The discussion revolves around determining the appropriate size of a transformer for a system with a 480 V primary and a 120 V secondary, supplying approximately 10 A in a 3-phase configuration. Participants explore various considerations for selecting the transformer, including specifications, calculations, and the necessity of phase type.

Discussion Character

  • Technical explanation
  • Debate/contested
  • Mathematical reasoning

Main Points Raised

  • One participant suggests that the transformer should be purchased from a catalogue to ensure proper specifications, implying that constructing one may not be feasible for the inquirer.
  • Another participant questions whether a 3-phase transformer is necessary, proposing that a single-phase transformer might suffice and asks for clarification on how the 10 A was calculated.
  • A different participant notes that the power requirement appears low and suggests that a larger transformer might be beneficial for one-off equipment, while emphasizing the importance of accurate estimates for larger quantities.
  • One participant provides a formula for calculating transformer size, suggesting that a transformer with a minimum capacity of 2.5 kVA should be used, while also highlighting the need to consider the power factor of the equipment.

Areas of Agreement / Disagreement

Participants express differing views on the necessity of a 3-phase versus a single-phase transformer, and there is no consensus on the optimal transformer size or the calculation methods. The discussion remains unresolved regarding the best approach to sizing the transformer.

Contextual Notes

Participants mention various assumptions regarding power requirements and the importance of considering factors like power factor and potential voltage drops, but these assumptions are not fully explored or agreed upon.

Who May Find This Useful

Individuals involved in electrical engineering, particularly those working with transformer sizing and power distribution in industrial or commercial settings, may find this discussion relevant.

Som_P
Messages
6
Reaction score
0
480 V primary
120 V secondary.

9 temperature controllers and 2 power supplies coming off the 120VAC

total Amps are ~10A

This is 3-phase. How do I find the right size transformer?
 
Engineering news on Phys.org
You go to a catalogue and buy one with the right specification. It is the only way to be sure. You will not be able to make one for yourself (if you need to ask this particular question).
 
Do you require a 3 phase transformer or a single phase transformer?
My guess is a single phase transformer.
How did you calculate the 10A?
 
It always helps to describe your problem is more depth than you have done. On the face of it, the requirement is relatively low power and it does seem unlikely that you would need 3Phase.
If it is a one-off piece of equipment then there is no harm in going a bit bigger than you think you may need. If you are doing this in hundreds, then the economics of a cheaper and smaller transformer may make it worthwhile to get your estimate more accurate.
 


I would suggest using the following formula to calculate the required size of the transformer:

Transformer size (VA) = (Total Amps x Secondary Voltage)/Primary Voltage

In this case, the required transformer size would be:

Transformer size = (10A x 120V)/480V = 2.5 kVA

This means that a transformer with a minimum capacity of 2.5 kVA should be used to power the 9 temperature controllers and 2 power supplies. It is important to note that the transformer size should always be slightly larger than the calculated value to allow for any potential voltage drops or fluctuations.

Additionally, it is important to consider the power factor of the equipment being powered by the transformer. If the power factor is less than 1, the transformer size should be adjusted accordingly to ensure proper power supply.

In summary, using the appropriate formula and considering the power factor, the right size transformer can be determined to efficiently power the equipment in question.
 

Similar threads

  • · Replies 8 ·
Replies
8
Views
3K
Replies
6
Views
4K
Replies
2
Views
2K
  • · Replies 1 ·
Replies
1
Views
5K
Replies
5
Views
2K
Replies
12
Views
3K
  • · Replies 5 ·
Replies
5
Views
3K
Replies
9
Views
6K
  • · Replies 27 ·
Replies
27
Views
2K
Replies
7
Views
8K