Resistive load bank testing for generator

Click For Summary
SUMMARY

The discussion centers on resistive load bank testing for generators, specifically addressing the power factor (pf) implications during testing. A technician encountered issues while load banking a 25kVA generator at 480V, where the data plate indicated a maximum of 30.1 amps and a power factor of 0.8. It was concluded that the generator's active power capacity is 20 kW, allowing for a maximum current of 24 amps under resistive load conditions. The conversation highlights the importance of considering both electrical and mechanical limitations when testing generators.

PREREQUISITES
  • Understanding of generator specifications, including kVA and power factor.
  • Knowledge of resistive load bank testing principles.
  • Familiarity with electrical power calculations, including active power capacity.
  • Basic concepts of electrical limitations in generator performance.
NEXT STEPS
  • Research "Generator power factor calculations" to understand its impact on load testing.
  • Learn about "Resistive load bank design" to optimize performance for generator testing.
  • Explore "Mechanical limitations in generator operation" to ensure comprehensive testing.
  • Study "Electrical power capacity of generators" to accurately assess load bank requirements.
USEFUL FOR

Technicians, electrical engineers, and anyone involved in generator testing and maintenance will benefit from this discussion, particularly those focusing on load bank testing and power factor considerations.

pic498
Messages
1
Reaction score
0
Ok, so here's my scenario/question. I am a technician that works on generators and does load bank testing on them. I'm having a debate with my boss about power factor and IF I'm wrong--I would like to understand why.
Today I load banked a generator that was rated at 25kVA and could run at 120/240 single phase, 120/208 3 phase, or 277/480 3 phase. I was running the generator on the 480 setting and, according to the data plate, the max amps at 480 is 30.1. The power factor on the data plate says .8, however the load bank is purely resistive and has a pf of 1.0. So, I put 30.1 amps on it and the generator couldn't take it. My boss told me that I was overloading the generator and that i need to factor in the .8 power factor, but my thinking is--the load is a 1.0 so i need to forego the pf and run it at what the data plate says. Who is right and who is wrong? a little explanation of pf would be helpful. thanks.

matt
 
Engineering news on Phys.org
He is right. Generally in generators we face the two group limitation, mechanical and electrical limitation. In your description you just concentrate to machine electrical characteristics whereas you should check the mechanical performance of machine too.
Seemingly, the active power capacity of your machine is 25/0.8 = 20 KW, if it is right, you can drive a resistive load with maximum current of 24 A (20000/1.73*480) not 30.1 A.



-----------------------------------------------------------------
Creative thinking is enjoyable, Then think about your surrounding things and other thought products. http://electrical-riddles.com
 
Resistive load bank for testing generators

We have developed a resistive load bank 30 KWatts in our setup based on readings we have taken on different loads with different generators and maximum current rating observed was 36 Amperes at 0.8 Pwr Factor. Therefore, we designed our load bank catering to the maximum current being drawn by the load and developed our load bank with a capacity of 45 Amperes (which is 20 % over and above the observed current).

Now, the user is objecting on our design on the premise that we have designed our load bank as purely resistive bank of loads without appreciating the fact that our developed load bank design is already catering the maximum current rating.

Kindly offer your comments whether there are going to be any parameters which will remain un-checked if our load bank is connected to a generator having same specifications (i.e 30 KVA).

Best regards

Adeel
 

Similar threads

  • · Replies 38 ·
2
Replies
38
Views
7K
Replies
12
Views
3K
  • · Replies 10 ·
Replies
10
Views
2K
Replies
1
Views
3K
Replies
9
Views
2K
Replies
15
Views
2K
  • · Replies 11 ·
Replies
11
Views
4K
  • · Replies 5 ·
Replies
5
Views
2K
  • · Replies 8 ·
Replies
8
Views
2K
  • · Replies 5 ·
Replies
5
Views
4K