The discussion revolves around the concepts of voltage, current, resistance, and Ohm's Law, exploring their relationships and implications in circuit analysis. Participants engage in clarifying definitions and addressing common confusions, particularly regarding the sequence of voltage and current in electrical circuits.

Discussion Character

  • Conceptual clarification
  • Debate/contested
  • Technical explanation

Main Points Raised

  • Some participants propose that Ohm's Law describes a constant ratio of voltage to current in ohmic materials.
  • One participant notes that voltage must be present for current to flow, suggesting that this is often overlooked in circuit analysis.
  • Another participant disagrees, arguing that in circuit analysis, voltages and currents are treated as simultaneous, with no clear first or second.
  • It is mentioned that while circuit analysis assumes simultaneous existence of voltage and current, physically, current cannot exist without a driving voltage.
  • Participants discuss the implications of Maxwell's equations, suggesting that understanding the physical behavior of voltage and current requires considering time domain solutions.
  • There is a debate about whether a battery can be considered a voltage source, with some participants emphasizing the need for an electric field to drive current.
  • One participant expresses concern that the discussion may be too advanced for beginners, suggesting a focus on basic definitions and relationships.

Areas of Agreement / Disagreement

Participants express differing views on the relationship between voltage and current, with some asserting that voltage must precede current, while others argue that they exist simultaneously in circuit analysis. The discussion remains unresolved regarding the causal relationship between voltage and current.

Contextual Notes

Participants acknowledge that the discussion involves complex concepts that may not be suitable for beginners, and there are limitations in how circuit analysis can represent physical phenomena without considering the underlying field dynamics.

Pogba
Messages
1
Reaction score
0
So what's the smplest illustration for voltage ,current and resistance and what's ohms law ?
 
Engineering news on Phys.org
virginia-route-29-copper-circuit.png


The picture shows the simplest case when the material for the resistor R is ohmic. Ohmic means that the ratio V/I is constant.

:welcome:
 
  • Like
Likes   Reactions: Pogba and Simon Bridge
Simon Bridge said:
you said you had "voltage confusion"

I think that is that moment of disorientation after coming into contact with mains voltage. (PS: don't try this at home)

BoB
 
One problem that can be confusing is the formula on paper fails to point out that voltage has to be there first for current to flow. People sometimes make the mistake of assuming a voltage is present simply because IR says it should be there.
 
CraigHB said:
One problem that can be confusing is the formula on paper fails to point out that voltage has to be there first for current to flow. People sometimes make the mistake of assuming a voltage is present simply because IR says it should be there.

Sorry, but I disagree. In circuit analysis, for Kirchoff's laws to apply, we say that voltages and currents apply simultaneously. There is no first/second.

It is also perfectly valid to say "voltage is present simply because IR says it should be there". If you prefer, think of a resistor connected to an ideal current source. The voltage appears because the current flows (and the current flows because the voltage appears). No first and second, but simultaneously.

If you really want to find out what happens first, then you need time domain solutions to Maxwell's equations, but then that it no longer circuit analysis. You will find that the fields propagate at near light speed.

This recent thread talked about the assumptions of circuit analysis in some detail.
https://www.physicsforums.com/threads/why-does-a-voltmeter-measure-a-voltage-across-inductor.880100
 
anorlunda said:
It is also perfectly valid to say "voltage is present simply because IR says it should be there". If you prefer, think of a resistor connected to an ideal current source. The voltage appears because the current flows (and the current flows because the voltage appears). No first and second, but simultaneously.
....
If you really want to find out what happens first, then you need time domain solutions to Maxwell's equations, but then that it no longer circuit analysis. You will find that the fields propagate at near light speed.

Yes - it is, certainly, correct for the purpose of circuit analysis to assume that both - voltage and current - do exist at the same time and that - for example - a current is able to produce a voltage across a resistor (V=I*R).
However, from the physical point of view it is clear that no current can exist without driving voltage - hence, voltage first and current next. This basic rule applies, of course, also to circuits with "current sources" which, in reality, always are voltage sources eqipped with a very large (dynamic) source resistance.

Remember: Current is movement of electrical charges - and the force which can cause such a movement is provided by the electrical field created within the conducting material by the applied voltage.
 
