Unbalanced 3 phase power - what happens without a neutral wire?

Click For Summary

Discussion Overview

The discussion revolves around the behavior of unbalanced three-phase power systems, particularly in configurations without a neutral wire. Participants explore theoretical and practical implications of unbalanced loads in electrical distribution networks, focusing on transformer connections and the role of capacitance in such systems.

Discussion Character

  • Technical explanation
  • Conceptual clarification
  • Debate/contested

Main Points Raised

  • Some participants suggest that in IT earthing configurations, unbalanced currents can exist despite the absence of a neutral wire, potentially returning through system capacitance.
  • Others argue that while line currents may become unequal and deviate from a 120-degree phase difference, they still sum to zero, indicating a geometric relationship among the currents.
  • It is noted that unbalanced loads can be supported without a neutral wire, and that transformers connected in Y-Y configurations require a neutral for balancing, which is avoided in three-phase systems to reduce conductor mass.
  • Participants discuss various transformer configurations (Y-delta, delta-Y, delta-delta, and V-V) that can support unbalanced loads without needing a neutral wire.
  • One participant highlights that in HV/EHV/UHV transmission networks, system phase and line voltages can remain balanced even under severe load unbalance.
  • There is a discussion on how currents circulate in delta configurations and how unbalanced loads affect the primary and secondary windings of transformers.

Areas of Agreement / Disagreement

Participants express multiple competing views regarding the handling of unbalanced loads in three-phase systems without a neutral wire. The discussion remains unresolved, with differing interpretations of how unbalanced currents are managed and the implications of various transformer configurations.

Contextual Notes

Some limitations include the dependence on specific transformer configurations and the assumptions about load characteristics. The discussion does not resolve the mathematical or theoretical complexities involved in these systems.

Pawlal
Messages
2
Reaction score
0
Hi

I've recently started learning about electrical three phase theory, and therefore got some questions.

Imagine the following:
Countries like Albania, Norway ++, have IT earthing configuration in their distribution grids, i.e. the neutral point is not solidly grounded, however "grounded" through the system capacitance.

So, I imagine that its hard to balance each transformer and some unbalance current exist?
How can this exist, if there is no neutral, does all this unbalanced current return back via the capacitance?Thanks for any help for this fundamental question.
 
Engineering news on Phys.org
Pawlal said:
So, I imagine that its hard to balance each transformer and some unbalance current exist?
How can this exist, if there is no neutral, does all this unbalanced current return back via the capacitance?

No,
the line currents become unequal and their phase difference shifts away from 120 degrees.
They still sum to zero (or to whatever small amount can return through system capacitance)

so your current phasors no longer make an equilateral triangle.
It becomes an exercise in geometry to construct a triangle with sides proportional to your actual line currents.
 
Last edited:
  • Like
Likes   Reactions: cabraham, Pawlal, CalcNerd and 1 other person
In 3 phase distribution, unbalanced loads are supported without the need for a neutral wire. No load is truly balanced, but system phase & line voltages stay balanced even with severe load unbalance.
It was learned over a century ago, that transformers connected in Y-Y, without a delta tertiary, cannot support unbalanced load with only 3 wires, a neutral wire is needed for Y-Y units.
But that defeats the purpose of using 3 phase. Using 3 wires with 3 phase requires only 75% the conductor mass as other numbers of phases.
So the power company avoids Y-Y xfmrs. They use Y-delta, delta-Y, delta-delta, & V-V (open delta). These xfmr configurations support unbalanced loads with only 3 wires.
If it is necessary for primary & secondary to both be Y connected, a third winding, a tertiary, connected in delta, is used. With Y-Y-delta, unbalanced loads are supported with just 3 wires.
The grid is a 3 wire system, but 4th wires are used for lightning protection & safety grounding. The lighter gauge wires above the 3 power wires are for lightning protection. Xfmr neutrals are grounded to keep system close to ground potential. Otherwise the potential to ground is determined by capacitance. The 240 volt side of a xfmr could be near 2,400 volts with respect to ground via capacitive coupling, if ungrounded.
Neutral connections are not relied upon to carry unbalance in current.

Claude Abraham
PhD student in EE now
40 year EE
 
  • Like
Likes   Reactions: Pawlal, anorlunda and jim hardy
cabraham said:
No load is truly balanced, but system phase & line voltages stay balanced even with severe load unbalance.
Hi @cabraham, this is interesting!
Could you please elaborate this point? How is this achieved in an HV/EHV/UHV 3-wire transmission network?
 
cnh1995 said:
Hi @cabraham, this is interesting!
Could you please elaborate this point? How is this achieved in an HV/EHV/UHV 3-wire transmission network?
Power has been studied for over a century. Transformers are used to step generated voltage up (current gets stepped down), transmit long distance, then xfmr steps down voltage at load end.
3 phase xfmr configurations include Y-Y, delta-Y, delta-delta, Y-delta, & V-V (open delta).
Only the Y-Y connection requires 4 wires to stay balanced when load is unbalanced. Suppose the load end xfmr is Y-delta, with unbalanced load at secondary, delta side.
A delta is a closed loop, & currents may circulate inside delta without leaving the closed loop.
If the B-C leg of the delta is loaded, with phases A-B & C-A open, what happens? The current in B-C liad is sourced by 2 parallel paths, the B-C secondary winding of the delta, in parallel with the series combination of A-B & C-A windings of the delta secondary. The current divides as follows. Leg B-C sources 2/3 of load current. Leg A-B-C-A sources 1/3 load current.
The 3 primary windings of the Y reflect these currents. Since the B-C leg of secondary delta has 2/3 load current, the corresponding Y winding in primary has 2/3 the amp turns of the load as well. The remaining 2 windings have 1/3.
Kirchhoff current law is met as 2/3 enters neutral & 2 times 1/3 leaves neutral.
Remember this, 3 phase systems stay balanced with only 3 wires, except Y-Y, because unbalanced current in one phase can return via the other two phases.
In the case above, if B-C winding in delta secondary couples n-c winding in Y primary, the neutral to phase C winding has unbalanced current, 2/3 value. The return path for phase C excess current is phases A & B.
I will attach sketches later.

Claude Abraham
PhD student in EE
EE 41 years
 

Similar threads

  • · Replies 6 ·
Replies
6
Views
2K
  • · Replies 16 ·
Replies
16
Views
5K
  • · Replies 19 ·
Replies
19
Views
4K
  • · Replies 7 ·
Replies
7
Views
3K
  • · Replies 26 ·
Replies
26
Views
4K
  • · Replies 41 ·
2
Replies
41
Views
19K
Replies
12
Views
5K
  • · Replies 6 ·
Replies
6
Views
3K
  • · Replies 7 ·
Replies
7
Views
5K
  • · Replies 11 ·
Replies
11
Views
5K