The discussion revolves around power factor correction for a motor, specifically addressing calculations related to the motor's current, the addition of capacitors, and the resulting power factor adjustments. Participants engage in clarifying the mathematical derivations and the implications of power factor requirements.

Discussion Character

  • Technical explanation
  • Mathematical reasoning
  • Debate/contested

Main Points Raised

  • One participant seeks clarification on the origin of the values 0.51 and 0.28 used in calculations related to the sine of angles corresponding to power factors.
  • Another participant points out the difficulty in reading a posted image, suggesting that the image should be enlarged for better visibility.
  • A detailed breakdown of the motor's specifications and calculations is provided, including efficiency, power input, and current calculations for both the original and corrected configurations.
  • One participant explains the relationship between the power factor and the sine of the angles derived from the arccosine of the power factors, specifically noting the calculations for sin(30.68°) and sin(16.26°).

Areas of Agreement / Disagreement

Participants express differing levels of understanding regarding the calculations and the clarity of the information presented. While some calculations are detailed, there is no consensus on the clarity of the image provided or the initial question regarding the values of 0.51 and 0.28.

Contextual Notes

The discussion includes assumptions about the efficiency and power factor of the motor, as well as the implications of adding capacitors for power factor correction. There are unresolved aspects regarding the clarity of the image and the initial question posed by the participant.

Kasim
Messages
23
Reaction score
0
< Mentor Note -- thread moved to HH from the technical engineering forums, so no HH Template is shown >[/color]

Hi there. I am wondering if someone can help me.. Below is a question and answer, I need help with IV . Where does the 0.51 and 0.28 come from? I've tried cos and sin and thitha but doesn't give me correct number
 

Attachments

  • image.jpg
    image.jpg
    34.3 KB · Views: 572
  • image.jpg
    image.jpg
    30.3 KB · Views: 589
Last edited by a moderator:
Engineering news on Phys.org
Seriously? You ask people for help by posting a tiny unreadable image of something
 
Cant you enlarge it by opening the actual picture? Sorry but I am new here..
 
Kasim said:
Cant you enlarge it by opening the actual picture? Sorry but I am new here..
The "enlargement" is tiny

The issue is not about this forum it's about the size of the image you posted.
 
A 12.5 kW motor is to be powered from a 440 V, 50 Hz supply. Data from

factory testing indicates the motor has an operating efficiency of 85% and

that the power factor is 0.86 lagging. The power utility feeding the factory

requires that the motor’s power factor is 0.96 lagging or better.(i) Explain how the addition of a capacitor to the motor would give the required power factor.

(ii) Determine the motor current in the original configuration.

(iii) Determine the supply current with the capacitor in place.

(iv) Determine the current flowing in the capacitor.

(v) Calculate the value of the capacitance which must be added to give the

desired performance

(vi) Determine the ‘VAr’ rating of the additional component.
 
(ii) Efficiency of motor = Power output/power input,

ð 0.85 = 12500/power input

ð power input = 14706 WPower input = VImcosФ = (440)(I)(0.86)

ð I am = 14706/(440)(0.78) =

ð I am = 42.85 A

The motor current I am is 42.85 A(iii) The current in the parallel capacitor leads the supply voltage by 90°.

The phasor sum of the original current I am and the capacitor current Ic must be such that the supply current Is lags by 0.96 or better.Resistive component of motor current = I am cosФ = (42.85)(0.86) = 36.85 AResistive component of new supply current = Is cosФ’ = Is (0.96) = 0.96 Is AAs resistive component of current does not change => 36.85 = 0.96 Is

=> New supply current, Is = 38.39 A(iv) Reactive component of motor current = I am sinФ = (42.85)(0.51) = 21.87 AReactive component of new supply current = Is sinФ’ = (38.39)(0.28) = 10.75 AAs reactive component of current in capacitor is balance of current => Ic = 21.87 – 10.75

=> Capacitor current, Ic = 11.12 A(v) Capacitor current, Ic = V/Xc => Xc = V/Icð 1/(2πfC) = V/Ic

ð C = Ic /(2πfV) = 11.12/(2π(50)(440))

ð C = 1.26 x 10-4 = 80.44 μF
(vi) The var rating of the capacitor = VIc = (440)(11.12) = 4.89 kvar
 
Old PF is cosФ = 0.86 = arccos(0.86) = 30.68° so the sin of 30.68° degrees is sin (30.68°) = 0.51
Since the new PF must be equal to cosФ = 0.96 = arccos(0.96) = 16.26° so the sin of 16.26° is 0.28.
 
Last edited:
Thank you
 

Similar threads

  • · Replies 31 ·
2
Replies
31
Views
4K
  • · Replies 8 ·
Replies
8
Views
3K
  • · Replies 15 ·
Replies
15
Views
3K
  • · Replies 55 ·
2
Replies
55
Views
9K
  • · Replies 5 ·
Replies
5
Views
3K
  • · Replies 2 ·
Replies
2
Views
3K
Replies
11
Views
4K
Replies
11
Views
3K
  • · Replies 32 ·
2
Replies
32
Views
7K
  • · Replies 2 ·
Replies
2
Views
1K