acknowledge the complexity of calculating voltage drop and thermal effects in bundled wires, with some noting the limitations of existing resources and the need for more rigorous engineering methods.

Who May Find This Useful

This discussion may be useful for automotive engineers, electrical engineers, and hobbyists involved in designing wiring harnesses for vehicles, particularly those working with bundled wire configurations in high-current applications.

IntegraR0064
Messages
5
Reaction score
0
Hi,

I'm designing a wire harness for class 8 heavy duty trucks. I need to size the wires. Everything is 12V DC. I have designed a first draft of a wiring harness and I have all of the currents and voltage drops over each wire mapped out. All the wires are in a bundle that will be run along the frame rails of the truck.

My question is - how do I determine the acceptable voltage drop and/or maximum current in each wire? I have seen tables online but they all assume open air. I have seen references to "compensating for bundles" but have not found how to do it. Of course they need to be sized so that each of the components has adequate voltage but I think the more limiting factor is overheating the bundle. Another complicating factor is I have pretty high peak amperages at startup, but after a fairly short time these amperages drop to very low levels. How do I deal with that?

I have also searched for a textbook or paper or something on this and have come up short - is there a good reference I should be looking at?

For more detail on the wiring, it is GXL wiring, 125 degrees C maximum insulation temperature, SAE J1228. Right now wire sizes are between 10 and 22 AWG. It will be bundled in groups of varying number of wires up to maybe 10 or 15 wires, but usually 3-5 wires, with a PVC coated woven yarn (max temperature 80 C) over the bundle.

Thanks for any input on any of my questions!
 
Engineering news on Phys.org
IntegraR0064,

I don't have an engineering degree, so take my thoughts as a simple layman's recommendation.

You might consider taking the current through each wire and calculating the I^2R losses as 100% heat addition to the interior of a PVC pipe similar in diameter to your bundle. You should be able to calculate the heat loss through a PVC pipe to ambient air based on the temperature differential. It should be fairly easy to write an iterative program that tests the heat added and lost in one second intervals, and as long as it can make it through 36,000 iterations w/o getting too close to 125C, you should be fine.

I am certain there are more rigorous engineering ways of proving safety, but I figured if I threw this out there, someone better qualified might give you the answer you are looking for.

Fish
 
IntegraR0064,

I don't have an engineering degree, so take my thoughts as a simple layman's recommendation.

You might consider taking the current through each wire and calculating the I^2R losses as 100% heat addition to the interior of a PVC pipe similar in diameter to your bundle. You should be able to calculate the heat loss through a PVC pipe to ambient air based on the temperature differential. It should be fairly easy to write an iterative program that tests the heat added and lost in one second intervals, and as long as it can make it through 36,000 iterations w/o getting too close to 125C, you should be fine.

I am certain there are more rigorous engineering ways of proving safety, but I figured if I threw this out there, someone better qualified might give you the answer you are looking for.

Fish
 
Good suggestion! I'll try that as an approximation.
 
Hey thanks for those links. From one of them I found a NEC bundled wire table - http://www.houwire.com/products/technical/article310_16.html . I'm pretty far under those values so I think I'm good from a melting wires perspective. Thanks again.
 
Last edited by a moderator:

Similar threads

  • · Replies 28 ·
Replies
28
Views
17K
  • · Replies 7 ·
Replies
7
Views
3K
  • · Replies 11 ·
Replies
11
Views
4K
  • · Replies 17 ·
Replies
17
Views
4K
  • · Replies 3 ·
Replies
3
Views
2K
  • · Replies 5 ·
Replies
5
Views
2K
  • · Replies 5 ·
Replies
5
Views
5K
Replies
28
Views
7K
  • · Replies 15 ·
Replies
15
Views
2K
Replies
6
Views
3K