Why auto-transformer starter for 4160V motor causes voltage sag without shorting contactor

Join the discussion
Registration is free. Start your own thread to ask a follow-up.
13 replies · 3K views
kenneth edmiston
Messages
45
Reaction score
2
A 4160v chiller motor is drawing too much power at start-up. Utility company only let's them run it once or twice a year because of it. It dims all the lights etc.. It was originally a primary reactor starter (2 contactors). The PR was replaced with an auto-xfmr and wired the same. So now it’s a series auto-xfmr with no shorting contactor. The xfmr is fed, the secondary output supplies the motor at start-up, then a bypass or run contactor pulls in. So the xfmr is not shorted or disconnected from the circuit.

What could be causing the voltage dip on the source, or why is it causing it?

And why does a 3-phase auto xfmr need a shorting contactor? What does connecting the windings do besides dissipate the energy in the winding, and what does leaving them open do?

Thanks!
 
Last edited by a moderator:
Engineering news on Phys.org
kenneth edmiston said:
A 4160v chiller motor is drawing too much power at start-up.

4000+ V motor ??
surely a typo
 
No sir. It’s a 4160v 3-phase wye motor. They are common
 
  • Like
Likes   Reactions: davenn
kenneth edmiston said:
what could be causing the voltage dip on the source, or why is it causing it?

Motors draw several time rated current during startup. See
https://www.engineeringtoolbox.com/locked-rotor-code-d_917.html

upload_2018-3-15_17-2-19.png


The source is not "stout" enough to hold up under your chiller's starting current.

What is the KVA code of your motor on its nameplate? And its horsepower ? How does that compare to the nameplate of your building's supply transformer ?

Somebody should have specified a motor with KVA code that's early in the alphabet.
In my Nuke plant Westinghouse did that for motors that have to start from our diesel generator. Little details make a big difference.

kenneth edmiston said:
And why does a 3-phase auto xfmr need a shorting contactor?
Without knowing how it's connected one can only speculate - to take it out of the circuit once motor has reached running speed, perhaps ?

old jim
 
Attachments
  • upload_2018-3-15_17-2-19.png
    upload_2018-3-15_17-2-19.png
    2.8 KB · Views: 1,180
  • Like
Likes   Reactions: Asymptotic
kenneth edmiston said:
No sir. It’s a 4160v 3-phase wye motor. They are common
WOW, OK ... way outside my field of expertise :eek::smile:
 
davenn said:
WOW, OK ... way outside my field of expertise :eek::smile:
You don't run across them at Home Depot.

Our boiler feed pumps were 4160 volt 7,000 horsepower. Size of a big storage shed.
 
  • Like
Likes   Reactions: davenn
Sounds like a good application for a VFD. The utility would also like it if the motor was decelerated gradually when stopping instead of merely cutting power.
 
jim hardy said:
Our boiler feed pumps were 4160 volt 7,000 horsepower. Size of a big storage shed.
Pictures? :smile:
 
  • Like
Likes   Reactions: davenn
berkeman said:
Pictures? :smile:

Something like this. I used to work next door to GE's Large Generator & Motor Factory. There are lots of those babies around.

smBRD12-097-1.jpg
 
Attachments
  • smBRD12-097-1.jpg
    smBRD12-097-1.jpg
    9.5 KB · Views: 617
  • Like
Likes   Reactions: Asymptotic, jim hardy and berkeman
anorlunda said:
Something like this.
Thanks ! I was looking in my archives... i don't have any of them opened up like that..

The roar standing next to one has to be experienced in person... as you well know.
 
Sounds like this was the initial configuration. The Primary Reactors limited the inrush current and after speed was obtained the Shorting Contactors close to supply full line voltage to the motor. I can conceive of a similar function with autotransformers but best get a schematic of what exists before further speculation.
Pri Reactor.png
 
Attachments
  • Pri Reactor.png
    Pri Reactor.png
    12.1 KB · Views: 621
  • Like
Likes   Reactions: Asymptotic
jim hardy said:
Motors draw several time rated current during startup. See
https://www.engineeringtoolbox.com/locked-rotor-code-d_917.html

View attachment 222064

The source is not "stout" enough to hold up under your chiller's starting current.

What is the KVA code of your motor on its nameplate? And its horsepower ? How does that compare to the nameplate of your building's supply transformer ?

Somebody should have specified a motor with KVA code that's early in the alphabet.
In my Nuke plant Westinghouse did that for motors that have to start from our diesel generator. Little details make a big difference.Without knowing how it's connected one can only speculate - to take it out of the circuit once motor has reached running speed, perhaps ?

old jim
Thanks Jim. I couldn’t find a good nameplate on the motor but it’s not an overly big motor. Main power fuses are around 100-120 amp fuses. I know I’m not giving
 
kenneth edmiston said:
Thanks Jim. I couldn’t find a good nameplate on the motor but it’s not an overly big motor. Main power fuses are around 100-120 amp fuses. I know I’m not giving
^Sorry I’m a newbie. Here’s my circuit. Only the reactor has been replaced with an auto-xfmr tapped at 80%
 
Attachments
  • B392104B-FF9B-424C-B425-D0DDAC09A330.jpeg
    B392104B-FF9B-424C-B425-D0DDAC09A330.jpeg
    34.4 KB · Views: 694
Many years ago, I worked in a steel rolling mill. I'm pretty sure the drive motors for the mill were 4160 v, and pulled several thousand amps when starting. They were truly awe-inspiring.

The current draw was enough that it was measured by simply measuring the voltage difference between two pins about 1-1/2 inches apart embedded in the copper buss bars feeding the motors.