Industrial current to pneumatic convertor

Join the discussion
Registration is free. Ask a follow-up in this thread, or start your own.
1 reply · 2K views
zulfiqar
Messages
1
Reaction score
0

Homework Statement


A Current to pneumatic convertor which is shown here in the attachment has the given data which is
Kc=2500N/A (constant of proportionality
X+Y = 100mm
Z=75mm
A=5cm^2

1-to check the response of I/P as per graph what is the suitable value of x and y
2- what is the value of Fs


Homework Equations



Pout = (Kc*Y/A*X)Iin+Fs*Z/A*X

The Attempt at a Solution


Given data is
Kc =2500NA-1 or 2500,000mNA-1

X+Y = 100mm

Z=75mm

A= 5cm^2 or 500mm^2




Solution
The balance equation of the system is

Pout = (Kc * Y/A*X)Iin + Fs*Z/A*X

Y=MX+C




Now by looking the graph the intercept c of the line run through zero so
The Fs*z/A*X part of the equation iS neglected so new equation is lik
Pout = (Kc*Y/A*X) Iin

Or Y = MX





As per the graph the value of
Pout =1 bar or 100,000pascals
Iin = 20mA
now by putting these values in the above equation
100,000 = ( Kc*y/A*X) 20

Kc*Y/A*X = 5000

Now by putting the value of Kc and A

2500,000*Y/500*X = 5000

SO
Y/X = 1
Now as per the given data the

X+Y = 100
And Y = 100-X

Now by putting this value of X in the above equation


100-X/X = 1
100-X =1X
100 =1X+X
100 =2X
X =50mm

Now by putting this value of X in the given x+y =100 we will get the value

X+y = 100

50+Y = 100

Y = 100-50

Y = 50mm

so the value of x = 50mm and Y= 50mm
I am not sure this the correct solution and the unit selection is correct or not
If any friend has some idea about this please guide me
 