Measuring Power Consumption of a Light Bulb with a Dimmer Switch

Click For Summary

Discussion Overview

The discussion centers around measuring the power consumption of a 100W incandescent light bulb connected to a dimmer switch, specifically addressing the accuracy of plug-in energy monitors when used in circuits with dimmers. Participants explore various methods for measuring power consumption and the potential errors introduced by dimmers.

Discussion Character

  • Exploratory
  • Technical explanation
  • Debate/contested
  • Mathematical reasoning

Main Points Raised

  • Some participants express concern that plug-in energy monitors may provide inaccurate readings (up to 50% error) when used with dimmers, particularly when the light is significantly dimmed.
  • Others argue that power monitors can accurately measure power consumption through various methods, such as using low-ohmage resistors or current transformers, and that chopping the AC voltage does not necessarily affect the accuracy of the readings.
  • One participant suggests an alternative method of measuring power consumption by thermally insulating the dimmer module and measuring temperature changes over time.
  • There is a discussion about the need for RMS values in power calculations and whether the average current value is sufficient for accurate power measurement.
  • Some participants highlight the complications introduced by non-sinusoidal current curves from dimmers and the implications for power calculations.
  • Concerns are raised about the variability of the resistance of incandescent bulbs depending on the dimming level, which complicates power calculations.
  • One participant asserts that the averaging effect of the load voltage over time mitigates the need for squaring current values in certain contexts.

Areas of Agreement / Disagreement

Participants do not reach a consensus on the accuracy of plug-in energy monitors with dimmers, with multiple competing views on the effectiveness of different measurement methods and the implications of dimmer technology on power calculations.

Contextual Notes

Participants mention various assumptions regarding the equipment available for measurements, the nature of the AC voltage, and the characteristics of the load. There are unresolved questions about the accuracy and reliability of different measurement techniques in the presence of dimmers.

baha
Messages
7
Reaction score
0
Hi guys,

For a science experiment I've got to measure the power consumption of my circuit of a 100W incandescent light bulb connected to the mains AC, with a dimmer switch to vary its brightness. I was planning on just using one of those plug-in energy monitors with a digital display but I've heard that when there is a dimmer in the circuit (triac) this would make the readings of these plug-in energy monitors completely wrong - errors up to 50% - is this true? If so how else can I easily measure the power consumption of such a circuit?

Thanks
 
Physics news on Phys.org
Which plug in energy monitor are you referring to? Can you provide a link to a description, or advertisement for sale so we can see which unit it is?
 
The Electrician said:
Which plug in energy monitor are you referring to? Can you provide a link to a description, or advertisement for sale so we can see which unit it is?

Sorry should have said in the original post - it's this one that I've got and want to use http://www.lowenergysupermarket.com/collections/energy-monitors/products/plug-in-energy-monitor
 
You haven't said, but I'm assuming you live in a country where the mains voltage is 230 VAC.

What equipment do you have available for making measurements at your school? Do you have voltmeters, ammeters, oscilloscopes, resistors, capacitors, small transformers, etc.?l

Do you understand how dimmers work (by narrowing the waveform of the applied voltsge)?

I suspect that the circumstance where the error of your energy monitor becomes high is where the light is greatly dimmed, and the applied voltage becomes a very narrow pulse.

What accuracy will be acceptable for your project? Will reduced accuracy be acceptable at the highly dimmed range of the dimmer?
 
baha said:
Hi guys,

For a science experiment I've got to measure the power consumption of my circuit of a 100W incandescent light bulb connected to the mains AC, with a dimmer switch to vary its brightness. I was planning on just using one of those plug-in energy monitors with a digital display but I've heard that when there is a dimmer in the circuit (triac) this would make the readings of these plug-in energy monitors completely wrong - errors up to 50% - is this true? If so how else can I easily measure the power consumption of such a circuit?

Thanks

I doubt that that's true.

Power monitors work in several possible ways.

One way samples the ac current with a very low-ohmage resistor (like 0.01 ohms). That limits the power dissipation of a 1500W load to the sampling resistor to (1500/220)^2 * 0.01 < 0.5W. The sampling ac voltage then ranges from 0 to 68 mV which is then amplified, rectified, filtered, and sent to a dc a-d converter for display.

Reducing the duty cycle of the load by chopping the ac voltage thereto will not affect the accuracy of the filtered dc voltage, hence the displayed power.

Another way is to pass the load current thru a current transformer. The load current is passed thru a 1-turn, very low-resistance primary winding with a large number of secondary windings. This sizable ac voltage is again rectified etc. Again, no problem with a chopped load current.

I use a low-cost Belkin device which has no problem handling chopped line voltages. It has < 1 mW offset and good scale factor accuracy. The only problem for such devices is reactive loads for which VA rather than W is displayed. A chopped resistive load is no problem.
 
As an alternative, you could (carefully - to avoid fires):
* Thermally insulate the dimmer module with a thermometer probe and an unconnected heating resistor.
* Let the dimmer run until it's temperature increases by some about, say 10C.
* Let it all cool down.
* Connect the resistor and measure the time that it takes to get the same temperature increase with a known wattage.
 
rude man said:
I doubt that that's true.

Power monitors work in several possible ways.

