Ok I have a question that hopefully someone can answer. I'm an electrician and I recently had a service call where a hotel had a 175 amp 3 phase breaker feeding an ac unit with 4 compressors and 2 blowers that kept tripping. I first checked all the compressors and blowers to see if they were grounded or open and all were good. I then turned on the unit and all 4 compressors ran for about an hour and then the breaker tripped. Once it tripped I felt the 3 phases and phase C which happens to be the high leg was very hot so that leg is the culprit which tripped the breaker. I amp probed all three phases while they were running and it was a little off balance. The C phase was drawing around 120 amps, B phase 115 amps and A phase 105 amps. The compressors are 7.5 hp and draw approximately 22 amps each at 240 Volts. Does anyone have any idea why this one leg could be getting hot and tripping the breaker? Could it be that the motors are wired for wye connection and the delta service is the problem? Any suggestions would be helpful. Thank you in advance