SteamKing said:
Yeah, get an electrician or let the power company run this line and provide the necessary equipment. If you turn yourself into a Roman candle, you won't have anybody to blame but yourself.
Safety shouldn't be a particular issue as long as you use a suitable fuse and Earth Trip. (Also, avoid using the cable on the reel if you want to test the system - it can overheat)
This length of run is problematical, I'm afraid, and would cost a lot, whichever way you want to do it. I bet your local 'professional' would love the job!.
You really have to know the Current demand. The resistance per 100ft (or whatever) for standard wire gauges can be found on the Net an it will be easy for you to work out the total resistance of your cable run (times two because of the return trip!). (2000ft (doubled) of 8 gauge will be about 2.4Ω and, for 12 gauge, about 6.4Ω)
See this link.
The voltage drop can be worked out by multiplying the cable resistance by the current (ignore the fact that the current will be a bit less, due to the cable resistance; it will be a pessimistic answer and put you on the right side). For just 10A, you can expect to lose about 60V over your 12 gauge run! Using 8 gauge over the whole length, the drop would be (pro rata) around 20V, which may not be too embarrassing.
Unless you are dealing with no more than a couple of low wattage lamps, I would think you need to spend a lot more on cable. Imo, just putting in a transformer would not make sense, in such an extreme case as this.
But the numbers count. I looked at the cost of cable and you would be talking in terms of quite a high cost. Commiserations!