Understanding Reactive Power Measurements with a Smart Meter

  • Thread starter Thread starter Sebastian Neo
  • Start date Start date
  • Tags Tags
    Resistor
Join the discussion
Ask a follow-up here, or get your own question answered by working scientists, mathematicians and engineers — people, not an autocomplete.
Real named experts · corrections over time · the nuance an AI answer skips
4 replies · 3K views
Sebastian Neo
Messages
5
Reaction score
0
Hi,

I was doing some test with the load bank today and I obtain a value which I don't quite understand.
I supply a 400V Line to Line, 50Hz to a smart meter and to the resistor load bank. The measured value by the smart meter was 500W and -40Var with a current of 0.71A. As the current increases, the real power increases and the reactive power decreases further.

I know that there is no such thing as ideal load but to have a negative reactive power does not make any sense.

Please kindly advice. Thank you
 
Engineering news on Phys.org
the setup was quite simple. I am taking supply from the main power grid into my microgrid and to my smart meter which is connected to the resistor bank.
That's all for my setup
 
A couple of thoughts:

1. Can i assume single phase ?

500 watts and 40 vars is only 501.6 VA
what is the advertised accuracy of your smart meter ? Do your discrepancies fall outside its guaranteed performance?

2. With single phase 501.6VA at 400 volts is 1.254 amps not 0.71,
however
1.254 divided by √3 = 0.723, within 2% of what you report measuring.
So was my assumption of single phase perhaps wrong?

3. There's an ambiguity in your description.
Sebastian Neo said:
As the current increases, the real power increases and the reactive power decreases further.
By 'decreases' do you mean becomes a larger negative number as in moving toward -50, -60, -70 vars?

4. If this is three phase recall that when PF = 1 the line current and line-line voltage are displaced by 30 degrees, which at first glance looks like a PF of about 0.87. That's why there's a two wattmeter method for measuring three phase power.
If you are trying to measure three phase power with a single phase "smart meter", it sounds to me like everything is behaving pretty much as it should.

5. So, what's your "smart meter" ? Got a link to its instruction manual ? And a sketch of your hookup?
 
jim hardy said:
A couple of thoughts:

1. Can i assume single phase ?

500 watts and 40 vars is only 501.6 VA
what is the advertised accuracy of your smart meter ? Do your discrepancies fall outside its guaranteed performance?

2. With single phase 501.6VA at 400 volts is 1.254 amps not 0.71,
however
1.254 divided by √3 = 0.723, within 2% of what you report measuring.
So was my assumption of single phase perhaps wrong?

3. There's an ambiguity in your description.

By 'decreases' do you mean becomes a larger negative number as in moving toward -50, -60, -70 vars?

4. If this is three phase recall that when PF = 1 the line current and line-line voltage are displaced by 30 degrees, which at first glance looks like a PF of about 0.87. That's why there's a two wattmeter method for measuring three phase power.
If you are trying to measure three phase power with a single phase "smart meter", it sounds to me like everything is behaving pretty much as it should.

5. So, what's your "smart meter" ? Got a link to its instruction manual ? And a sketch of your hookup?
By 'decreases' do you mean becomes a larger negative number as in moving toward -50, -60, -70 vars?
Yes, that's what i meant.

I am using ABB A44 meter.

544W is total power for all 3 phase. single phase voltage is 230V. Current for Phase A is 0.71A. Power for 1 phase is 178W.

Total reactive power is -38.94. Phase A reactive power is -15.55 Var, Phase B is -4.92 Var and Phase C is -18.46 VAr