Shady data from a transformer’s short-circuit test
Kamakiri
Data from the short-circuit test of a 60-Hz, 100-kVA, 4600–230-V transformer are:
VSC = 172.3 V
ISC = 20.2 A
PSC = 1046 W
Get the per-unit parameters.
2. Relevant equations
ISC ≠ Irated, so how will I solve the problem?
The problem is from the book with ISBN 0130612103.
Kamakiri said:
I_(SC) is unequal to the rated current, so how will I solve the problem?
Rated current is about 100 kVA / 4.6 kV = 21.7 A, so the error-ratio is 21.7 A / 20.2 A = 1.076
So you multiply Vsc and Isc by 1.076.
Multiply Psc by 1.0762. ( P = R * I2. )
The per-unit parameters are the same whether or not I multiplied the data by 1.076 or 1.0762.