Understanding the Difference between Ground and Neutral in Electrical Systems

  • Thread starter Thread starter neduet
  • Start date Start date
  • Tags Tags
    Ground Neutral
Click For Summary
SUMMARY

The discussion clarifies that Ground (Earth) and Neutral are not the same in electrical systems. Ground serves as a fault current path, while Neutral acts as a current return path during normal operation. In Pakistan and Australia, both systems operate at 415V, with specific connections at the main switchboard. The IEC 60364 standard defines three earthing systems: TN, TT, and IT, each aimed at ensuring safety against indirect contacts and insulation faults.

PREREQUISITES
  • Understanding of electrical systems and safety codes, specifically the National Electric Code (NEC) and IEC 60364.
  • Knowledge of three-phase electrical systems and their configurations.
  • Familiarity with the concepts of fault current paths and current return paths.
  • Basic comprehension of electrical wiring and grounding techniques.
NEXT STEPS
  • Research the IEC 60364 standard for earthing systems and their applications.
  • Learn about the differences between TN, TT, and IT earthing systems.
  • Study the implications of improper neutral and ground connections in electrical systems.
  • Explore the role of protective devices in electrical safety and fault detection.
USEFUL FOR

Electrical engineers, electricians, safety inspectors, and anyone involved in the design or maintenance of electrical systems will benefit from this discussion.

neduet
Messages
64
Reaction score
0
hello friends

can i say that Ground(earth) and neutral are same ?
if not so, please distinguish them for me :smile:


thanks
 
Engineering news on Phys.org
neduet said:
hello friends

can i say that Ground(earth) and neutral are same ?
if not so, please distinguish them for me :smile:


thanks

What is the context of your question? In what country? In what point in the power distribution system? Some places they are connected, and other places they are not.
 
berkeman said:
What is the context of your question? In what country? In what point in the power distribution system? Some places they are connected, and other places they are not.


if three phase motor grounded and neutral are also connected so,
my question only one can doing all necessary work.

like safety and all neutral kind of stuff
 
neduet said:
if three phase motor grounded and neutral are also connected so,
my question only one can doing all necessary work.

like safety and all neutral kind of stuff

What country? What voltages? What is the national electrical safety code in your country? In the US, it is the National Electric Code (NEC).
 
berkeman said:
What country? What voltages? What is the national electrical safety code in your country? In the US, it is the National Electric Code (NEC).


i am from Pakistan Asia, and voltage is 415 v three phase.
 
The neutral acts as a current return path in normal operation whilst the Earth acts as a fault current path in the event a malfunction causes the active conductor to come in contact with a conductive part of equipment (assuming it is bonded to an Earth conductor). It allows a large current to flow and this in turn trips the protective device.

In australia, the only place the neutral and Earth are connected is at the main switch board. We also use 415V, there may be similarities.
 
It's possible to transmit electric power over large distances with just one wire. The Earth (ie, the planet Earth) is used as the current return path. But, there's some danger of electrocution for people nearby. So, we normally let the current return over a second copper wire (the neutral). But if the neutral wire is cut, you, again, get a risk of electrocution. So we end up connecting both the Earth and the neutral to our appliances (three or four wires in total), which is kind of inefficient. Oh well.
 
Neutral is star point of a balance multi phase system, but grounding /earthing is a terminology for explain the connection way of electrical and /or nonelectrical equipment body to Earth as a huge electrical conductor. It presents the three earthing systems defined in standard IEC 60364 and used to varying degrees in all countries. Each earthing system is looked at in terms of dependability (safety, maintainability and availability).
Today the 3 earthing systems such as defined in IEC 60364, are:
- Exposed-conductive parts connected to neutral -TN-;
- Earthed neutral -TT-;
- Unearthed (or impedance-earthed) neutral -IT-.
The purpose of these three systems is identical as regards protection of persons and property: mastery of insulation fault effects. They are considered to be equivalent with respect to safety of persons against indirect contacts.

--------------------------------
Creative thinking is breezy, Then think about your surrounding things and other thought products. http://electrical-riddles.com
 
Snoogans said:
The neutral acts as a current return path in normal operation whilst the Earth acts as a fault current path in the event a malfunction causes the active conductor to come in contact with a conductive part of equipment (assuming it is bonded to an Earth conductor). It allows a large current to flow and this in turn trips the protective device.

In australia, the only place the neutral and Earth are connected is at the main switch board. We also use 415V, there may be similarities.

Why is it not the same if you connect the neutral line to the casing instead of the ground wire? Since neutral is connected to ground at the breaker anyway so what's the different?
 
  • #10
david90 said:
Why is it not the same if you connect the neutral line to the casing instead of the ground wire? Since neutral is connected to ground at the breaker anyway so what's the different?
In case the neutral wire was wired up wrong. Duh. :-p Electrical codes don't always have overwhelming imperative behind them. But they increase safety slightly enough to be worth it. Plus, the electricians unions' get more work for themselves.
 
  • #11
Also it would be less likely (if not completely unable) to identify and interrupt Earth leakage currents. The Earth cable is there for safety, to provide controlled path for faults.

It's not only equipment that is earthed, steel structure, reinforcing in concrete and metal plumbing are also electrically earthed. This means if an active cable somehow comes into contact there is a low impedance path to ground which will activate any protective devices instead of leaving the window frame 'live'.
 
  • #12
david90 said:
Why is it not the same if you connect the neutral line to the casing instead of the ground wire? Since neutral is connected to ground at the breaker anyway so what's the different?

Warning! It is very dangerous; it may be cause the dangerous shock and dying. For description and figure please refer to http://electrical-riddles.com/topic.php?lang=en&cat=7&topic=616"
 
Last edited by a moderator:

Similar threads

  • · Replies 7 ·
Replies
7
Views
2K
Replies
19
Views
2K
  • · Replies 12 ·
Replies
12
Views
5K
  • · Replies 32 ·
2
Replies
32
Views
4K
Replies
12
Views
756
  • · Replies 3 ·
Replies
3
Views
1K
  • · Replies 28 ·
Replies
28
Views
1K
  • · Replies 1 ·
Replies
1
Views
1K
Replies
4
Views
10K
  • · Replies 8 ·
Replies
8
Views
1K