Ok, so here's my scenario/question. I am a technician that works on generators and does load bank testing on them. I'm having a debate with my boss about power factor and IF I'm wrong--I would like to understand why.
Today I load banked a generator that was rated at 25kVA and could run at 120/240 single phase, 120/208 3 phase, or 277/480 3 phase. I was running the generator on the 480 setting and, according to the data plate, the max amps at 480 is 30.1. The power factor on the data plate says .8, however the load bank is purely resistive and has a pf of 1.0. So, I put 30.1 amps on it and the generator couldn't take it. My boss told me that I was overloading the generator and that i need to factor in the .8 power factor, but my thinking is--the load is a 1.0 so i need to forego the pf and run it at what the data plate says. Who is right and who is wrong? a little explanation of pf would be helpful. thanks.
matt
Today I load banked a generator that was rated at 25kVA and could run at 120/240 single phase, 120/208 3 phase, or 277/480 3 phase. I was running the generator on the 480 setting and, according to the data plate, the max amps at 480 is 30.1. The power factor on the data plate says .8, however the load bank is purely resistive and has a pf of 1.0. So, I put 30.1 amps on it and the generator couldn't take it. My boss told me that I was overloading the generator and that i need to factor in the .8 power factor, but my thinking is--the load is a 1.0 so i need to forego the pf and run it at what the data plate says. Who is right and who is wrong? a little explanation of pf would be helpful. thanks.