  • One participant suggests calculating the force needed to open the cover using the weight of the cover and the angle, arriving at a static pressure requirement of approximately 63.8354 Pa based on airflow area.
  • Another participant questions the angle used in calculations, suggesting it should be 20 degrees instead of 15 degrees due to the duct mouth chamfer.
  • Concerns are raised about whether the calculated pressure is static or dynamic, with some participants indicating it may be both.
  • A participant proposes using a balanced door or a counterweight to reduce the force needed to open the cover, while another suggests adding a spring as a counterweight.
  • One participant mentions the need to account for pressure drop along the duct, suggesting that the static pressure at the fan should be higher than initially calculated.
  • A later reply introduces the idea of using compressed air to assist in opening the cover, given the updated system with back pressure from new equipment.

Areas of Agreement / Disagreement

Participants express differing views on the calculations and methods for determining the necessary fan static pressure, with no consensus reached on the best approach or the accuracy of the calculations presented.

Contextual Notes

Participants note limitations in the calculations, including assumptions about the angle of the cover, the distinction between static and dynamic pressure, and the impact of duct pressure drop on overall requirements.

longz
Messages
11
Reaction score
0
Hi all great PF members,

Can anyone help me to sizing fan static pressure strong enough to open a metal cover an angle 15 degree at the end of the duct (20m in length with few 90 degree bends), I'm really not good at math so any help are greatly appreciated. Please refer to sketch attached for clear view.

Sorry for weak English.

upload_2016-12-29_14-54-35.png
 
Physics news on Phys.org
Welcome to PF.
You specify the air flow rate, the mass and the angle of door. That over constrains the solution.
Maybe you could approach it this way.
The 4kg cover hanging at 15° will need a force of 4 kg * Sin( 15° ) * 9.80665 m.s-2 Newton acting at the centre.
4 * Sin( 15° ) * 9.80665 = 10.15 N
The 450 mm diameter flow has an area of 0.159 square metres.
The pressure will therefore need to be 10.15 / 0.159 = 63.8354 Pa
The dynamic pressure of a flow is Pa = ½ * density * v2 pascal
The density of standard air is 1.225 kg/m3
Therefore v2 = Pa * 2 / density = 104.2
Therefore v = 10.2 m/sec
The cross section of the duct is 0.159 m2
Which requires a flow of 10.2 * 0.159 = 1.623 m3/sec = 1623. litre/sec.

But you only specify a flow of 40 litre/sec.
 
  • Like
Likes   Reactions: longz
Could you use a balanced door so that only a small force would be needed to open it ?
 
  • Like
Likes   Reactions: longz
Hi Baluncore,

Thank a lot for your guides. I have some queries about your calc., Sin( 15° ) or Sin( 20° ) is correct ? the duct mouth chamfer 5° therefore cover open with an angle 20° to vertical axis.

The result 63.8354 Pa is static or dynamic pressure ? if this is dynamic so how to find the static pressure ?

I had a mistake when mentioned air flow rate 40 litre/sec, it should be "minimum 40 litre/sec" as duty request air changes factor minimum 3 times of duct volume / 5 minutes (equiv. 32 litre/sec). Due to very tight room I can't chose a fan with big air flow, an ideal is sizing fan with enough pressure with airflow rate just enough.
 
Nidum said:
Could you use a balanced door so that only a small force would be needed to open it ?

Thank Nidum, the balanced door look not suitable to this case as the hinge axis is horizonal not vertical as door. I'm thinking a counterweight on the cover may works.
 
longz said:
I have some queries about your calc.
Check my calculations carefully, especially the units. It was only a guess at the best approach.
Yes, the duct cover angle needs to be increased to 20°.

longz said:
The result 63.8354 Pa is static or dynamic pressure ?
I believe it is both.
We do know that the dynamic pressure of the duct airflow will act on the door. I assumed it would act at the centre of the door and ignored the height of the hinge.
The force needed to hold the duct cover open is known, but we do not know where the static pressure will be dropped as the air escapes from the duct through the partly open cover.
You might consider a lighter-weight duct cover to save energy.
 
Take into consideration the pressure drop along the 20m duct , the static pressure at the fan will be higher by 20-30% from the above calculated value
 
you could add spring to act as counter weight
 
Thank Malemk for your advises.
The ducting system has just updated with an equipment installed at the outlet of the fan with back pressure 40 mBar !. the fan now come to quite huge .
I come up with an solution use available compressed air to push the cover open and the fan just blow air out.

One again, Much appreciated to all great PF guys and Happy New Year 2017 to all.
 

Similar threads

  • · Replies 12 ·
Replies
12
Views
5K
  • · Replies 15 ·
Replies
15
Views
4K
Replies
6
Views
8K
  • · Replies 7 ·
Replies
7
Views
11K
  • · Replies 14 ·
Replies
14
Views
7K
  • · Replies 5 ·
Replies
5
Views
2K
  • · Replies 3 ·
Replies
3
Views
2K
  • · Replies 19 ·
Replies
19
Views
3K
  • · Replies 1 ·
Replies
1
Views
3K
Replies
5
Views
5K