Help understanding auto transformer shorting

Click For Summary

Discussion Overview

The discussion revolves around the operation and significance of shorting an autotransformer in a motor starting circuit. Participants explore the mechanics of voltage reduction during motor startup, the role of various contactors, and the implications of leaving the autotransformer in the circuit while the motor is running.

Discussion Character

  • Technical explanation
  • Conceptual clarification
  • Debate/contested
  • Experimental/applied

Main Points Raised

  • Some participants explain that during startup, the autotransformer reduces voltage, and once the motor reaches speed, the run contacts short the transformer, effectively removing it from the circuit.
  • Others discuss the potential issues of leaving the run contacts open, suggesting that this would introduce inductance in series with the motor, negatively affecting the power factor.
  • A participant raises questions about the configuration of the windings and whether the shorting process bypasses the Y connection.
  • Concerns are expressed regarding the performance of the autotransformer in place of a reactor, with one participant noting that it may not be effectively reducing line current during startup.
  • Some participants share their experiences with different tap settings on the autotransformer and their effects on current and torque during startup.
  • There is mention of a previous thread that may relate to the current discussion, indicating a broader context of troubleshooting motor startup issues.

Areas of Agreement / Disagreement

Participants exhibit a mix of agreement on the basic operation of the autotransformer but express differing views on its effectiveness and the implications of its configuration in the circuit. The discussion remains unresolved regarding the optimal setup and the impact of the autotransformer versus a reactor.

Contextual Notes

Some participants note limitations in their understanding of the physical workings of the autotransformer, and there are unresolved questions about the circuit configuration and its effects on performance.

Who May Find This Useful

Individuals interested in motor control systems, electrical engineering, and those troubleshooting similar motor startup issues may find this discussion relevant.

kenneth edmiston
Messages
45
Reaction score
2
Will someone please help me understand the significance of shorting an auto transformer? This feeds a motor. At reduced voltage, the motor starts at 65% of line voltage, a run contactor pulls in bypassing the transformer and the shorting contactor pulls into take the transformer out of the circuit.

How does this happen? What is the significance of shorting them out? Why is it necessary? And what if they were left open? If anyone can explain in detail I would greatly appreciate it!

Thanks!
 

Attachments

  • E9B22EBE-18CB-4013-9CCB-FFD3B33BB9EF.jpeg
    E9B22EBE-18CB-4013-9CCB-FFD3B33BB9EF.jpeg
    27.6 KB · Views: 694
Engineering news on Phys.org
I assume this is related to your other thread. https://www.physicsforums.com/threa...ge-sag-at-large-chiller-motor-startup.942228/

For the circuit to operate as intended, that is start at reduced voltage then switch to full line voltage, would require M and S contacts to close for start-up. Then when speed is reached, S contacts open and R contacts close. Make sure ther is no overlap of the S and R contacts, that could lead to spectacular results. Probably the safest way is have the S and R contacts on the same contactor that the manufacturer guarantees not to have contact overlap under any failure conditions.
 
kenneth edmiston said:
How does this happen? What is the significance of shorting them out? Why is it necessary? And what if they were left open? If anyone can explain in detail I would greatly appreciate it!
During the start period, the voltage is reduced by the Y or star connected 3PH autotransformer.

When running, the common terminal at the centre of the Y is disconnected from all autotransformer phase windings.
The remaining windings are shorted by the run contacts, so the transformer is effectively without voltage or current.
The autotransformer is NOT energised while it is shorted.

If the run contacts were left open, the autotransformer would appear to be inductors in series with the motor.
Series Inductors would reduce the power factor, which is really bad.
 
Baluncore said:
During the start period, the voltage is reduced by the Y or star connected 3PH autotransformer.

When running, the common terminal at the centre of the Y is disconnected from all autotransformer phase windings.
The remaining windings are shorted by the run contacts, so the transformer is effectively without voltage or current.
The autotransformer is NOT energised while it is shorted.

If the run contacts were left open, the autotransformer would appear to be inductors in series with the motor.
Series Inductors would reduce the power factor, which is really bad.
Exactly what I was looking for. Thank you sir
 
Baluncore said:
During the start period, the voltage is reduced by the Y or star connected 3PH autotransformer.

When running, the common terminal at the centre of the Y is disconnected from all autotransformer phase windings.
The remaining windings are shorted by the run contacts, so the transformer is effectively without voltage or current.
The autotransformer is NOT energised while it is shorted.