One way samples the ac current with a very low-ohmage resistor (like 0.01 ohms). That limits the power dissipation of a 1500W load to the sampling resistor to (1500/220)^2 * 0.01 < 0.5W. The sampling ac voltage then ranges from 0 to 68 mV which is then amplified, rectified, filtered, and sent to a dc a-d converter for display.

I see a couple of problems with this. First you end up with a value proportional to the average (absolute, if full wave rectified, preferably) value of the AC current, when what is needed is the RMS value. Then how does this value for the current become a value for power? Isn't a multiplication by some voltage needed? We don't want to display the current; we want to display power.
 
The Electrician said:
I see a couple of problems with this. First you end up with a value proportional to the average (absolute, if full wave rectified, preferably) value of the AC current, when what is needed is the RMS value.

This is just a matter of scaling. FYI for a sine wave, rms = (1/√2)(2/π) of the fw rectified voltage dc component.
Then how does this value for the current become a value for power? Isn't a multiplication by some voltage needed? We don't want to display the current; we want to display power.

The voltage for the load is known and constant. It's 220V or whatever (in the US, 115V). So again, just a matter of scaling.

Don't confuse load power with sampling resistor power. We are not interested in the sampling resistor power which would indeed require squaring the current (or voltage).
 
Dimmers are often based on varying the conduction angle of thyristors or SCRs, and result in current curves that are non-sinusoidal (and often create an appreciable amount of RFI for the cheaper versions). This will complicate power calculations.
 
  • #10
rude man said:
This is just a matter of scaling. FYI for a sine wave, rms = (1/√2)(2/π) of the fw rectified voltage dc component.The voltage for the load is known and constant. It's 220V or whatever (in the US, 115V). So again, just a matter of scaling.

Don't confuse load power with sampling resistor power. We are not interested in the sampling resistor power which would indeed require squaring the current (or voltage).

The load voltage and current aren't sine waves, which I thought you understood, since you said "Reducing the duty cycle of the load by chopping the ac voltage...".

Also, the OP said "...there is a dimmer in the circuit (triac)..."

rude man said:
Don't confuse load power with sampling resistor power. We are not interested in the sampling resistor power which would indeed require squaring the current (or voltage).

I'm not confusing load power with sampling resistor power.

Obtaining load power would still require squaring the current, if we knew the load resistance.

But, since the load is an incandescent light bulb, the resistance of the bulb is not a constant; it depends on the amount of dimming. Just squaring the current won't work when the load resistance isn't known.

gneill said:
Dimmers are often based on varying the conduction angle of thyristors or SCRs

Which is what the OP said he has (triac rather than SCR); the standard household dimmer style.
 
  • #11
Fellas, it doesn't matter that the load voltage does not consist of integer numbers of sinusoids. The period of the off-on cycle is on the order of seconds (my microwave is actually an unacceptable 30 sec. or so) whereas the ac frequencies are 50 or 60 Hz. Lots of whole 60 Hz load current cycles go undistorted before one cycle is distorted. And on top of that it averages out.

I don't know what else to tell electrician about his "need" to square things. Not necessary at all. Load power = Vi and you know V = 220 and i is measured.

If you really want to be critical you might do some calculations on the required op amp offset voltage precision reuired to do a 16 bit conversion, which my Belkin does. It makes me think the transformer method might be a lot better.
 
  • #12
rude man said:
Fellas, it doesn't matter that the load voltage does not consist of integer numbers of sinusoids. The period of the off-on cycle is on the order of seconds (my microwave is actually an unacceptable 30 sec. or so) whereas the ac frequencies are 50 or 60 Hz. Lots of whole 60 Hz load current cycles go undistorted before one cycle is distorted. And on top of that it averages out.

I don't know what else to tell electrician about his "need" to square things. Not necessary at all. Load power = Vi and you know V = 220 and i is measured.

If you really want to be critical you might do some calculations on the required op amp offset voltage precision reuired to do a 16 bit conversion, which my Belkin does. It makes me think the transformer method might be a lot better.

You apparently don't understand how a triac light dimmer works. The on-off period is not on the order of seconds. How would that be called a "dimmer"? The light would be on full brightness for a few seconds and then completely off for a few seconds.

A triac light dimmer is a phase controlled device. The 50/60 Hz mains waveform is turned on to the load partway through every half cycle, so the on-off period is every 100/120th of a second.

Here's a scope capture showing mains voltage (green), load current (purple) and instantaneous power (dark red) with about half power applied to a 60W incandescent bulb:

attachment.php?attachmentid=66523&d=1392176034.png
 

Attachments

  • MainsPlusLoad.png
    MainsPlusLoad.png
    5.2 KB · Views: 942
  • #13
Thread closed temporarily for Moderation...
 

Similar threads

  • · Replies 51 ·
2
Replies
51
Views
20K
Replies
5
Views
2K
Replies
21
Views
3K
  • · Replies 2 ·
Replies
2
Views
3K
  • · Replies 14 ·
Replies
14
Views
2K
  • · Replies 8 ·
Replies
8
Views
17K
  • · Replies 1 ·
Replies
1
Views
833
  • · Replies 2 ·
Replies
2
Views
752
  • · Replies 1 ·
Replies
1
Views
4K
Replies
1
Views
3K