To calculate the relative humidity (RH) after cooling a room from 30 degrees Celsius with 30% RH to 25 degrees Celsius, it is essential to consider the equilibrium vapor pressures at each temperature. At 30 degrees Celsius, the partial pressure of water vapor is 1275 Pa, while at 25 degrees Celsius, the equilibrium vapor pressure is 2340 Pa. Since no water is removed from the air during cooling, the final RH at 25 degrees Celsius is approximately 40%. However, if the air conditioner’s evaporator temperature drops below 10 degrees Celsius, condensation may occur, affecting the humidity levels. Understanding these factors is crucial for accurate humidity calculations in air conditioning scenarios.
studentLearn
Messages
1
Reaction score
0
Hello everyone,
I have a question about calculating Relative humidity.
If I have a surrounding with 30 degrees Celsius and RH of 30%.
I am cooling the surrounding with an air conditioner that works at 15 degrees Celcius.
At the end of the process, the room reaches 25 degrees Celcius.
In this situation, there is no condensation in the process.
How can I calculate what is the RH at the end of the process?
Thank you very much
 
Science news on Phys.org
Welcome!
Are you sure there is no condensation on the evaporator of the machine?
 
The equilibrium vapor pressure of water at 30 C is 4250 Pa, and, for 30% RH, that means that the partial pressure is 1275 Pa. At 15 C, the equilibrium vapor pressure is 1700 Pa, so no water will condense. At 25 C, the equilibrium vapor pressure is 2340 Pa. So, with a partial pressure of 1275 Pa, what will the RH be at 25 C?
 
  • Like
Likes Lord Jestocost
What you need is known as a "psycrometric chart." The answer will vary somewhat based on your elevation, but there are charts for many different elevations and some correction factors for stuff inbetween. Long story short, without removing any water from the air (looks about 8g H2O/kg dry air), at sea level your final humidity is around 40%.

Note: Although the cool air coming from the AC might be at 15 degrees, as Lnewqban points out, the temperature of your AC evaporator could be much less, and if the coils are less than about 10 degrees, you will be getting some condensation out of the air.
 
  • Like
Likes Lnewqban and russ_watters
I need to calculate the amount of water condensed from a DX cooling coil per hour given the size of the expansion coil (the total condensing surface area), the incoming air temperature, the amount of air flow from the fan, the BTU capacity of the compressor and the incoming air humidity. There are lots of condenser calculators around but they all need the air flow and incoming and outgoing humidity and then give a total volume of condensed water but I need more than that. The size of the...
Thread 'Why work is PdV and not (P+dP)dV in an isothermal process?'
Let's say we have a cylinder of volume V1 with a frictionless movable piston and some gas trapped inside with pressure P1 and temperature T1. On top of the piston lay some small pebbles that add weight and essentially create the pressure P1. Also the system is inside a reservoir of water that keeps its temperature constant at T1. The system is in equilibrium at V1, P1, T1. Now let's say i put another very small pebble on top of the piston (0,00001kg) and after some seconds the system...