MCCB and cable selection for 135A load on 420V 3-phase supply

  • Thread starter MOHAMMADMISBAH
  • Start date
  • Tags Tags
    Cable Doubt
1 reply · 1K views · last reply
MOHAMMADMISBAH
Messages
1
Reaction score
0
hello
i have got a 150A breakerMCCB and the cable connected is 95sqmm and load current is 135A
is this correct or any changes is to be made?
what will happen if the supply is given from 420v 3phase system
 
You have to state:
1) the conductor: copper, aluminum?
2) insulation: PVC, XLPE?
3) single-core or multi-core cable?
4) in air at 40oC, in conduit, in underground [in duct?]
5) if it is embedded in Earth what is Earth temperature and what is the thermal resistivity.
6) how many other cables are in close vicinity?
 