What is the recommended size for a neutral conductor in a 3 phase 4 wire system?

Click For Summary
In a 3-phase 4-wire system, the recommended size for the neutral conductor can vary based on the application, with some suggesting it should match the phase conductor size for safety. The neutral is not typically expected to carry current except in fault conditions, particularly when powering motors, while it may carry current in low voltage (LV) distribution systems with unbalanced loads. Standards such as IEC or NEC may require the neutral busbar to be the same size as the phase busbar, although specific clauses were not cited in the discussion. Users are advised to err on the side of caution and use the same size conductor if unsure. Proper sizing is crucial for safety and efficiency in electrical distribution systems.
Zubair8
Messages
2
Reaction score
0
Hi,
Frankly, I'm new to this forum. So please do guide me if I posted wrongly.

I need some help in sizing the neutral wire. For a 3 phase 4 wire system (3Ph + N), what is the recommended size of the neutral conductor. Should it be the same as the phase conductor or should it be 50% of the phase conductor. Let say a power cable that is sized up to 300sqmm, does the neutral cable also need to be sized to 300sqmm or can it be less?

Is there any specific standard, IEC or NEC that mentioned the requirement for neutral conductor size. Appreciate if you guys can mention the IEC or NEC number.

Thanks.
 
Engineering news on Phys.org
Do you mean neutral or ground? There may be a difference depending on what you are running power to. When running 3 phase power to a motor for example, what you are calling 'neutral' isn't really neutral at all. It is not supposed to carry any current except in the case of a fault. It is to be grounded to the case of the motor. However, when running 208 or 240 volt power into a building the 4th conductor (combination neutral/ground) will carry some current because of lights and other 120 volt loads. You are always safest making the 4th conductor the same size as the other 3.
 
I agree with Averagesupernova. Use the same size conductor if in doubt.

Three phase systems may or may not have a neutral wire. A neutral wire allows the three phase system to use a higher voltage while still supporting lower voltage single phase appliances. In high voltage distribution situations it is common not to have a neutral wire as the loads can simply be connected between phases (phase-phase connection).
http://www.3phasepower.org/3phasewiring.htm"
 
Last edited by a moderator:
With motor its pretty straight forward, but main concerns are when dealing with LV distribution where unbalanced load exist.

For LV distribution, normally the power supply from LV Switchgear to LV MCC utilizes big cables (150sqmm - 300sqmm). The same case also applies to LV Switchgear Busbar Rating. To save copper, some people opt for lower neutral busbar rating compared to the phase busbar.

As I understand, recently either IEC or NEC requires the neutral busbar to be of the same size as the phase busbar. Can anybody point out to which clause in IEC or NEC that mentioned this.

Appreciated it. Thanks.
 
I am trying to understand how transferring electric from the powerplant to my house is more effective using high voltage. The suggested explanation that the current is equal to the power supply divided by the voltage, and hence higher voltage leads to lower current and as a result to a lower power loss on the conductives is very confusing me. I know that the current is determined by the voltage and the resistance, and not by a power capability - which defines a limit to the allowable...

Similar threads

Replies
21
Views
5K
Replies
9
Views
5K
  • · Replies 6 ·
Replies
6
Views
3K
Replies
8
Views
8K
  • · Replies 1 ·
Replies
1
Views
5K
Replies
12
Views
5K
Replies
1
Views
3K
  • · Replies 1 ·
Replies
1
Views
6K
  • · Replies 10 ·
Replies
10
Views
3K
Replies
6
Views
3K