Question about a PD controller.

  • Thread starter Thread starter nylonman
  • Start date Start date
  • Tags Tags
    Controller Pd
Click For Summary
SUMMARY

The discussion centers on the use of a PD (Proportional-Derivative) controller in control engineering, specifically regarding its impact on the root locus plot of a system. The user seeks clarification on how the introduction of a zero affects the system's response, particularly when the leftmost pole is ignored. It is established that while the leftmost pole can be disregarded, the zero's presence is crucial as it influences the movement of the leftmost pole towards it, thereby affecting the overall system dynamics. A large gain (kd) can lead to the leftmost pole coinciding with the zero, which, although beneficial for stability, may result in a slower system response due to the pole's proximity to the right-half plane.

PREREQUISITES
  • Understanding of PD controller design in control systems
  • Familiarity with root locus plots and their interpretation
  • Knowledge of complex conjugate poles and their significance in system stability
  • Experience with gain tuning and its effects on system dynamics
NEXT STEPS
  • Explore the effects of varying gain (kd) on system response in PD controllers
  • Study the implications of zeros in control system design
  • Learn about the stability criteria for systems with poles in the right-half plane
  • Investigate advanced control strategies, such as PID controllers, for improved performance
USEFUL FOR

Control engineers, students in control engineering courses, and practitioners involved in designing and analyzing control systems will benefit from this discussion.

nylonman
Messages
11
Reaction score
0
Hi, I'm taking a control engineering course and I've got a little doubt about PD controllers.

Here is my root locus plot: http://imageshack.us/photo/my-images/535/controlw.png/

I have the system defined by the poles in the root locus with some design specifications that are satisfied when the complex poles are in the same position as the green stars. In order to move the branches of the root locus a PD controller is used, so a zero appears in the plot. With a specific gain the specifications are satisfied as shown in the right plot.

My question is: the specifications are computed assuming a normalized second order system, so the transfer function of the final system would have only the two complex conjugate poles. I know that the leftmost pole can be ignored, but what about the remaining zero? Wouldn't it affect the response?

Any help will be appreciated!
 
Last edited:
Engineering news on Phys.org
When placing your two right most poles using the gain kd, your left most pole will tend to move toward the zero position at some position specified by kd also. So if you're ignoring the left most pole only, then it has the same effect of ignoring both the left most pole and the zero, since the zero is only there to assure that the pole moves towards it (As shown by the green line)
 
The zero is just an "end point" of the locus of the left most pole.

In other words, if the gain is large enough, the left most pole coincides at the zero which is still good because it sits on the negative real axis. However, system response is slower due to the pole approaching right-half plane.
 
Last edited:

Similar threads

  • · Replies 12 ·
Replies
12
Views
4K
Replies
4
Views
5K
  • · Replies 3 ·
Replies
3
Views
2K
Replies
1
Views
3K
  • · Replies 4 ·
Replies
4
Views
5K
  • · Replies 1 ·
Replies
1
Views
2K
Replies
1
Views
2K
  • · Replies 3 ·
Replies
3
Views
3K
Replies
4
Views
4K
  • · Replies 1 ·
Replies
1
Views
6K