Phasor diagram for 3-phase stator voltage drop

5 replies · 4K views · last reply
Cassy85
Messages
1
Reaction score
0
Hi, I'm struggling to find out how to create a phasor diagram. I have attached a photo of the question any help would be greatly appreciated.
Photo of a printed exam question on a textbook page about a three-phase delta-connected synchronous induction motor, with parts 2a and 2b listing phasor and load angle tasks.

This is what I have attempted so far.
It's question 2b I am really struggling with.
I'm not looking for the answers just looking for some direction.

  1. Calculate phase current
Phase current = 250003 x 415 x 0.8
Phase current = 25.1 Amps
cos-10.8=36.87
I = 25.1 ∠36.87° Amps
  1. Calculate the stator reactive voltage drop IXs

Voltage drop = IaXs
25.1 x 4 ∠36.87° + 90°
Voltage drop (IXs) = 100.4 ∠126.87° volts
 
First no such motor "synchronous induction motor" does exist .Since the power factor is leading it is about synchronous motor when the excitation current is more than rated.
The motor has an a.c. winding in stator part and a d.c. winding [poles] on the rotor. Since it is a separately E noted, the generated voltage is equal to supply voltage.
The generated voltage has to be in the load case.
If the power mentioned is "input power" the apparent power it is the ratio 25/0.8.
Phasor diagram of an overexcited synchronous motor showing current I_A leading the terminal voltage V_phi by angle theta, load angle delta, E_A cos delta greater than V_phi, and the jXs*I_A drop from E_A to V_phi.

The loaded current it is 25000/0.8/√3/415=43.475 A
 
Actually this is the current from the network. The current in the motor winding in triangle it is only 25.1A, indeed.
 
Attachments
  • Phasor diagram on a grid: vector AB labelled IAB=25.1 A points right, vector BC runs from B down-left to C, vector CA closes the triangle, and red vector BB' points up-right labelled 43.475 A, From the network, BB'=AB-BC.
    Triangle currents.jpg
    27.3 KB · Views: 248
In my opinion, the power factor and Xs are calculated from the network point of view so for an equivalent star motor. In this case the current IA= 43.475 A and is leading the phase-to-neutral voltage VAN with φ= 36.87 degrees. Then the voltage drop [total] is IA*[cosφ+jsinφ]*jXs and the reactive part is jIA*cosφ*Xs.
 
The vectorial diagram it could be like this one:
 
Attachments
  • Phasor diagram of three-phase voltages and currents on a dashed circle: VAB, VAN, VBN, VBC, VCA and VCN voltage phasors in blue, and IA, IAB, IBC, ICA and -IBC current phasors in red, with angles 6.86°, 30°, 36.86° and 23.14° marked.
    synchronous motor vectorial diagram.jpg
    48.4 KB · Views: 236
My mistake. The voltage considered for equivalent motor is not
“the leading the phase-to-neutral voltage” as I said but the phase-to-phase voltage. So, the vectorial diagram on the trigonometric circle it has to be like this:
 
Attachments
  • Phasor diagram on a dashed circle showing three-phase line-to-line voltages VAB, VBC and VCA, line-to-neutral voltages VAN, VBN and VCN, and currents IA, IAB, IBC, -IBC and ICA, with angles 30 degrees, 36.86 degrees and 6.86 degrees marked.
    synchronous motor vectorial diagram.jpg
    44.9 KB · Views: 251