cnh1995 said:
But what makes it rotate at a constant speed after providing extra torque? Is it the "motor action" of injected reactive current that creates an opposing torque?
Motor action is exact right term but the current that produces torque is the real component not the reactive...
Note in that phasor sketch above armature and field fluxes are nearly perpendicular so torque results. Were they aligned, they simply aid or oppose instead of making torque.
cnh1995 said:
Also, when the grid injects reactive current into the machine, total flux remains constant and hence, terminal voltage remains constant. Then when exactly are AVRs used?
AVR is on nearly all the time.
Have you studied "Armature Reaction" ?
If not it's okay.
AVR holds terminal voltage constant when load on the grid changes.
If you just hold constant excitation, terminal voltage will sag when customers get home and switch on their airconditioners.
In simplest terms, a utility generator is like any other voltage source it has internal impedance. In fact, quite a bit of it and it's mostly inductive.
Think of the generator as a Thevenin, an internal ideal voltage source in series with that internal impedance.
The AVR measures terminal volts and adjusts the internal source so as to cancel the drop across that internal impedance.
That keeps customers' voltage nearly constant.
cnh1995 said:
The voltage is kept constant by the grid itself.
Hmmmm i sort of think the other way
the grid is held constant by the combined actions of the hundreds of AVR's working to that end.
Were a generator actually tied directly to an infinite bus you're right, it could not change terminal volts.
Go back to the thevenin idea for a moment
V
bus is fixed, so is Z
internal
If you change V
internal by changing excitation,
machine amps will change by ΔV
internal / Z
internal
and Z
internal being (mostly) inductive and fixed, Δmachine amps will be reactive. That's why voltage regulator controls Vars. AVR's keep each machine's Var contribution constant, too
All the AVR's acting in concert is what keeps V
bus nearly constant.and the system stable.
There are whole books on this subject
i hope this helps prepare you for Anorlunda's insight article. I'm no power engineer , just try to help folks over the basic stumbling blocks i crawled across.
You'll get to where you work the system in your head. Hang in there. Does your school have a machinery lab? It is very instructive to shine a stroboscope on a generator shaft and watch the angle change with load and excitation, then figure out why.. That was my favorite EE course - we had ~10hp machines and dynamometers...
old jim