Last edited:
  • Like
Likes   Reactions: cnh1995
anorlunda said:
If you really want to find out what happens first, then you need time domain solutions to Maxwell's equations, but then that it no longer circuit analysis. You will find that the fields propagate at near light speed.

With respect to time, yes that's the case. I was not trying to say voltage is first in instance, but that voltage is a prerequisite for current to flow. V=IR does not make that distinction. If you assume a current you also have to assume a voltage which may or may not be there. That can give a person trouble conceptually looking at what's happening in a real circuit.
 
LvW said:
However, from the physical point of view it is clear that no current can exist without driving voltage - hence, voltage first and current next.
You'd agree that Maxwell's equations describe your physical point of view? If so, then voltage does not come before current or vice versa - there's no causal relationship between them.

@LvW, can you give an example of something you'd consider a voltage source? A battery perhaps, do you consider that a voltage source?
 
  • #10
LvW said:
However, from the physical point of view it is clear that no current can exist without driving voltage - hence, voltage first and current next. This basic rule applies, of course, also to circuits with "current sources" which, in reality, always are voltage sources eqipped with a very large (dynamic) source resistance.

The physical equations that describe the behavior are Maxwells Equations. To solve the time evolution is a study of fields, not circuits. With fields, you need the exact geometry to describe the sequence of events because fields are 3D. If you have just a resistor, and no geometry information, you can't solve the field equations, so the only tool you have left is circuit analysis.

You may be thinking of the Drude Model. Maxwells Equations are a much better foundation.

Edit: Also, consider that the OP was very much a beginner's question. We (including me) should not be injecting this esoteric stuff to this thread.
 
Last edited:
  • Like
Likes   Reactions: sophiecentaur
  • #11
milesyoung said:
You'd agree that Maxwell's equations describe your physical point of view? If so, then voltage does not come before current or vice versa - there's no causal relationship between them.
@LvW, can you give an example of something you'd consider a voltage source? A battery perhaps, do you consider that a voltage source?
OK - I must admit that I didn`t express myself clear enough. It was not correct to say "voltage first and current next" because this involves a time sequence.
It was my only intention to answer the question: Which force causes the charges to move within the conductive material. Is it not true that we need an electric field as a precondition? And - yes - I would consider a battery as a (of course non-ideal) voltage source.
 
  • #12
LvW said:
... I would consider a battery as a (of course non-ideal) voltage source.
Okay, let's use this as a starting point. In the following, in the questions I might pose, I'm not trying to trick you or anything, I genuinely just want to present you an alternative viewpoint. Your line of reasoning is shared by many.

Let's assume non-ideal components, no hocus pocus. How do you know a battery is a voltage source? I just mean in practical terms - is it something you can measure?
 
  • #13
milesyoung - I am not sure if it makes much sense to discuss here the properties of a battery.
On the other hand - it would be interesting to learn more about your "alternative viewpoint".
Perhaps you consider the moving/separation of charges within the device - prior to using it as a usable voltage source - also as a kind of current ?
In this case - my answer would be: Obviously, the OP was asking for some clarification regarding the terms "voltage", "current" and "resistor" - as they appear as electrical quantities in electrical circuits. And for such circuits the basic rule applies: Each current needs a driving voltage.
Do you see my point? I think - in particular for beginners - it is important to know that relations like R=V/I may be used also in other forms (like I=V/R or V=I*R) - however, it is not always (per se) allowed to automatically derive from such forms any information about cause and effect.
(Have you seen a similar discussion about the relation Ic=B*Ib?)
 
  • #14
LvW said:
milesyoung - I am not sure if it makes much sense to discuss here the properties of a battery.
I'm not interested either in a discussion on the specifics of batteries, but it's one of the simplest examples I could think of of something you associate with a voltage source.

I'm not even talking about circuit theory, I just want to pose you the basic question: what is it about the behavior of a battery that makes you sure it's a voltage source? To put it another way, if I gave you a 2-terminal black box with a battery inside and asked you to probe the terminals, what would make you conclude that it's a voltage source?
 
  • Like
Likes   Reactions: Averagesupernova
  • #15
milesyoung said:
... I gave you a 2-terminal black box with a battery inside and asked you to probe the terminals, what would make you conclude that it's a voltage source?

Any electrostatic measurement device would react upon the potential difference, would it not?
 
  • #16
LvW said:
Any electrostatic measurement device would react upon the potential difference, would it not?
Sure, but that would also be the case for a nonideal current source.

