Unloaded Transmission Cable Shocks Worker

  • Thread starter Thread starter stuckie27out1
  • Start date Start date
  • Tags Tags
    Cable Transmission
AI Thread Summary
An electrical worker was shocked while cutting insulation from a transmission cable that had been offloaded and was not connected to power. The incident occurred less than four hours after another crew had tested the cable for continuity with a megger. Factors such as dry weather, lack of insulation gloves, and the cable's length likely contributed to a significant triboelectric charge buildup. The shock experienced was akin to touching a charged capacitor, causing pain but no lasting harm. The discussion highlights the importance of proper discharge procedures after testing cables to prevent such incidents.
stuckie27out1
Messages
3
Reaction score
0
So here is the situation:

At a particular site a crew of electrical workers were putting some transmission cable in the ground. The cable was off loaded from behind a trencher machine (the cable is in a roll of around 2000 feet). Some short time less than 4 hours another crew came to put some intermediate grounds into the soil.

This is all straight forward but what happened next is hard to explain. When the worker reached in and began to cut away the insulation with a knife to get access to the concentric neutral. He was shocked with enough magnitude to have to receive a trip to the hospital. He recovered and was unharmed.

Note there was no power connected to the cable.

What could explain this strange phenomenon?

Specifics:
Cable is similar to this look at 4/0 for specifics http://www.generalcable.com/NR/rdon...-9E30-B468D4B75A85/0/p046_047_ConcenNeuUG.pdf

Weather conditions were dry and hot mid/low 90's
Worker was not wearing insulation gloves
Cable had been tested with a megger some day previous for continuity.

I have a few ideas floating around but thought I would suppress them to see what you guy thought/ or have experienced before.
 
Engineering news on Phys.org
Tribolelectric charge buildup when the cable was handled?
It is a serious problem with some types of cables, it can results in voltages up a volts even if the cable is only a few feet long, so for 2000 feet cable both the charge and voltage could presumably be significant.

From the workers point of view it was probably like touching both terminals of a charged high voltage capacitor; not much current but still very painful.
 
Very interesting...

f95toli charge must have played a part in what was a cummulative effect...

i had immediately thought that this was problably a test cable off the line and some kind of insulation test was done...

then i read what you said...

Weather conditions were dry and hot mid/low 90's
Worker was not wearing insulation gloves
Cable had been tested with a megger some day previous for continuity.

each of those conditions are ripe for charge collection but its the megger test that did it for me...
bet that cable wasnt adequately discharged after the kit was disconnected...

what kind of currents did the megger pump down the line?
i'd expect that it would take some while to discharge after charging considering the length of the cable...

the meggers we have pumps 25 amps just for a ground test...so it would be good to know...
 
The shock was more than likely a result of the IR test performed previously. This is quite common on cables of that length if the conductors are not discharged after the test. I've had it happen to me (once) about 10 years ago. However, the shock should be minimal though.

CS
 
I was thinking that the cable could have been parallel to some overhead transmission lines and induction was charging it.
 
Very basic question. Consider a 3-terminal device with terminals say A,B,C. Kirchhoff Current Law (KCL) and Kirchhoff Voltage Law (KVL) establish two relationships between the 3 currents entering the terminals and the 3 terminal's voltage pairs respectively. So we have 2 equations in 6 unknowns. To proceed further we need two more (independent) equations in order to solve the circuit the 3-terminal device is connected to (basically one treats such a device as an unbalanced two-port...
suppose you have two capacitors with a 0.1 Farad value and 12 VDC rating. label these as A and B. label the terminals of each as 1 and 2. you also have a voltmeter with a 40 volt linear range for DC. you also have a 9 volt DC power supply fed by mains. you charge each capacitor to 9 volts with terminal 1 being - (negative) and terminal 2 being + (positive). you connect the voltmeter to terminal A2 and to terminal B1. does it read any voltage? can - of one capacitor discharge + of the...
Thread 'Weird near-field phenomenon I get in my EM simulation'
I recently made a basic simulation of wire antennas and I am not sure if the near field in my simulation is modeled correctly. One of the things that worry me is the fact that sometimes I see in my simulation "movements" in the near field that seems to be faster than the speed of wave propagation I defined (the speed of light in the simulation). Specifically I see "nodes" of low amplitude in the E field that are quickly "emitted" from the antenna and then slow down as they approach the far...

Similar threads

Back
Top