A power plant is experiencing a load spike issue with one engine dropping to zero kW and then quickly recovering, following a previous generator blast accident. The plant operates in droop mode using heavy furnace oil and is not connected to the grid. There are concerns about the control system, as a communication failure occurred, preventing the emergency stop from functioning. Additionally, the hardware panel's ground connection was found to be faulty, which may contribute to the problem. Monitoring fuel pressure and injector rack position is suggested to diagnose the underlying issues effectively.
Asghar Hussain
Messages
3
Reaction score
0
Dear All,

one of our power plant has load spike when engine is running in parrell operation 7 * (3.5MW) capacity.

one engine suddenly down the load at zero kw in three seconds again load pick at full load .
this engine had an accident of generator blast last year.
please advise
 
Engineering news on Phys.org
Diesels ?
Sounds like a governor or fuel pressure problem.
Can you connect some sort of recorder to monitor to fuel pressure and injector rack position?
 
Are you saying the one generator rejected load after a system load spike and then attempted to take on load again? Or did you mean the load reduction on one generator caused a spike in the other six generator loads?

Also define sudden. Do you mean a few cycles or seconds?
 
Are you running in Island mode or connected to a grid? What type of fuel control do you have, mechanical, electronic? Are you running in droop or load control?
 
Dear All,

plant is running droop mode not connected with grid
fuel type HFO heavy furnace oil engines, this engine is software control,
during operation communication failure appeared and all parameters held (hang) emergency stop does not work.
this engine one accident of over speed alternator rotor poles broken

today we found that control system hardware panel Earth (ground) is not connected may have this reason for this issue, please give your comments.
 
this engine is software control, ...
during operation communication failure appeared and all parameters held (hang) emergency stop does not work.

I never trust a computer with anything important.

I hope it has a centrifugal overspeed trip. If not, stay physically away from it.
 
Hey guys. I have a question related to electricity and alternating current. Say an alien fictional society developed electricity, and settled on a standard like 73V AC current at 46 Hz. How would appliances be designed, and what impact would the lower frequency and voltage have on transformers, wiring, TVs, computers, LEDs, motors, and heating, assuming the laws of physics and technology are the same as on Earth?
I used to be an HVAC technician. One time I had a service call in which there was no power to the thermostat. The thermostat did not have power because the fuse in the air handler was blown. The fuse in the air handler was blown because there was a low voltage short. The rubber coating on one of the thermostat wires was chewed off by a rodent. The exposed metal in the thermostat wire was touching the metal cabinet of the air handler. This was a low voltage short. This low voltage...
Thread 'Electromagnet magnetic field issue'
Hi Guys We are a bunch a mechanical engineers trying to build a simple electromagnet. Our design is based on a very similar magnet. However, our version is about 10 times less magnetic and we are wondering why. Our coil has exactly same length, same number of layers and turns. What is possibly wrong? PIN and bracket are made of iron and are in electrical contact, exactly like the reference design. Any help will be appreciated. Thanks. edit: even same wire diameter and coil was wounded by a...