How Are VA Ratings Derived for Different 3-Phase Transformer Configurations?

  • Thread starter Thread starter Serena_hm
  • Start date Start date
  • Tags Tags
    Transformer
Click For Summary
SUMMARY

The discussion centers on the VA ratings derived from different 3-phase transformer configurations: Wye-Wye, Wye-Delta, Delta-Delta, Delta-Wye, and Open Delta. It is established that the VA rating for Open Delta is 0.58 of the Delta-Delta rating due to its use of only two transformers, which results in lower capacity. Each configuration has distinct advantages based on load types, with Wye-Wye being optimal for balanced loads and Delta-Delta for unbalanced loads. The total 3-phase power obtainable from a 60 KVA transformer varies by configuration, necessitating careful selection based on specific load requirements.

PREREQUISITES
  • Understanding of 3-phase transformer configurations
  • Knowledge of VA ratings and their implications
  • Familiarity with load types: balanced vs. unbalanced
  • Basic electrical engineering principles
NEXT STEPS
  • Research the mathematical derivation of VA ratings for transformer configurations
  • Explore the design considerations for selecting transformers based on load requirements
  • Learn about the impact of winding polarity on transformer operation
  • Investigate the efficiency differences between Open Delta and Delta-Delta configurations
USEFUL FOR

Electrical engineers, power system designers, and students studying transformer technology will benefit from this discussion, particularly those focusing on 3-phase systems and transformer configuration optimization.

Serena_hm
Messages
18
Reaction score
2
hello there ; I have several questions about the 3-phase transformer connections and I will be really grateful if anyone could help ...

I've learned that there are several types of 3-phase transformer connections which are in general ; the (Wye-wye) , ( Wye-Delta ) , (Delta-Delta ) , ( Delta-Wye ) , and Open Delta

but I got a bit confused with the VA relation for each ...I also have read in a book that the VA rating of Open-delta configuration is = 0.58 of ( Delta-Delta ) rating , how this relation been derived in the first place !?

and what's the different between each configuration and another , I know that only 2 transformers have to be used for Open-delta configuration , and 3 transformers for the rest configurations ...

what if the current ratings for each winding increased , could the open-delta configuration work as well as the Delta-Delta configuration !?

what about a transformer with capacity of 60 KVA what total 3-phase power can be obtained in each of the ; (Wye-wye) , ( Wye-Delta ) , (Delta-Delta ) , ( Delta-Wye ) , and Open Delta !?


thanks in advance .
 
Engineering news on Phys.org
I've checked the links I found somethings interesting
I'm still wondering what might happen if I reversed winding polarities in both Wye and Delta connection , will there be a short circuit !?
 
As long as you reverse the polarities in all three transformers, there should not be a short.
 


I would be happy to help clarify any confusion you may have about 3-phase transformer connections. Firstly, the VA rating for each configuration is dependent on the type of load being supplied. For example, a wye-wye connection is best suited for balanced loads, while a delta-delta connection is better for unbalanced loads. The VA relation for open-delta configuration being 0.58 of delta-delta rating is derived from the fact that open-delta only uses two transformers instead of three, resulting in lower overall capacity.

The main difference between each configuration is the number of transformers required and the suitability for different types of loads. As for your question about increasing current ratings, it is important to carefully design and select the appropriate transformer for the specific load and configuration. While open-delta may be able to handle higher currents, it may not be the most efficient or suitable option for certain loads.

As for the total 3-phase power that can be obtained from a 60 KVA transformer, it would depend on the specific configuration and load being supplied. Each configuration can provide different levels of power, so it is important to consider the specific needs and requirements when selecting a transformer.

I hope this helps clarify some of your questions about 3-phase transformer connections. It is always important to carefully consider and design the best configuration for your specific needs to ensure efficient and effective power supply. If you have any further questions, please don't hesitate to ask. Best of luck with your studies.
 
Most likely this can only be answered by an "old timer". I am making measurements on an uA709 op amp (metal can). I would like to calculate the frequency rolloff curves (I can measure them). I assume the compensation is via the miller effect. To do the calculations I would need to know the gain of the transistors and the effective resistance seen at the compensation terminals, not including the values I put there. Anyone know those values?

Similar threads

  • · Replies 20 ·
Replies
20
Views
3K
  • · Replies 77 ·
3
Replies
77
Views
8K
  • · Replies 11 ·
Replies
11
Views
6K
  • · Replies 7 ·
Replies
7
Views
3K
Replies
2
Views
2K
  • · Replies 1 ·
Replies
1
Views
3K
Replies
9
Views
2K
  • · Replies 5 ·
Replies
5
Views
10K
  • · Replies 13 ·
Replies
13
Views
4K
Replies
4
Views
3K