Windadct said:it is a short time power cycle, every oscillation goes from 0 to about 10X average power - 2 x per cycle. So if you want 100KW avg output many of the components need to be sized to handle 1MW peak power...a significant cost driver - and then there is lifetime - determined by the Temp Swing in the devices, delta T of 60-80C not uncommon -- with a 1-2 Second oscillation you get to millions of thermal cycles very quickly, all you can do is throw more silicon at it. Even putting the energy into a battery would "work" but they also have finite life. Even traditional wind turbines have power electronics lifetime much shorter then expected due to sub-harmonic power surges.
Is there are circuit/control design that is standard in such a high voltage? high variance input situation. I'd love to have a better sense of where the state of the art is in terms of unit and system control for these kinds of machines. Like is anyone using them in an "integrated array" to distribute load variance across a wider field, reducing per unit variance? Anything crazy like that? maybe another thread though. Any reference pointers would be welcome.