K type thermocouple malfunction at 800-1000K

  • Thread starter Thread starter gpsimms
  • Start date Start date
  • Tags Tags
    Thermocouple Type
Click For Summary

Discussion Overview

The discussion revolves around the malfunctioning of K-type thermocouples in a PID heating system, particularly at high temperatures ranging from 800K to 1200K. Participants explore potential causes for erratic temperature readings and the relationship between wiring, grounding, and programming issues within the LabVIEW environment.

Discussion Character

  • Exploratory
  • Technical explanation
  • Debate/contested
  • Mathematical reasoning

Main Points Raised

  • One participant questions whether the DAQ cards have thermocouples wired directly or if there is a buffer (transmitter) involved, suggesting not to wire commons together at the DAQ.
  • Another participant proposes that the issue may stem from the thermocouple weld opening and suggests silver soldering the faulty thermocouples.
  • A later reply indicates that wiring the thermocouple common to ground may have been problematic, as the readings improved but still exhibited issues at higher temperatures.
  • It is noted that the PID system is controlled through LabVIEW, and turning off the PID control loop seems to restore accurate temperature readings at high ranges.
  • Participants discuss the specifics of the heating elements used, including their electrical configuration and connection to the PID system.

Areas of Agreement / Disagreement

Participants express differing views on the root cause of the thermocouple malfunction, with some attributing it to wiring issues and others suggesting potential programming problems. The discussion remains unresolved regarding the exact cause of the erratic readings at high temperatures.

Contextual Notes

There are limitations regarding the understanding of grounding issues and the specifics of the LabVIEW programming that may affect the thermocouple readings. The discussion does not clarify the exact nature of the wiring or programming errors.

gpsimms
Messages
30
Reaction score
1
Hey Everybody,

So we have a PID heating system with K-type thermocouples running through labview. We have a chassis that has 6 DAQ cards for Tc inputs (2 daq cards), flowcontroller in/out, an output for the heating elements for the PID control, and another input for a pressure transducer.

Anyway, the thermocouples give nice reading at most temperatures near room temperature. And the PID system seems to work, as I can control temperature pretty closely in the 300K-800K range. However, when I get to 800K+, some (not all) of the thermocouple readings go kind of nuts. They might randomly spike up to 1200K in a second, and then come down to 400K, etc. If I turn off the heating, after enough time passes and things have cooled back down, they might start behaving normally again.

I have all the DAQ cards coms wired together and then sent together to ground. Is this more likely to be a wiring/grounding issue or is it likely some sort of programming/labview issue? I don't suspect the problem is with the Tc's, as they are pretty new. I have no background at all in circuits, so I kind of think it is most likely something I am doing wrong, but I have to admit, when someone says "It's probably a grounding issue," I don't really understand what exactly that means or how I should ground it differently.

Sorry if this is a really basic question, but I guess this is what happens when a mathematician tries to like, actually do stuff.

Thanks!

simms
 
Engineering news on Phys.org
Does your DAQ cards have thermocouples wired directly into it or is there a buffer which is commonly called a transmitter between the thermocouples and the DAQ? I would not wire any commons together at the DAQ. What are you measuring? Obviously something that gets hot, but how is it heated? Electrically?
 
Sounds to me like the thermocouple Nickel to Chromium weld is opening. I would silver solder the bad ones and give them a try. If you want to run a test of temperature vs t/c voltage, here's a type K temperature (ºC) vs. voltage (millvolts) table.

"www.omega.com/temperature/Z/pdf/z204-206.pdf"
 
Last edited by a moderator:
Thanks for the replies. I definitely think it was bad wiring the Tc common to ground. They are
working better now. But still, not perfectly. Now, instead of freaking out at the 800K range,
they start behaving badly at the 1100K range, and become useless at 1200K. I would really
like to go up to 1200K.

To answer your question, I am using electrical heating elements from Omega. There are two
57-Volt heaters wired in series, and then plugged directly into the wall/PID system. The PID
system is controlled by labview through a different set of DAQ cards, but connected to the
same chassis as the TC Daq cards.

I'm starting to think that there may be a programming issue as well, because I noticed that in
the labview program, when I turn off the "start PID" programming loop, the TCs go back to
giving accurate temperatures, even at the high range.

Here is a picture of everything behaving nicely at 1000, and then heating to 1100, and
starting to bug out a bit:

IXV5Y0V.jpg


Here is a picture of everything working completely terribly as I approach 1200K, but
then when I turn off the 'start PID' switch, the TCs acting a lot better as the temp comes down.

DyKmHst.jpg


Thanks again for all the help!

EDIT: yikes! Sorry they are huge. If someone knows how to fix that, let me know. Thank you!
 
Last edited:

Similar threads

  • · Replies 30 ·
2
Replies
30
Views
4K
  • · Replies 6 ·
Replies
6
Views
2K
  • · Replies 1 ·
Replies
1
Views
2K
  • · Replies 19 ·
Replies
19
Views
4K
  • · Replies 4 ·
Replies
4
Views
6K
  • · Replies 1 ·
Replies
1
Views
5K
  • · Replies 2 ·
Replies
2
Views
7K
  • · Replies 24 ·
Replies
24
Views
6K
Replies
13
Views
5K
  • · Replies 1 ·
Replies
1
Views
2K