I'm currently stuck on a transformer question and require a little clarification
  • Thread starter Thread starter that.kid
    Stuck Transformer
The discussion revolves around calculating the efficiency of a transformer based on open circuit and short circuit test results. The user initially calculated an efficiency of approximately 61%, which is inconsistent with typical transformer efficiencies of around 90%. They discussed the formulas used for power calculations and impedance values obtained from the tests, expressing confusion over the correct method to derive efficiency. The user also referred the short circuit current back to the primary side and provided equivalent circuit parameters. Clarification on the calculations and relationships between various parameters is sought to resolve the discrepancies in efficiency results.
that.kid
A 50 kVA 6360 V/240 V, 50 Hz, transformer is tested on open circuit and short circuit to obtain its efficiency. The results of the tests are as follows:
Open Circuit: Primary Voltage 6360 V, Primary current 1.0 A, Input power 2 kW.
Short Circuit: Voltage across primary 280 V, Current in secondary 175 A, Input power 1kW
power factor at 0.8 lagging
So far I've calculate the impedances using the open circuit and short circuit equations, and I'm having trouble getting the power equations.
I've used P(open circuit) = P(input)*I(open circuit)*cos(theta)
where cos(theta) = PF
I've used P(short circuit) = P(input)*I(short circuit)*cos(theta)
And then P(output)/(P(output) + P(open circuit)+P(short circuit)), and I'm getting an efficiency of ~61%. I'm pretty sure this is wrong.
I think it's wrong because transformers should usually have an efficiency of ~90% and above. To be getting such an inefficient transformer with those values just doesn't seem right. Can anybody please confirm?
I get η>90%. What did you calculate the impedances to be?
From the open circuit test, I got Rc = 7950 ohm, and Xm = 10600 ohm
From the short circuit test, I got z = 1.6 angle 36.86 degrees using the formula z(s/c) = (short circuit voltage/short circuit current) angle theta
I found the angle (theta) from PF = cos theta
I'm not sure what I've done wrong from there, is it possible that you could show me your working out? I followed the notes on open circuit/short circuit test that my lecturer gave me, and I re-watched the video of him lecturing this particular topic, but I found that it hasn't helped much at all, and it's only gotten me more confused.
I know that if I do
(50 * 0.8)/(50 * 0.8 +(2+1)) I get an efficiency of about 93%,
where the 50 is the 50 KVA input voltage, the 0.8 is the power factor, the 2 comes from the 2KW input on the open circuit test, and the 1 comes from the 1KW input on the short circuit test. I think I'm just confusing myself more by doing that though. I saw my lecturer do it this way, and I don't really understand why or what exactly it achieves. Electricity just doesn't like me :P
Have you referred the S/C current back to the primary side for this calculation?
Yes, I have referred it back to the primary and drawn an equivalent circuit. Referring it to the primary I got R(E)=1123.6 and X(Z)=674.16. What equation did you use to calculate the copper/core losses? I've tried P=I^R and P(open circuit)=P(input)*I(open circuit)*power factor and P(short circuit)=V(short circuit)*I(short circuit)*power factor using the values given/calculated for each.
From From the short circuit test, I got z = 1.6 angle 36.86 degrees using the formula z(s/c) = (short circuit voltage/short circuit current) angle thetathe short circuit test, I got z = 1.6 angle 36.86 degrees using the formula z(s/c) = (short circuit voltage/short circuit current) angle theta
How do I relate that↑[/color] to this↓[/color] ?
