How does voltage in wires affect conduit and nearby materials?

Click For Summary

Discussion Overview

The discussion revolves around the effects of voltage in wires on conduit and nearby materials, particularly in the context of electrical installations involving high voltage and three-phase motors. Participants explore the implications of running conductors in separate conduits versus together, as well as the safety considerations regarding proximity to metal materials.

Discussion Character

  • Exploratory
  • Technical explanation
  • Debate/contested
  • Engineering installation

Main Points Raised

  • Some participants suggest that running three-phase motor conductors in separate conduits may induce heating due to eddy currents in the conduit, while running them together cancels out the magnetic fields.
  • Others argue that the heating of the conduit is a real phenomenon and reference the National Electric Code to support this claim.
  • A participant raises concerns about the safety of running high voltage DC cables near metal, questioning whether non-ferrous materials are safe and discussing the potential for induced charges on nearby ungrounded metal.
  • There is a mention of arc-over risks associated with high voltage conductors and the importance of maintaining adequate spacing from other conductors.
  • One participant proposes using non-metallic conduit and fasteners to mitigate shock hazards, seeking justification for this approach.

Areas of Agreement / Disagreement

Participants express differing views on the implications of running conductors in separate conduits versus together, with some supporting the idea of induced heating while others provide counterarguments. The discussion on safety regarding high voltage installations also remains unresolved, with multiple perspectives on the risks associated with nearby metal.

Contextual Notes

Participants reference practical tests and codes but do not reach a consensus on the best practices for conduit use or the safety of high voltage installations. The discussion includes assumptions about the behavior of magnetic fields and eddy currents without fully resolving the underlying physics.

Who May Find This Useful

Electrical engineers, safety professionals, and those involved in electrical installations or maintenance may find this discussion relevant to their work.

quikpik
Messages
2
Reaction score
0
Two questions here. From real-world problems, I was hoping someone smarter than me could explain the physics behind some issues I was told about. It's been a long time since I looked at an engineering or physics book, so please bear with me.

1) For a 3-phase motor, I was told that someone had the idea to run each conductor in its own conduit. He thought it was a good idea until the wires started to heat up and melt. Let's assume that the wires were sized for the correct full load amps of the motor. I was told that when the 3 conductors are run in the same conduit, that voltage/current offset each other. When they were run independently, it must've induced some sort of a charge in the conduit causing it to heat up? Is this possible, or is this story made up?

2) If I have a power supply, very high DC voltage (~60kV) with very low current (15mA), do you have to keep the wiring away from all metal? This is more of an engineering installation question, so maybe this isn't appropriate here. I was of the belief that as long as things were non-ferrous, everything would be fine, perhaps even putting the cables in aluminum conduit. I was told this was bad practice. For such an installation, no metal (even non-ferrous) should be within a foot of the cable, due to the possibility of the cable inducing a charge on nearby ungrounded metal. If someone were to then touch that metal, they're liable to get a shock. Is this backed by science?

Thanks for any explanations. It's been a long time since I even had to think about Maxwell or Faraday.
 
Engineering news on Phys.org
quikpik said:
Two questions here. From real-world problems, I was hoping someone smarter than me could explain the physics behind some issues I was told about. It's been a long time since I looked at an engineering or physics book, so please bear with me.

1) For a 3-phase motor, I was told that someone had the idea to run each conductor in its own conduit. He thought it was a good idea until the wires started to heat up and melt. Let's assume that the wires were sized for the correct full load amps of the motor. I was told that when the 3 conductors are run in the same conduit, that voltage/current offset each other. When they were run independently, it must've induced some sort of a charge in the conduit causing it to heat up? Is this possible, or is this story made up?

2) If I have a power supply, very high DC voltage (~60kV) with very low current (15mA), do you have to keep the wiring away from all metal? This is more of an engineering installation question, so maybe this isn't appropriate here. I was of the belief that as long as things were non-ferrous, everything would be fine, perhaps even putting the cables in aluminum conduit. I was told this was bad practice. For such an installation, no metal (even non-ferrous) should be within a foot of the cable, due to the possibility of the cable inducing a charge on nearby ungrounded metal. If someone were to then touch that metal, they're liable to get a shock. Is this backed by science?

Thanks for any explanations. It's been a long time since I even had to think about Maxwell or Faraday.

Welcome to the PF.

1) When the wires are run together in the same conduit, there is no net B-field (the currents cancel). When run alone, it may be that the eddy currents induced in the conduit heat it up too much.

2) The spacing issue is to avoid arc-over from the HV conductors to other conductors.
 
Steel conduit experiencing inductive heating is certainly not made up. See the attached section of the National Electric Code.
 

Attachments

  • 99nec300-20.png
    99nec300-20.png
    35.2 KB · Views: 747
He thought it was a good idea until the wires started to heat up and melt.

he's not the first, by a long shot.

http://media.nowpublic.net/images//97/7/977a0e06c35f94412e56c9d32e1704f5.jpg

Those red magnetic lines heat iron . But it takes substantial current, like to a motor or something, to make it dangerously hot.

if the iron encircles the return conductor too then the two magnetic fields will cancel.
That's why that paragraph in electrical code says run them all together.

If you have a clamp-around ammeter , clamp it around both wires of a lampcord and observe zero reading. Then split the cord and clamp around either conductor observe you read lamp current.

Then repair or replace the lampcord.

old jim
 
Last edited by a moderator:
That's actually a very simple, practical test. I wish I had thought to try that earlier.

As for my second question, would arc-over be an issue since my plan would have been to run the HV cable in aluminum conduit? The cable itself would also be insulated, of course. The shock hazard posed extended to metal fasteners as well, which might be in the vicinity of where the conduit is routed.

I have no problem using all non-metallic conduit, fasteners, etc, I'd just like to convince myself of why it'd be needed.
 

Similar threads

  • · Replies 18 ·
Replies
18
Views
5K
  • · Replies 1 ·
Replies
1
Views
3K
  • · Replies 16 ·
Replies
16
Views
4K
  • · Replies 21 ·
Replies
21
Views
7K
  • · Replies 7 ·
Replies
7
Views
2K
  • · Replies 24 ·
Replies
24
Views
6K
  • · Replies 3 ·
Replies
3
Views
2K
  • · Replies 4 ·
Replies
4
Views
2K
  • · Replies 19 ·
Replies
19
Views
5K
Replies
9
Views
3K