Voltage/Current variation in a motor

  • Thread starter Thread starter rbarbali
  • Start date Start date
  • Tags Tags
    Motor Variation
Click For Summary

Discussion Overview

The discussion revolves around the behavior of a WEG asynchronous 3-phase motor under varying line voltages and its corresponding current measurements. Participants explore the implications of voltage changes on motor performance, including magnetizing current and power factor, while considering the motor's loading conditions.

Discussion Character

  • Technical explanation
  • Debate/contested
  • Experimental/applied

Main Points Raised

  • One participant notes that the motor's line voltage of 410 V exceeds its rated voltage of 380 V, suggesting that this may lead to increased magnetizing current as the motor approaches saturation.
  • Another participant agrees that the relationship between voltage and current is valid only if the motor operates at constant power to the load.
  • A participant questions whether the observed current measurements indicate that the motor is not operating at full load, given the current readings at different voltages.
  • One participant estimates that the motor is lightly loaded based on the current drop below nameplate values at increased voltage levels.
  • There is a suggestion to measure leakage flux using a solenoid coil to observe variations in performance under different voltage conditions.
  • Another participant humorously suggests replacing the motor with a 400 V model if it fails due to overvoltage conditions.

Areas of Agreement / Disagreement

Participants express differing views on the implications of voltage changes on motor performance and loading conditions. While some agree on the effects of overvoltage leading to increased magnetizing current, there is no consensus on the exact loading status of the motor or the relationship between voltage increment and power factor decrement.

Contextual Notes

Participants acknowledge the complexity of the motor's behavior under varying voltage conditions, including the potential for saturation and its effects on current draw. There are also references to specific measurements and calculations that remain unresolved.

Who May Find This Useful

This discussion may be of interest to electrical engineers, technicians working with motors, and individuals involved in industrial applications where motor performance under varying voltage conditions is relevant.

rbarbali
Messages
3
Reaction score
2
Hi all.
I have a question.
I have a WEG asynchronous 3-phase motor, 0.55 kW (0.75 HP), 380 V, 50 Hz, cos PHI 0.82, 1410 RPM, star / Wye connected, plate current 1.50 A.
It's mounted on a conveyer belt and powered simply trough a 3-phase contactor and a Thermal Magnetic GV2ME.
In the facility, there were 410 V line voltage and I measured a line current of 1.60 A, but when later the voltage down to 400 V the current measured was 1.35 A, the current was measured by an RMS current probe.

I thougth that greater line voltage reduces the line current working near motor's nominal power, but I don't understand the measurement. Any suggestions?

rbarbali
 
Engineering news on Phys.org
rbarbali said:
I thougth that greater line voltage reduces the line current working near motor's nominal power, but I don't understand the measurement. Any suggestions?

Your 410 volts is more than the motor's rated 380 by about 8%.

Which means you're driving its magnetic flux higher, nearer saturation
so it draws a bit more magnetizing current.

That's because of the ubiquitous B-H curve
from http://www.coolmagnetman.com/magfund07.htm
upload_2019-1-30_20-8-33.png

Since this plot has no numbers on it, we can say it's effectively amps horizontal & volts vertical

Flux will be in proportion to voltage
and once you're out past the knee it takes quite a bit more magnetizing current to push flux higher..
rbarbali said:
greater line voltage reduces the line current working near motor's nominal power,

If you drop volts low enough, the motor will begin to slow down and could even draw starting current.
That's why they burn up if you try to run them on an inadequate extension cord ..So there's a 'sweet spot' for voltage, and as you move away from it in either direction current goes up. ..

Any help?

old jim
edit PS i see Tom and i crossed in the mail again !
 

Attachments

  • upload_2019-1-30_20-8-33.png
    upload_2019-1-30_20-8-33.png
    11 KB · Views: 766
  • Like
Likes   Reactions: jrmichler and Tom.G
rbarbali said:
I thougth that greater line voltage reduces the line current working near motor's nominal power, but I don't understand the measurement. Any suggestions?
That is valid if the motor is operating at constant power to the load.

p.s. That is the short answer, I see Jim gave a long version as I was typing.
 
  • Like
Likes   Reactions: jim hardy
PS2 A curve with magnetizing current vertical and flux(and volts) horizontal,

upload_2019-1-30_20-29-15.png
 

Attachments

  • upload_2019-1-30_20-29-15.png
    upload_2019-1-30_20-29-15.png
    3 KB · Views: 689
Thanks Jim and Tom.
I thought that the effect of the increment of the voltage over the magnetizing current was minor than I measured, but I understand, from your explanation, that the motor is going into saturation.Can we relate the effect of the voltage increment / current increment with the decrement of the power factor in the graph?

upload_2019-1-31_13-52-26.png


I can't measure the machine with 380 V (motor's nominal voltage): the present line voltage is, more or less, 400 V. From the measurement (1.60 A @ 410 V and 1.35 A @ 400V) would you tell (estimate) that the motor is not working at full load? (Working at full load, at nominal voltage 380 V, I would expect measure 1.5 A as per plate).
 

Attachments

  • upload_2019-1-31_13-52-26.png
    upload_2019-1-31_13-52-26.png
    26.8 KB · Views: 696
I would estimate that as you suspect it's lightly loaded.

I say that because your current drops below nameplate between 5% and 8% overvoltage

Is my arithmetic right -
dividing your readings by nameplate values
at 7.9% overvoltage you have 6.7% overcurrent
and at 5.2% overvoltage you have 10%undercurrent
upload_2019-1-31_14-51-3.png


Is that motor running pretty hot to the touch ? Its iron is being worked fairly hard because of the overvoltage.
Find an old solenoid coil, connect it to a DMM set for AC millivolts.
Wave the coil around your motor and the meter will give you an indication of leakage flux.
Try it on days when your house voltage is running high, and when it's running low.
They'll differ because as the core moves into saturation more flux will squeeze out into the air.
If you have one of those battery "ScopeMeter" gizmos, observe the waveform. You'll see a very peaky wave, and you should notice the peaks are exaggerated on high voltage days.

Magnetics is a LOT of fun !

Any Industrial Plant is a tinkerer's paradise and such experimenting solidifies your basics - i hope your management is enlightened enough to permit it.
Write up an experiment plan and approach the boss?

old jim
 

Attachments

  • upload_2019-1-31_14-51-3.png
    upload_2019-1-31_14-51-3.png
    32.7 KB · Views: 742
Last edited:
  • Like
Likes   Reactions: Asymptotic
PS when it burns up , put in a 400 volt motor.
 
Hmmmm... a WEG you say ?
Does it have a little sticker saying it's wound with "Wise-Wire" ?
If so that's quality motor..
I found one, 30hp, in my favorite salvage yard(30 cents a pound) , bought and gave it to a friend.
Its construction was impressive.

old jim
 
Thanks Jim for your help.
I will check the temperature of the motor in a couple of weeks. Keep you informed.

Jose.
 
  • Like
Likes   Reactions: jim hardy

Similar threads

  • · Replies 20 ·
Replies
20
Views
3K
Replies
4
Views
2K
Replies
12
Views
4K
  • · Replies 1 ·
Replies
1
Views
2K
  • · Replies 1 ·
Replies
1
Views
4K
  • · Replies 3 ·
Replies
3
Views
3K
Replies
1
Views
4K
  • · Replies 13 ·
Replies
13
Views
5K
  • · Replies 5 ·
Replies
5
Views
6K
Replies
2
Views
2K