If the run contacts were left open, the autotransformer would appear to be inductors in series with the motor.
Series Inductors would reduce the power factor, which is really bad.
Tom.G said:
I assume this is related to your other thread. https://www.physicsforums.com/threa...ge-sag-at-large-chiller-motor-startup.942228/

For the circuit to operate as intended, that is start at reduced voltage then switch to full line voltage, would require M and S contacts to close for start-up. Then when speed is reached, S contacts open and R contacts close. Make sure ther is no overlap of the S and R contacts, that could lead to spectacular results. Probably the safest way is have the S and R contacts on the same contactor that the manufacturer guarantees not to have contact overlap under any failure conditions.
It is related, and it isn’t. The diagram I uploaded isn’t the motor I’m working on. I just want to know all I can about what I’m working on. How an auto transformer even actually works on a physical level is still a mystery to me haha. Thanks for the article and the reply
 
Baluncore said:
During the start period, the voltage is reduced by the Y or star connected 3PH autotransformer.

When running, the common terminal at the centre of the Y is disconnected from all autotransformer phase windings.
The remaining windings are shorted by the run contacts, so the transformer is effectively without voltage or current.
The autotransformer is NOT energised while it is shorted.

A couple of questions:
Are all 3 windings (primary/secondary x3) connect at the common terminal? So as to be consider a single autotransformer and not 3 singles.
And does the shorting process change the configuration to bypass the y connection so to speak?
Right now I have an auto transformer in a primary reactor RV starter. Wired like a PR. Power company installed PFCC and it fixed the problem slightly, but not completely.
I think it’s the set-up but I want to be certain.

One more question— A primary reactor is still left in the circuit, just bypassed by a run contactor. why is that inductance not an issue like it would be with a transformer? (The circuit does have 20uf of capacitance to offset some of the L.

Thanks a lot!
 
Here’s the circuit. Wired the same only reactor has been replaced with xfmr tapped to 80%.
It seems to be causing some major issues. I just surge tested the “c” phase winding and it appears to be almost dead shorted. I wonder if leaving a medium duty xfmr in the circuit has been causing heat as well.

Thanks again chaps
 

Attachments

  • 93DE1F0E-A02B-4B46-965C-A61C40E845A8.jpeg
    93DE1F0E-A02B-4B46-965C-A61C40E845A8.jpeg
    34.4 KB · Views: 589
Or do I have this completely backwards and the 0% is the star point and is needed to provide the reduced voltage, then is disconnected after motor reaches desired speed? This would make sense too
 
My experience is limited to 200 to 400 HP, 460V, delta-wye starters, and not 4160V machines, but from what I can make out in the schematic there is no delta-wye transitioning. Rather, the motor is started by closing contactor 1K with contactor 2K de-energized (allowing current to flow through the auto-transformer to achieve the reduced voltage start), then (presumably, once a timer relay has timed out) closing contactor 2K to bypass the auto-transformer windings.

Have you tried using the lower taps?
 
  • #10
This is a typical auto-xfmr start
 

Attachments

  • E50F3FAF-860F-47E3-A94A-D06B0F66D0E7.jpeg
    E50F3FAF-860F-47E3-A94A-D06B0F66D0E7.jpeg
    27.6 KB · Views: 632
  • #11
We can only run this chiller 1ce per year. Makes troubleshooting a pain
 
  • #12
The 1st diagram was a primary reactor start setup, which we have, only the reactor has been replaced by an autoxfmr. I can only assume the auto xfmr is now being used as a series inductor and not a xfmr, so line current is not being reduced at start-up and power factor is being affected.
 
  • #13
Lower taps should increase inductance, lower stress on motor, but leave line current unchanged. If I understand this right.

Sorry for blowing up my own thread. Thanks to all for the help
 
  • #14
kenneth edmiston said:
This is a typical auto-xfmr start
This diagram is different than the first. Is this how it is wired?

If so, it looks like the 'M' contactor and 'S' contactor are closed during start. They drop out and the 'R' contactor closes when the start timer completes.

50% tap: 50% current & 25% torque
65% tap: 65% current & 42% torque
80% tap: 80% current & 64% torque
 
  • #15
The “autoxfmr diagram” was just to show you how a typical auto xfmr start is wired. How it’s shorted etc.

What I have is an auto xfmr in place of a reactor in the 1st diagram. So it’s not being connected during start up, and is only reducing motor voltage by way of dropping voltage through inductance of xfmr winding.

So it looks like the original reactor start was not a good choice for that motor and caused the voltage dip during start. so someone replaced it with an auto xfmr to try and reduce start up LINE current but did not install a means to connect the windings during start to actually reduce voltage. Instead it ended up operating the exact same way the reactor did.
 
