How Do You Calculate BTUs from Temperature Change in a Heat Exchanger?

Click For Summary
To calculate BTUs dissipated by the radiator, the temperature change of the water and the flow rate must be considered. With a water flow of 1.7 gallons per minute and a temperature drop of 8.3°C, the conversion to BTUs can be done using the formula: BTU/hr = flow rate (GPM) x temperature change (°F) x 500. The temperature change in Fahrenheit is approximately 14.94°F, leading to a calculation of about 12,000 BTU/hr. Understanding the definition of BTU as the amount of heat required to raise the temperature of one pound of water by one degree Fahrenheit is essential for accurate calculations.
drkidd22
Messages
59
Reaction score
0
Hello,
I'm working with a heat exchanger I'm trying to integrate into a cooling application. I've done some tests but want to have some clear understating of how the calculations are done or if I have missed something. Below is what I have so far.
So it's a radiation with 2 pwm fans, they push air through the radiator. It has a 1.7gpm water flow through the loop.

Air temp into fans: 30.1C
Air temp out fans (rear radiator): 59.2C
Input water temp to radiator: 64.8C
Output water temp from radiator:56.5C

So what I get from this is that the radiator is removing 8.3C from the water temp. How would this translate to actual power or BTUs dissipated by the radiator?
 
Engineering news on Phys.org
drkidd22 said:
1.7gpm water flow
drkidd22 said:
8.3C from the water temp
drkidd22 said:
actual power or BTUs
Power? You want BTU/hr if you're interested in English units. What's the definition of BTU?
 
Had my central air system checked when it sortta wasn't working. I guess I hadn't replaced the filter. Guy suggested I might want to get a UV filter accessory. He said it would "kill bugs and particulates". I know UV can kill the former, not sure how he thinks it's gonna murder the latter. Now I'm finding out there's more than one type of UV filter: one for the air flow and one for the coil. He was suggesting we might get one for the air flow, but now we'll have to change the bulb...

Similar threads

  • · Replies 3 ·
Replies
3
Views
2K
  • · Replies 3 ·
Replies
3
Views
3K
  • · Replies 3 ·
Replies
3
Views
3K
Replies
1
Views
3K
  • · Replies 34 ·
2
Replies
34
Views
6K
  • · Replies 4 ·
Replies
4
Views
3K
  • · Replies 3 ·
Replies
3
Views
2K
Replies
6
Views
5K
  • · Replies 17 ·
Replies
17
Views
8K
Replies
6
Views
3K