How Are Transformer Turns Calculated Using Voltage Measurements?

  • Thread starter Thread starter encoder007
  • Start date Start date
  • Tags Tags
    Transformer
Click For Summary

Discussion Overview

The discussion revolves around calculating the number of turns in the primary and secondary windings of a transformer based on voltage measurements. Participants explore the implications of applying a specific voltage to the secondary winding and how that affects the turns ratio, with a focus on understanding the methodology behind the calculations.

Discussion Character

  • Homework-related
  • Mathematical reasoning
  • Debate/contested

Main Points Raised

  • One participant presents a calculation method that yields approximately 980 turns for the primary and 245 turns for the secondary winding based on a voltage of 76 V applied to the 120 V winding.
  • Another participant questions the validity of the calculations, suggesting that the measurements should be scaled to reflect the actual 120 V applied to the winding, not the 76 V used in the test.
  • A third participant expresses confusion regarding the setup of the experiment, particularly the meaning of "3 turns of wire are wound around the external winding," questioning how the external winding interacts with the transformer flux.
  • One participant clarifies that the three turns were likely wound on top of the existing windings, which could allow for accurate measurements of the transformer flux.
  • Another participant provides a detailed calculation method that aligns with the first participant's results, reinforcing the conclusion of 245 turns for the secondary and 980 turns for the primary winding.

Areas of Agreement / Disagreement

Participants express differing views on the calculations and the experimental setup. While some calculations yield consistent results, there is no consensus on the appropriateness of the applied voltage or the interpretation of the experimental conditions.

Contextual Notes

Participants note potential limitations in the experimental setup, including the application of a lower voltage than nominal and the ambiguity surrounding the external winding setup, which may affect the accuracy of the turns calculation.

encoder007
Messages
3
Reaction score
0
Question: The nameplate on a 50 kVA transformer shows a primary voltage of 480 V and a secondary voltage of 120 V.We wish to determine the approximate number of turns on the primary and secondary windings. Toward this end, three turns of wire are wound around the external winding, and a voltmeter is connected across the 3-turn coil. A voltage of 76 V is then applied to the 120 V winding, and the voltage across the 3-turn winding is found to be 0.93 V. How many turns are there on the 480 V and 120 V windings (approximately)?

Answer: With 76 volts applied, the constant is 0.93v/3T = 0.31 V/T. Correcting that for 120 volts instead of 76, that becomes (0.31 V/T)(120/76) = 0.489 V/T.So the 120 volt winding has 120 V / 0.489 V/T = 245 turns the 480 would have 4 times as many or 980 turns.

Thats the answer what my teacher gave me but i don't understand it,if that's right can anyone explain me in detail. Or Should it not be like this when i tryed to solve it:

The worked out ratio is 0.31 V/T
Primary turn = 1548 turns for 480 V
Secondary turn = 387 turns for 120 V

Please any suggetions and explanations will be helpful.Thank you.
 
Physics news on Phys.org
Hi encoder007! http://img96.imageshack.us/img96/5725/red5e5etimes5e5e45e5e25.gif

The answers you get would be correct had the test been performed with 120V applied to the 120V winding. But that wasn't so. Only 76V was applied, so you have to scale up the measurement of volts/turn to what would apply when using 120V.

For future questions, note that the forum for homework help is the homework subforum.
 
Last edited by a moderator:
This problem seems a bit bizzarre. The only way the computations make sense is if the 3 turns of wire saw the same transformer flux as the transformer's own primary and secondary windings. But these are obvioulsy not accessible from outside the transformer.

What does "3 turns of wire are wound around the external winding" mean? What external winding?
 
I guess the three turns were wound on top of the windings; outside the insulations. It would work that way.
 
I did it like this...

The 120V winding has an unknown number of turns = X.

During the test the ratio of the voltages = ratio of turns eg...

76/0.93 = X/3

Rearrange to give..

X = 3 * 76/0.93 = 245

So the 120V winding has 245 turns.

The 480V winding has an unknown numbe of turns Y:

480/120 = Y/245

Y = 245 * 480/120 = 980

So the 480V winding has 980 turns.
 

Similar threads

  • · Replies 33 ·
2
Replies
33
Views
10K
  • · Replies 12 ·
Replies
12
Views
5K
  • · Replies 2 ·
Replies
2
Views
2K
  • · Replies 7 ·
Replies
7
Views
3K
Replies
1
Views
2K
Replies
1
Views
4K
  • · Replies 1 ·
Replies
1
Views
3K
  • · Replies 7 ·
Replies
7
Views
2K
Replies
29
Views
22K
Replies
0
Views
2K