Transformer Calculations: 200 kVA, 415V to 11 kV, 0.8 PF at 2% Regulation

Click For Summary

Discussion Overview

The discussion revolves around calculations related to a 415V to 11 kV transformer with a rating of 200 kVA, focusing on determining voltage regulation at different power factors and analyzing winding resistances. The scope includes theoretical calculations and practical considerations in transformer design.

Discussion Character

  • Homework-related
  • Technical explanation
  • Debate/contested

Main Points Raised

  • Post 1 presents a calculation for voltage regulation at 0.8 power factor lagging and discusses the implications of winding resistance for achieving 2% regulation at unity power factor.
  • Post 2 and Post 3 assert that the transformer is likely a 3-phase transformer, questioning the absence of explicit data regarding reactance in the problem statement.
  • Post 4 seeks clarification on the reasoning behind considering the transformer as 3-phase, suggesting that the voltage levels are typical for distribution systems.
  • Post 7 and Post 8 inquire about common applications for 415V to 11 kV transformers, speculating on their use in small wind farms and as step-down transformers on power poles.
  • Post 9 challenges the equation for voltage regulation presented in Post 1, expressing confusion over its units and suggesting that the higher voltage winding should be considered the primary winding.
  • Post 10 reiterates the original question and defends the use of the equation based on course material.
  • Post 11 introduces a per unit system approach to the calculations, showing that the results align with those obtained in Post 1, while also expressing a preference for this method.

Areas of Agreement / Disagreement

Participants express differing views on whether the transformer is a single-phase or three-phase device, and there is no consensus on the interpretation of the problem statement regarding reactance. Additionally, there are varying opinions on the appropriateness of the voltage regulation equation used.

Contextual Notes

Some participants note the lack of information regarding reactance in the problem statement, which may affect the calculations. There is also a discussion about the definitions of primary and secondary windings that remains unresolved.

Numbskull
Messages
54
Reaction score
1

Homework Statement



A 415V to 11 kV transformer has a rating of 200 kVA. The winding resistance and leakage reactance when referred to the primary are 0.014 ##\Omega## and 0.057 ##\Omega## respectively.

(a) Determine the % regulation of the transformer at 0.8 power factor lagging.

(b) In designing a particular 415V to 11 kV, 200 kVA transformer, the primary winding resistance is to be 10 m##\Omega##. Find the maximum winding resistance of the secondary winding if the transformer is to have 2% regulation at unity power factor.

Homework Equations


% Regulation = ## \frac {{VA}_{rating}} {V_1^2} ## x (R’p cos ##\theta## + X’p sin ##\theta##) x 100%

The Attempt at a Solution


(a)
##\frac {200 \times 10^3}{(415)^2}## x ((0.014 ##\times## 0.8) + (0.057 ##\times## ##\sqrt{1 - 0.8^2}))## x 100% = 5.272% regulation

(b)
Voltage regulation (%) ## \approx \frac {200 \times 10^3}{(415)^2} ## x R'p x 100%

Rearranging to make R'p the subject, I get 17.2225 m##\Omega## (as the primary reflected impedance), and this is only an approximation according to the formula provided in the textbook.

Trying to analyse this part in my head, I think that I need to get that primary impedance down to 10m##\Omega##. This means that I need to alter (calculate) the maximum current / voltage on the secondary side taking the 2% voltage drop, leakage reactance and 200kVA max power into consideration?

I'm keen to learn this as per the forum principles, but some gentle guidance would be welcome :smile:
 
Physics news on Phys.org
Numbskull said:
A 415V to 11 kV transformer has a rating of 200 kVA.
This would be a 3-phase transformer, even though not stated explicitly. Does your textbook give their answer?

In part (b) there is no data given concerning reactance, so you'll regard reactance as zero.
 
NascentOxygen said:
This would be a 3-phase transformer, even though not stated explicitly. Does your textbook give their answer?

In part (b) there is no data given concerning reactance, so you'll regard reactance as zero.
I'm interpreting the question as a single phase transformer with the constraints in the first paragraph, but with the special considerations laid out in part (b). I do not think it is anything other than a single phase transformer. What would make you think it might be a 3-phase transformer, would it be because of the voltages involved are typical of distribution grid values?
 
Numbskull said:
What would make you think it might be a 3-phase transformer, would it be because of the voltages involved are typical of distribution grid values?
Those are the precise 3ɸ voltages seen on our 240V system here (in Australia). What country was your textbook printed for?
 
It's a UK print.
 
Numbskull said:
It's a UK print.
Then ditto.
 
Just curious but where are 415V to 11KV step up transformers used most? Small wind farms?
 
CWatters said:
Just curious but where are 415V to 11KV step up transformers used most? Small wind farms?
Maybe, I don't know.
But turned around they are used as 11kV:415V step-down on powerpoles. ☺
 
Numbscull-

I'm not sure I agree with your first equation for voltage regulation. Was it given to you?

If you examine the units, it doesn't make sense to me.

Also, I usually refer to the higher voltage winding as the primary. As a distribution transformer supplying load, I'd expect 11 kV would be the primary winding.
 
  • #10
The question was exactly as phrased, and the formula taken from the text where there's a very similar example problem solved in the course material with slightly different values:

text_sample.JPG


For (b), what's wrong with a step-up transformer? From the assignment:

text_example_2.jpg
 
  • #11
Sorry to question your equation, but I am used to working in per unit.

In per unit, you select the phase to phase voltage in kV and the MVA base.

So, in your case,
kV = 0.415
MVA = 0.2
Zbase = kV^2/MVA = 0.861125

All impedances in ohms have to be divided by the base Z or Zbase to express them in per unit.
r(pu) = 0.014/.861125 = 0.016258
x(pu) = 0.057/.861125 = 0.066192

So my voltage drop equation becomes:

V Drop = I * (r cos th + x sin th)
I = 1 per unit for 100% load
cos th = 0.8
sin th = 0.6

V Drop = 1*(0.016258 * 0.8 + 0.066192 * 0.6)
= 0.052722
To express it in %, just multiply it by 100, so you get 5.2722% - which is exactly what you got by the equation you used.

I just wanted to show that your equation method is OK even though it is foreign to me.
 

Similar threads

  • · Replies 1 ·
Replies
1
Views
3K
  • · Replies 1 ·
Replies
1
Views
2K
  • · Replies 16 ·
Replies
16
Views
9K
  • · Replies 2 ·
Replies
2
Views
4K
  • · Replies 11 ·
Replies
11
Views
7K
  • · Replies 33 ·
2
Replies
33
Views
10K
  • · Replies 6 ·
Replies
6
Views
2K
  • · Replies 2 ·
Replies
2
Views
2K
  • · Replies 7 ·
Replies
7
Views
3K
  • · Replies 2 ·
Replies
2
Views
1K