Junior01 said:Why it is necessary to ground one side of secondary?
FactChecker said:So to specifically answer your questions: One side is grounded so that you know there is a gound provided and can keep track of ground. The "wire" between the primary and secondary is probably a metal form that both primary and secondary wires are wrapped around and is mounted in the transformer chassis. So it should be grounded.
Oh, the wires are insulated (or at least one of them). There is no electrical connection in the winding.Junior01 said:Thank you, but if the "Wire" is wrapped around metal form, and this metal form is grounded it would means that we have a "ground fault", because phase and Earth are directly connected via this metal form?
It is quite possible to have the secondary of a transformer 'floating' The problem is that a 'negligible' high resistance path from the primary side can leave you with the mean voltage of the secondary connections floating at a high voltage. This is a shock risk and can be avoided by a connection of one of the secondary terminals to earth. It defines the range of voltages that can exist in the secondary circuit (never greater than the nominal secondary volts)..Junior01 said:Why it is necessary to ground one side of secondary? What is the line between primary and secondary which is also grounded and why it is grounded?
Really? I thought that double pole fusing was not approved of these days. A few decades ago, we went through all our imported equipment, eradicating all neutral fuses.Hamish Winter said:Imagine wearing a foetal heart monitor and do your usual day to day work?
FactChecker said:There is no electrical connection in the winding.
After you have read those two you may need a bit of a sit down and a jar of the beverage of your choice. (But some people do it for pleasure! Cheers @jim hardy .)jim hardy said:After you've read "The Green Book" , the "National Electric Code" starts to make sense. Surely somebody in your engineering department has a copy you could borrow - it's a small book only about 1/4 inch thick. You can get the basics in an evening.
That was in response to the suggestion in post #6 wires winding around the core would short out. At least that is how I interpreted it.jim hardy said:Not sure quite what that was meant to convey.
One point on the transformer winding SHOULD be 'grounded' ( i prefer term "earthed" ) for two reasons:
i didnt understand #6 myself... my post was more toward Junior01 and I've clarified that with a late edit. No offense meant..FactChecker said:That was in response to the suggestion in post #6 wires winding around the core would short out. At least that is how I interpreted it.
I recently ran into electrostatic shields in an isolation transformer (single phase) project. Here's a link for downloading a pdf file about them and here's a screen shot from it:jim hardy said:1. So static charge cannot build up on the winding (plus whatever it powers) and pierce the insulation.