What if I, in my EE studies, had a very difficult teacher. He/she had a preference for current sources and would almost never show a voltage source - practically everything would be modeled as current sources. I'd later come to this board, engage in this same discussion with you, but I'd be adamant about there being a current source in the box, not a voltage source. Who of us is right?
 
  • #17
milesyoung said:
Sure, but that would also be the case for a nonideal current source.

Yes - because each non-ideal current source is (in reality) a non-ideal voltage source.
Remember: Which effect (which force) causes the charges to move (forming the quantity we call "current") ?
 
  • #18
LvW said:
Yes - because each non-ideal current source is (in reality) a non-ideal voltage source.
Why is my black box not part of your reality? :cry:

LvW said:
Remember: Which effect (which force) causes the charges to move (forming the quantity we call "current") ?
The force can be either electric or magnetic, depending on your choice of reference frame. I assume you're analyzing this from the rest frame of the conductor, but that frame is no more fundamental than any other.

https://en.wikipedia.org/wiki/Classical_electromagnetism_and_special_relativity

I can try to find an example that shows the effect for a charged particle within a conductor that's not in electrostatic equilibrium, but even the simplest of cases tend to become very complicated very fast, and I'm afraid I never studied special relativity much beyond the simple cases I saw in classical EM.
 
  • #19
Doesn't the discussion come down to can we have a circulating current with no voltage? Is there not current in a copper pipe when we drop a magnet through it? In the real world there is a finite resistance in the copper. What about a super conducting pipe?
 
  • #20
The core of our discussion is: What is "electrical current" and where does it come from - correct?
More than that, I think, here we speak about classical electric/electronic circuits and applications (and not about "exotic" arrangements based on superconducting material).
In this context: Is there any real technical device which we call "current source" (labor slang), that is not energized by a voltage?
And - we shouldn`t forget that the start of the discussion was the question: Is it correct to say "a current produces a voltage according V=I*R" ?
 
  • #21
The OP has not shown himself since the top of the thread. Perhaps Pogba could respond and tell us
1. What he/she already knows about the topic
2. His/her views on what has been written already.
 
  • #22
Where are you going to draw the line? Sure most folks can't come up with a super conductor in their garage or basement. Most people can come up with a voltage source by popping the hood of their car and messing with the battery. Very little knowledge of electronics is required for that. Slightly more knowledge is required to come up with a current source. Is a current source considered exotic by those who are only able to hook a voltmeter and simple loads to a voltage source?
 
  • #23
Averagesupernova said:
Is a current source considered exotic by those who are only able to hook a voltmeter and simple loads to a voltage source?
I think, this can be answered only by means of an example for a technical realization of that what we call "current source".
Where is such an example?
 
  • #24
sophiecentaur said:
The OP has not shown himself since the top of the thread. Perhaps Pogba could respond and tell us
1. What he/she already knows about the topic
2. His/her views on what has been written already.

Yes - for my opinion, it is a very unfortunate situation (which happens rather often) that an OP never tells us (forum members who gave answers) if he is satisfied or not.
 
  • #25
LvW said:
I think, this can be answered only by means of an example for a technical realization of that what we call "current source".
Where is such an example?
There is no such example in the real world. This is why I brought up super conductors since they are as close to ideal as we can get in the real world. No voltage, yet we have circulating currents. Maybe this drags the discussion in a different direction. Just thought I would throw it out there.
 
  • #26
Re, A Current Source:
Averagesupernova said:
There is no such example in the real world.
We are talking 'real world' and not mathematics.
There is a pretty good example, certainly in Engineering Terms, of a current source and that is the electron beam in a CRT. With tens of keV available, currents in the order of 1mA will be 'whatever they want to be', when the Anode of a EHV electron tube is connected in circuit. It may not be in our general experience and whilst the nice constant voltage from a car battery is very familiar as a Voltage Source, a beam of charged particles is just as insistent in doing what it was designed to do.
Brute force High impedances may be a bit more trouble to produce than brute force Voltage sources but you can find them all over the place. (Solar wind?)
[Edit: Perhaps I should have included a note on Health and Safety at this point. But that also applies to the use of car batteries by the uninitiated]
 
Last edited:
  • #27
Averagesupernova said:
Doesn't the discussion come down to can we have a circulating current with no voltage? Is there not current in a copper pipe when we drop a magnet through it? In the real world there is a finite resistance in the copper. What about a super conducting pipe?