  • #16
kenneth edmiston said:
Sorry for blowing up my own thread. Thanks to all for the help
I think you just learned something. A forum is not like a fast two way conversation.

You need to get a reasoning.text file. Rather than thinking out loud in posts, do your reasoning and construct your questions in that file. You will find it advantageously disciplines your reasoning. When you have noted your observations and refined your question(s), you will probably realize what the answer must be.

If you cannot find the answer, then you will at least have a succinct question, with relevant observations, to post on the forum.
 
  • #17
I debated on even responding because it contradicts your post . Yeah but noted, I’ll take it as constructive criticism. I’m a newb to the forums. I learned more than one thing today though. Many thanks
 
  • #18
kenneth edmiston said:
I debated on even responding because it contradicts your post .
Most answers need to be questioned.
To answer a question we must first work out what the question should have been.

“The only interesting answers are those that destroy the questions”. Susan Sontag.
 
  • Like
Likes   Reactions: kenneth edmiston
  • #19
I completely understand what you’re saying.
But I’m really good at questioning myself to the point of confusion. I’ve found that my biggest revelations come from thinking out loud to one or many so to speak and piecing together the conversations. I’ve always thought there were no such thing as dumb questions, only dumb answers. I still do, but I’ve never thought of it the other way around. But the truth is, I didn’t know what the question was, I was in the middle of troubleshooting and flying by the seat of my pants. But I believe I was able to understand what I was dealing with by being on this thread. Maybe the way this thread was formatted was exactly how I needed it. Who’s to say. But I’ll quit rambling on, unfortunately this isn’t a physics/philosophy forum :oldbiggrin:
 
  • #20
kenneth edmiston said:
But the truth is, I didn’t know what the question was, I was in the middle of troubleshooting and flying by the seat of my pants. But I believe I was able to understand what I was dealing with by being on this thread.
Glad we could help. And Bravo for continually looking for answers when you realized they were needed. Too many people just throw up there hands and say 'That's the way it is.' I think all of us have learned a bit on this thread.

Cheers,
Tom
 
  • Like
Likes   Reactions: kenneth edmiston
  • #21
Just a thought. For trouble shooting can you find a lower supply voltage to drive the circuit? I'm thinking 208V or 440V. Maybe you can run a temporary line from somewhere else in the plant to keep things under control while tracking down the problem.
 
  • #22
Tom.G said:
Just a thought. For trouble shooting can you find a lower supply voltage to drive the circuit? I'm thinking 208V or 440V. Maybe you can run a temporary line from somewhere else in the plant to keep things under control while tracking down the problem.
There’s probably a way to do it, although I don’t think the low voltage would provide the torque needed to turn the motor. Even if it would, they wouldn’t spend the money for it. After figuring out the problem, it turns out they are content with putting a reactor back in and only running that particular machine once a year. (One start, and continuously running through summer). I work for a small company full of “that’s the way it is”. If it’s out of the norm, it’s scary. I don’t think my superior fully understood what I was trying to explain and reverted to the original design when making the executive decisions. The auto-xfmr would have dropped the inrush current on the source if it had been connected properly. But the boss was able to sell the easy way out.

...That’s the way it is :iseewhatyoudid:
 
  • #23
Bummer. I've worked for a few of those "Bosses", usually quite briefly.

Too often it's a case of There Are Two Rules:
1) The boss is always right.
2) If the boss is wrong, see rule #1.

Ah well. A roof over the head and food in the belly is good.
 
  • Like
Likes   Reactions: kenneth edmiston
  • #24
Tom.G said:
Bummer. I've worked for a few of those "Bosses", usually quite briefly.

Too often it's a case of There Are Two Rules:
1) The boss is always right.
2) If the boss is wrong, see rule #1.

Ah well. A roof over the head and food in the belly is good.
It’s alright though, I’ll chalk it up as a good learning experience and sleep like a baby.
 
  • Like
Likes   Reactions: Tom.G

Similar threads

Replies
13
Views
3K
  • · Replies 1 ·
Replies
1
Views
1K
  • · Replies 25 ·
Replies
25
Views
6K
  • · Replies 11 ·
Replies
11
Views
4K
  • · Replies 33 ·
2
Replies
33
Views
6K
Replies
12
Views
3K
Replies
6
Views
5K
  • · Replies 8 ·
Replies
8
Views
3K
Replies
9
Views
3K
  • · Replies 5 ·
Replies
5
Views
3K