Shear force and bending moment for triangular distributed load on 4.8m beam
1 reply · 7K views · last reply
jasonbot
I have to find the Shear Force and Bending Moment diagrams for this problem. The lengths in the picture are 1.2m each and the peak force is 4kN/m and I calculated the support reactions to be:
Ay=4,8kN (up)
Ma= 5.76kN.m (anticlockwise)
These are what I'm looking for but failed to do...
I first section the beam 0<x<4
Efy=0
+4.8 -.5x*3.33x-Vx=0
I got the 3.33x by using similar triangles; if triangle 1 is (1,2;4) then sectioned triangle should be (x;y) so therefore 4/1.2=y/x x=3.33xthis gave me Vx=-1.67x^3+4.8 which is wrong.
Then EMo=0
+Mx +.5x*3.33x*(x/3) -4.8x +5.76=0
which gets me Mx=-0.56x^3 +4.8x +5.76The correct answers for this question are:
Vx=4.8 -(x^3/6)
Mx=4.8x -(x^3/18) -5.76I have a feeling I'm not using the triangle force correctly. Please advise.
  • Beam diagram with fixed support at left end A and a triangular distributed load peaking at 4 kN/m at midspan; total span labeled 1.2 m and 1.2 m on either side.
jasonbot, welcome to PF!
Is it 12 m or 1.2 m?
Ay=4,8kN (up)
yes, looks good
0<x<12 m
Efy=0
if you correct the 1.2 m to 12m , then Vx = -.167x^2[/color] +4.8
Then EMo=0
something is afoul between 1.2 m and 12 m, the decimal point is messed.., but you are still not quite right, don't let the plus and minus signs wear you down...
Vx=4.8 -(x^2[/color]/6)
typo error
taking clockwise moments as plus, I don't know about that decimal point, however
Looks like you did well, but check out your plus and minus signs, they'll bite you every time...