Superconductors are real world. They can circulate current indefinitely with identically zero voltage drop.

The debate point in this thread is worth argument.

On one hand, we have circuit analysis in which V=IR happens simultaneously. There is no voltage first. Simultaneity is necessary for Kirchoffs laws (KVL, KCL) to work.

On the other hand we have fields described by Maxwells Equations. That is a 3D problem.

Still deeper, we have quantum electrodynamics (QED). QED is the only completely accurate way to describe voltages and currents. Even Maxwells equations need some simplifications before they can be derived from QED.

In between circuits/fields is a quagmire. Unfortunately, those yearning for a more physical explanation sometimes imagine electrons as little billiard balls, or as capsules of energy, and wind up in the middle of the quagmire. I argue "Stay away from the quagmire. Go all the way to Maxwells Equations as the next step deeper."

Even the history of the famous Drude model of electrical conduction shows quagmire.
https://en.wikipedia.org/wiki/Drude_model#Accuracy_of_the_model said:
Historically, the Drude formula was first derived in an incorrect way, namely by assuming that the charge carriers form an ideal gas. It is now known that they follow Fermi–Dirac distribution and have appreciable interactions, but amazingly, the result turns out to be the same as the Drude model because, as Lev Landauderived in 1957, a gas of interacting particles can be described by a system of almost non-interacting 'quasiparticles' that, in the case of electrons in a metal, can be well modeled by the Drude equation.

This simple classical Drude model provides a very good explanation of DC and AC conductivity in metals, the Hall effect, and thermal conductivity (due to electrons) in metals near room temperature. The model also explains the Wiedemann–Franz law of 1853. However, it greatly overestimates the electronic heat capacities of metals. In reality, metals and insulators have roughly the same heat capacity at room temperature. The model can be applied to positive (hole) charge carriers, as demonstrated by the Hall effect.

One note of trivia surrounding the theory is that in his original paper Drude made a conceptual error, estimating electrical conductivity to in fact be only half of what it classically should have been.
 
  • #28
I really don't wish to be involved in this any deeper than that circulating currents exist in superconductors with zero voltage. Anything beyond this is out of my area of expertise by several light-years. I tend to agree with anorlunda in that just accept that current and voltage are inseparable in simple circuit analysis and choose which is what based on convenience. I will blindly accept what has been said here about Maxwell's work and QM as it does not really apply to me at this point in my life.
 
  • Like
Likes   Reactions: sophiecentaur
  • #29
LvW said:
In this context: Is there any real technical device which we call "current source" (labor slang), that is not energized by a voltage?

I don't see how that could be possible. Current being "movement" of charge, it's always going to take some force to cause movement. That's just classic physics. In the case of a super-conductor a constant application of voltage is not required since resistance is essentially zero, but it still takes an initial application of voltage to induce a current.

From what I understand there is still some mystery around the workings of current flow. For example in a battery it's positively charged particles that provide movement of charge and in a wire it's negatively charged particles. In some cases it can be both.
 
  • #30
I do wonder whether the merit of this question justifies 30 posts. It's a bit like 'In a fight, would a bear beat a lion?'
I would point out that the definition of Voltage involves Energy (the King of Physical quantities, if ever there was one) and also charge so ,if you really want a pecking order, Voltage would probably come out on top. But who cares? It's relationships that count in Science and you need more than one variable to have a relationship.
Whilst it's been pointed out that current can flow without a voltage, it is worth noting that such current doesn't involve any Energy Transfer - so the phenomenon of superconductivity is, despite its usefulness, a bit of a red herring in this discussion.
 

Similar threads

  • · Replies 44 ·
2
Replies
44
Views
8K
  • · Replies 10 ·
Replies
10
Views
2K
  • · Replies 38 ·
2
Replies
38
Views
4K
  • · Replies 51 ·
2
Replies
51
Views
7K
  • · Replies 21 ·
Replies
21
Views
4K
  • · Replies 3 ·
Replies
3
Views
2K
  • · Replies 4 ·
Replies
4
Views
1K
  • · Replies 11 ·
Replies
11
Views
2K
  • · Replies 3 ·
Replies
3
Views
3K